Do what Mike said but pick up the 12th sprinkler off the 4th line.  I would 
imagine the intent of NFPA 13 was to calculated 4 sprinklers on a line as your 
worst case scenario to prove the line size.  Then pickup 12 sprinklers total to 
get an appropriate total flow.  So the standard reference 3 lines to do this as 
that is the common scenario.

Applying this assumption to your scenario, your 1st two lines have at least 4 
sprinklers per line so those are easy enough.  Your 3rd line only has 3 
sprinklers so pickup all 3 and then pick up the 4th sprinkler on the 4th line.  
You now have 12 total sprinklers flowing, and the last 4 of these sprinklers 
are going to overflow more than they normally would if they were on a single 
line (assuming tree/end fed system).  So this should be a more conservative 
design than what NFPA 13 requires.  But you also aren't forcing yourself to go 
ultra conservative by calculating 5 or 6 sprinklers on a single line which I do 
not believe was NFPA 13's intent.

Thanks,
Sean VG

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, July 9, 2019 7:44 AM
To: [email protected]
Subject: [EXTERNAL] RE: ESFR Calc's

Mike-
The lines on the other side of the wall only have (3) heads per line.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=AWdzKMSnfZTO1yzpl1Dd37Lrr1TeI1Fqx3BWjEHd-Zg&s=QGuUWxAksuh7c7L6oHoglZLzKjOOXn6OYIs8o4Fgsv4&e=>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Mike Hairfield
Sent: Tuesday, July 09, 2019 10:36 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: ESFR Calc's

Why don't you use 2 lines on one side of the wall and 1 line on the other side 
of the wall thus 3 lines with 4 heads?

Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Brian Harris 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 9, 2019 10:29 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR Calc's


I have an ESFR system that I do not have (3) rows of (4) heads to calc. Due to 
compartment wall layouts I have (2) rows of (6) heads and (6) rows of (3) 
heads. What is the best way to grab (12) heads?



Brian Harris, CET

BVS Systems Inc.

Design Manager