the 4" not flowing full would explain it

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack
Sent: Thursday, July 09, 2015 11:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Water Flow Information

They can't be getting the same readings. It is a reporting error by the user
providing the information. 

I see water authorities reporting flow test data wrong frequently. Many
incorrectly apply or don't apply at all the pumper modification for times
when flowing the pumper outlet. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jul 9, 2015, at 9:16 AM, Chad Matthews <c...@norcalfire.com> wrote:
> 
> That’s what I always thought, it doesn't make sense that they're getting
the same pitot readings out of the 4" that they are the 2.5".
> What am I missing?
> 
> To answer Matt's question, no I don't believe they're flowing them at the
same time.
> 
> 
> Chad Matthews
> Nor-Cal Fire Protection, Inc
> 16840 Joleen Way #A
> Morgan Hill, Ca 95037
> (408)776-1580
> www.norcalfire.com
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis
Mack
> Sent: Thursday, July 09, 2015 9:09 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Water Flow Information
> 
> If static/residual/pitot are the same from 4" and 2.5" ports I would be
questioning the results. A 25 psi pitot on 2.5" and 4" are very different
flows. This would cause for a different residual pressure in most systems. 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On Jul 9, 2015, at 9:06 AM, Chad Matthews <c...@norcalfire.com> wrote:
>> 
>> Is there is specific requirement when receiving water flow data, that 
>> I use the information as it flows from the 2½” outlet of a fire hydrant?
>> 
>> 
>> 
>> I ask because from a certain jurisdiction they give us the water flow 
>> info from the 2½” outlet and the 4” outlet, the static, residual, and 
>> pitot pressures are the same, but there is a big difference in the GPM 
>> which dramatically effects my water flow curve. It’s quite a bit more 
>> GPM when flowed from the 4” outlet. Conservatively speaking, I 
>> recognize it’s safer to design to the smaller supply but I’m having 
>> trouble understanding the difference I guess.
>> 
>> 
>> 
>> Thanks!
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> Chad Matthews
>> 
>> Nor-Cal Fire Protection, Inc
>> 
>> 16840 Joleen Way #A
>> 
>> Morgan Hill, Ca 95037
>> 
>> (408)776-1580
>> 
>> www.norcalfire.com
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to