Using the FDC (equiv  length of 100 ft) with a 4" Storz and 100 ft of 4 inch 
hose (and a very conservative C value of 0.8, the required pressure at the 
riser is around 36 psi.
Using he same FDC but flowing 2 - 2.5" outlet and NO hose, the riser pressure 
is around 25 psi.  If you add 100 ft of 2.5" hose, it's around 137 psi

Roland