>From NFPA 22 2012:
14.4.1 A permanent pipe connected to a water supply shall be provided to fill 
the tank, except as provided in 14.4.1.1. 

14.4.1.1 Where a permanent water supply is not available to refill the tank, an 
approved plan shall be permitted for manually refilling the tank.

14.4.1.2 During the time that the tank does not have sufficient capacity to 
meet the demand of the fire protection system(s), the impairment procedures of 
NFPA 25 shall be followed.

I would suggest maybe you consider (required supply GPM for NFPA duration) - 
(flow rate of filling source x 8 hr) reserve water in your pond which all but 
mitigates these requirements anyways, since it sounds like expanding the pond 
isn't out of the question.  In which case your plan would be "if we have a fire 
within 3 days of the first fire we'll hire a company to truck in water and 
evacuate and impair the building per NFPA 25 until the water arrives" and then 
file that plan away under "things that will probably never happen, but just in 
case".
 
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com <http://www.bmwc.com/> 
 

________________________________

From: [email protected] on behalf of Brad 
Casterline
Sent: Fri 5/17/2013 9:13 AM
To: [email protected]
Subject: RE: NFPA 22 2013 Water storage re-fill time.



Thanks Bruce. It is truly out in the sticks. 35 GPM well pump. The designer
is thinking if he made the pond capacity 300,000 gallons, after a 150,000
gallon fire event the required water would be restored in no time,
literally, but it would take 3 days to re-fill the 'tank', and the book says
8 hours max. (the tank A and tank B scenario was my idea, as a way of posing
what I was concerned about). I don't know quite what to think yet, just glad
I am not an A.H.J. :)

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, May 16, 2013 5:17 PM
To: [email protected]
Subject: Re: NFPA 22 2013 Water storage re-fill time.

Brad,

If this tank sits in a place with municipal water, but still needs a tank, I
would say you need to design for 8-hrs.

Start of what if's...

...What if water department will only allow a rate of fill that is 12-hours.
Document well (no pun), and fill tank in twelve.

...What if you are truly in the sticks, and you only have, and can only get,
a 20 gpm well. I think some sort of minimal tank for back up, or rent
temporary tank system during major schedule maintenance, and live within
your means.

Of course, restrict activites during this time.

While you tank is down is not the time for hot work to support new
equipment.

bv
From: "Brad Casterline" <[email protected]>
To: [email protected]
Sent: Thursday, May 16, 2013 11:42:59 AM
Subject: RE: NFPA 22 2013 Water storage re-fill time.

ok good, now then, if you are/were an A.H.J., how would you answer this
question: "How much time do we get to be able to re-fill a water storage
tank in 8 hours"? for example, 150,000 gallon capacity for demand*duration,
say tank A, from which the pump takes suction. Now we build a twin tank B,
and connect to tank A with 8" pipe with a shut-off valve normally closed.
There is an event and tank A runs dry. We open the shut-off valve and tank A

is re-filled in about 18 minutes. The well pump then starts refilling tank
B, which will take 3 days. So the question is "how much time do we get to be

able to re-fill the tank within in 8 hours?".

-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Thursday, May 16, 2013 8:18 AM
To: [email protected]
Subject: NFPA 22 2013 Water storage re-fill time.

asking for a co-worker:



1) Why are water storage tanks required to be re-filled in 8 hours?

2) Would the requirement apply to ponds (man-made with liner in this case)?

3) Are there any alternatives to the requirement?



(the pond is large and filled by a well pump with a pumping rate that would
take more than 8 hours)



many thanks,



Brad Casterline, NICET IV

Fire Protection Division



FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com



Engineering Solutions for the Built Environment



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to