Hello all, I have a CyberPower Systems CP850PFCLCD that I'm hooking up to NUT 2.4.3 from apt running under Ubuntu 10.04. Using the usbhid-ups driver, things *seem* to work at first glance, but there are some odd issues. The most notable issue is that the battery.charge indicator reads 120 when at full charge. I came across this post here: http://lists.alioth.debian.org/pipermail/nut-upsuser/2007-September/003222.htmlbut it looks like the user never supplied the necessary data.
The other issue that I found was that the LB flag is sent way to early when I unplugged the UPS from the outlet. I captured a log of upsc polling every 5 seconds and I'm attaching to this message. I'm more than happy to supply debug output, but I don't know if you want me to unplug the UPS from the outlet during that debug or not. Thanks in advance for any help, Justin ------------ ue Mar 29 23:30:39 CDT 2011 battery.charge: 120 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 450 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 117.0 input.voltage.nominal: 120 output.voltage: 117.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OL ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:30:44 CDT 2011 battery.charge: 105 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 367 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:30:49 CDT 2011 battery.charge: 96 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 360 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:30:54 CDT 2011 battery.charge: 96 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 360 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:30:59 CDT 2011 battery.charge: 87 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 304 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:04 CDT 2011 battery.charge: 87 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 304 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:09 CDT 2011 battery.charge: 83 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 290 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:14 CDT 2011 battery.charge: 81 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 283 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: OB DISCHRG LB ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:19 CDT 2011 battery.charge: 79 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 276 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: FSD OB DISCHRG LB ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:24 CDT 2011 battery.charge: 78 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 253 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: FSD OB DISCHRG LB ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:29 CDT 2011 battery.charge: 74 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 222 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: FSD OB DISCHRG LB ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Tue Mar 29 23:31:34 CDT 2011 battery.charge: 74 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 222 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP850PFCLCD device.model: CRDA103.981 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.34 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 0.0 input.voltage.nominal: 120 output.voltage: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 56 ups.mfr: CP850PFCLCD ups.model: CRDA103.981 ups.productid: 0501 ups.realpower.nominal: 510 ups.serial: CPS ups.status: FSD OB DISCHRG LB ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764
_______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser