Mike-
The lines on the other side of the wall only have (3) heads per line.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield
Sent: Tuesday, July 09, 2019 10:36 AM
To: [email protected]
Subject: Re: ESFR Calc's

Why don't you use 2 lines on one side of the wall and 1 line on the other side 
of the wall thus 3 lines with 4 heads?

Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Brian Harris 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 9, 2019 10:29 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR Calc's


I have an ESFR system that I do not have (3) rows of (4) heads to calc. Due to 
compartment wall layouts I have (2) rows of (6) heads and (6) rows of (3) 
heads. What is the best way to grab (12) heads?



Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com<http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935