So this lens creates a flat and continuous projection along the plane of the underside of the roof? Agree that you don't need a sprinkler in the skylight ... unless you consider the space above the lens to be a combustible concealed space.
Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Hairfield Sent: Wednesday, May 15, 2013 9:03 AM To: [email protected] Subject: Skylights I have a project where the skylights are more than 32 sq.ft. in area which normally would require sprinkler protection, my project has a translucent panel attached at the roof line sealing off the skylight thus eliminating a ceiling pocket. My thoughts since there is not a ceiling pocket then sprinklers would not be required for this type of skylight. Any opinions? Mike Hairfield _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org