Re: [Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

2024-04-24 Thread tim.o via Nut-upsuser

On 4/24/24 18:06, Charles Lepple wrote:

My guess is that if you sent 520, upsc would return 8 (for a revised
maximum of 511 seconds). If not, the UPS is even weirder than most 

As you found, the ignorelb option is available to work around
limitations in the UPS shutdown logic.


I can confirm

upsrw -s battery.runtime.low=520 -w CST150UC@localhost
battery.runtime.low: 8

I also tried

upsrw -s battery.runtime.low=480 -w CST150UC@localhost
battery.runtime.low: 480

upsrw -s battery.runtime.low=540 -w CST150UC@localhost
battery.runtime.low: 28

I guess none of this makes any sense to me so maybe the ignorelb option 
is the way to go unless you have a suggestion as to what value to use 
with upsrw -s battery.runtime.low, lol.


This seems to work though

mcedit /etc/nut/nut.conf
[CST150UC]
driver = usbhid-ups
port = auto
ignorelb
ondelay = -1
override.battery.runtime.low = 3600

upsc CST150UC@localhost
battery.runtime.low: 3600 (system will shutdown when 60 minutes of 
runtime is left)

ups.delay.start: -1 (never powers on the load, even when main power returns)

Thank you
___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

2024-04-24 Thread Charles Lepple via Nut-upsuser
On Apr 24, 2024, at 3:45 PM, tim.o via Nut-upsuser 
 wrote:
>> Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is 
>> quite possible the UPS is using an 8-bit field to store battery.runtime.low. 
>> I'm guessing the maximum is going to be 255.
>> 
> I am not sure I follow. Would you mind unpacking this for me?
> When I initially issued 'upsrw' this is what was returned. What does the 
> value '300' indicate, if not seconds;

Confirmed, it's seconds. (The maximum length for that field is just the number 
of digits that the driver is prepared to accept as a string, but it just 
converts them to a number to send to the UPS.)

> and attempting to change it to '3600' sets it two '16'. Is this what you mean 
> when you're referring to a '8-bit field'?

Yes, sorry, I missed the default of 300, and I was mixing bits and hexadecimal. 
At least 9 bits are needed to represent 300 decimal.

Let's say the UPS stores the runtime in 9 bits, and consider what would happen 
if you send 3600:

3600 decimal = 1110 0001  binary

Low 9 bits = ___0 0001  binary = 16 decimal

(note that 0 and -1 may have special meaning to the UPS, but this will probably 
hold true for other values)

My guess is that if you sent 520, upsc would return 8 (for a revised maximum of 
511 seconds). If not, the UPS is even weirder than most :-)

As you found, the ignorelb option is available to work around limitations in 
the UPS shutdown logic.

-- 
Charles Lepple
clepple@gmail


___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

2024-04-24 Thread tim.o via Nut-upsuser

Unfortunately, the SUCCESS response is just saying that upsrw was able to send 
that request to upsd (i.e. the username/password were correct). As you saw, the 
real proof is in what you read back from upsc.

Ah, gotcha.


Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is 
quite possible the UPS is using an 8-bit field to store battery.runtime.low. 
I'm guessing the maximum is going to be 255.

I am not sure I follow. Would you mind unpacking this for me?
When I initially issued 'upsrw' this is what was returned. What does the 
value '300' indicate, if not seconds; and attempting to change it to 
'3600' sets it two '16'. Is this what you mean when you're referring to 
a '8-bit field'?


upsrw CST150UC
            [battery.runtime.low]
        Remaining battery runtime when UPS switches to LB (seconds)
        Type: STRING
        Maximum length: 10
        Value: 300

In my research I found that editing 'ups.conf' may allow to change the 
'battery.runtime.low' as well, but I haven't tested it yet. I figured 
using the supported UPS variables may be the way to go first.


mcedit /etc/nut/ups.conf

[cyberpower]
    driver = usbhid-ups
    port = auto
    desc = "ups"
    offdelay = 20
    ondelay = 0
    ignorelb
    override.battery.runtime.low = 20
    override.battery.runtime.low = 40
    pollinterval = 15

Thank you, Charles

On 4/24/24 04:19, Charles Lepple wrote:

On Apr 23, 2024, at 3:51 PM, tim.o via 
Nut-upsuser  wrote:

The value changed to battery.runtime.low: 16, instead of 3600. I don't 
understand why, because executing the command resulted in SUCCESS.

Unfortunately, the SUCCESS response is just saying that upsrw was able to send 
that request to upsd (i.e. the username/password were correct). As you saw, the 
real proof is in what you read back from upsc.

Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is 
quite possible the UPS is using an 8-bit field to store battery.runtime.low. 
I'm guessing the maximum is going to be 255.

This is not entirely surprising - we have a GitHub issue label specific to CPS 
for issues with their USB HID protocol implementation.
___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

2024-04-24 Thread Charles Lepple via Nut-upsuser
> On Apr 23, 2024, at 3:51 PM, tim.o via Nut-upsuser 
>  wrote:
> 
> The value changed to battery.runtime.low: 16, instead of 3600. I don't 
> understand why, because executing the command resulted in SUCCESS.

Unfortunately, the SUCCESS response is just saying that upsrw was able to send 
that request to upsd (i.e. the username/password were correct). As you saw, the 
real proof is in what you read back from upsc.

Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is 
quite possible the UPS is using an 8-bit field to store battery.runtime.low. 
I'm guessing the maximum is going to be 255.

This is not entirely surprising - we have a GitHub issue label specific to CPS 
for issues with their USB HID protocol implementation.

-- 
Charles Lepple
clepple@gmail