2011/2/7 Kevin <bakd...@gmail.com>

>  On 06/02/2011 21:42, Kevin wrote:
>
> on 06/02/2011 21:06 Charles Lepple wrote:
>
>
> It looks like the only uncommented code which talks to the device is
> the last line. (The results from the getval() calls do not seem to be
> used.)
>
> APCDelayBeforeReboot maps to 0xff86007c, so Arjen's suggestion to
> change the 10 to 1 should be equivalent to the setvalue() line at the
> end.
>
>
> Thanks for the input Charles. I will post back the results tomorrow.
>
>
> Ok, I've tried that. The result of "clientcmd -u apcmon -p pass123 -a
> apc1500 shutdown.reboot" is nothing. Nothing that I can see changes at all.
>
> I did this with the old working modified hidups driver:
>
> # ./hidups -DDD -k /dev/hiddev0
> Network UPS Tools: HID UPS driver 0.13 (2.0.0)
>
> Warning: This is an experimental driver.
> Some features may not function correctly.
>
> debug level is '3'
> Detected American Power Conversion Back-UPS CS 500 FW:808.q10 .I USB FW:q10
> on port /dev/hiddev0
> Initiating UPS shutdown
> setvalue(ff86007c, 1): obtained 0 (report 40))
> setvalue(using type = feature): report sent successfully
>
>
> Something must be different! Is the "type = feature" relevant at all?
>
> There are three lines in the apc-hid.c code that reference shutdown.reboot:
>
>
>    1. { "shutdown.reboot", 0, 0, "UPS.PowerSummary.DelayBeforeReboot",
>    NULL, "10", HU_TYPE_CMD, NULL },
>    2. { "shutdown.reboot", 0, 0, "UPS.Output.DelayBeforeReboot", NULL,
>    "10", HU_TYPE_CMD, NULL },
>    3. { "shutdown.reboot", 0, 0,
>    "UPS.APCGeneralCollection.APCDelayBeforeReboot", NULL, "1", HU_TYPE_CMD,
>    NULL },
>
>
> I did "usbhid-ups -a apc1500 -k -DDD > CS500shutdown.txt 2>&1" and attached
> the output in case it holds any clues.
>

according to your attached output, shutdown.reboot has been mapped on
UPS.PowerSummary.DelayBeforeReboot

You should try putting the above last line
(UPS.APCGeneralCollection.APCDelayBeforeReboot) before all the other
possible paths (ie 3 before 1 and 2 in apc-hid.c), recompile and try again
your procedure.
The rule for the generic USB/HID engine is that the first HID path that
exist is used to map the NUT variable, in case multiple HID paths can
satisfy it.

cheers,
Arnaud
-- 
Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/