Citeren ahouse-support <supp...@ahouse.mine.nu>:

# ./nut start
Network UPS Tools - UPS driver controller 2.4.1
Network UPS Tools - Megatec/Q1 protocol serial driver 1.51 (2.4.1)
Supported UPS detected with megatec protocol
Vendor information read in 1 tries
Battery runtime will not be calculated (runtimecal not set) <================= !!!

RTFM - 'man 8 blazer'.

backup# upsc power...@localhost
battery.voltage: 28.80 <========= !!! it is a normal? what u thing about this value?? iam have 4x7AH battery in Ups

This boils down to about 2.4 V / cell, which is fairly high for a PbAc battery. But please understand that a UPS is not a measuring instrument. More often than not, the reported resolution is much more than the accuracy of the measurement justifies. So unless your batteries wear out quickly, you can safely ignore this.

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)