This should be put back to the architect or engineer for guidance. When we’ve 
piped exhaust through combustible construction and if I remember correctly it 
did require additional clearances.

Jamie Seidl
Century Fire Protection
3600 Woodpark Blvd., Ste G
Charlotte, NC 28203
P-(704) 888-3473 C-(704) 650-0033
[email protected]

On Sep 5, 2024, at 11:10 PM, Nicky Marshall <[email protected]> wrote:


External Email: ONLY open links/attachments from known safe sources
Help please
There is a building construction trend in New Zealand to use CLT timber rather 
than typical concrete and steel.
We have done sprinkler designs for quite a few CLT buildings now, but we have 
our first one which requires the diesel engine exhaust to penetrate the timber 
wall.  A relatively small engine - Lister Petter LPWT4.

Our standard requires a sleeve design so that the surface of combustible 
material shall not exceed 70°C. (158° F)
The exhaust pipe is 60mm (2.4”)
I am aware of the design in NFPA 211, but looking for something more practical 
than a 460-660mm (18-26”) hole through the wall.
Can anyone help/point me in the direction of someone who can assist with this?

Thanks in advance.

Kind regards

<image002.jpg>
Nicky Marshall
Southern Regional Manager

PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Mobile Phone: +64 (0)21 433 488  Email: 
[email protected]<mailto:[email protected]>  Web: 
www.protechdesign.co.nz<http://www.protechdesign.co.nz/>
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ
<image003.png>
“I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody” Lily Tomlin


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to