That is going to be hard to diagnose without the usbhid-ups logs for the time when those 
commands are sent - can you try to keep the log going while sending them, then note the 
time when the command was sent? You can use the "tee" command:

/lib/nut/usbhid-ups -DD -a TrippLiteUPS 2>&1 | tee /tmp/log.shutdown.return.txt

(please use gzip before attaching the log - the mailing list does not accept 
messages over 40kB without manual intervention.)



Sorry, I think there was a mistake on my part and for the large messages :)

When I originally tried to run "/lib/nut/usbhid-ups -DD -a TrippLiteUPS" 
It complained about other drivers running and did not show any logging 
of commands given to the driver. So I have been now stopping nut-driver 
before running that command. After starting the logging then running 
both upsrw and upscmd I would ctl+c the logging leaving no driver 
running. I now realize that only a little while after canceling the 
logging is when NUT decided to shut down the server.If I leave the 
logging going it does not shutdown.


I am assuming that is supposed to do that when no driver is seen running 
for awhile just incase?? And in that case is not part of my original no 
delay issue?


I have run it again and it looks like ups.shutdown.delay changes show in 
the log @ 28.068836. But no mention at all in the log of shutdown.return 
run @ 80.951272. Just the same "ERR CMD-NOT-SUPPORTED" when attempting 
to run it.




I think the load.off.delay behavior is expected, but I really thought the 
others should honor the delay variables. Will have to look further.
log trimmed; appears to be the same as before?



Yes looks about the same. Also I did a test on new installs of debian 8 
and debian 9. Both worked as expected except for the delay variables are 
still being ignored and "ERR CMD-NOT-SUPPORTED" when running "upscmd 
TrippLiteUPS@localhost shutdown.return".


NOTE: The issue of having to add a systemd service in my first post 
seems to be a proxmox issue, so I will look into that issue else where.


log.shutdown.return.txt.gz
Description: application/gzip
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] TrippLite SMART1500LCD no delay before ups shutdown.

2017-08-21 Thread Charles Lepple
On Aug 21, 2017, at 1:35 PM, Whiteshell Tech  wrote:
> 
> I ran it again on battery and upsd running, set upsrw ok and then 
> shutdown.return gave an "ERR CMD-NOT-SUPPORTED" Odd thing is after running 
> that I am getting random timed ups powering off for one or two seconds then 
> turns back on even on battery. Server then starts shutting down. Some times 
> its right away sometimes after 4+ minutes.

That is going to be hard to diagnose without the usbhid-ups logs for the time 
when those commands are sent - can you try to keep the log going while sending 
them, then note the time when the command was sent? You can use the "tee" 
command:

/lib/nut/usbhid-ups -DD -a TrippLiteUPS 2>&1 | tee /tmp/log.shutdown.return.txt

(please use gzip before attaching the log - the mailing list does not accept 
messages over 40kB without manual intervention.)

> I did notice that that return.shutdown was not found in the list running 
> "upscmd -l TrippLiteUPS". I did see "load.off.delay" which also if I give a 
> value of 60 (or any other value) it shuts down in 20sec and stays off either 
> on battery or online. ups does come back on if i replug the ups.

I think the load.off.delay behavior is expected, but I really thought the 
others should honor the delay variables. Will have to look further.

> 
> 
> I am setting up a test computer with fresh Debian 9 for testing to see if all 
> my issues are still there without every thing else.
> 
> Thanks for taking the time when you have some.
> 
> 
> root@host:~# upscmd -l TrippLiteUPS
> Instant commands supported on UPS [TrippLiteUPS]:
> 
> beeper.disable - Disable the UPS beeper
> beeper.enable - Enable the UPS beeper
> beeper.mute - Temporarily mute the UPS beeper
> beeper.off - Obsolete (use beeper.disable or beeper.mute)
> beeper.on - Obsolete (use beeper.enable)
> load.off - Turn off the load immediately
> load.off.delay - Turn off the load with a delay (seconds)
> reset.watchdog - Reset watchdog timer
> shutdown.reboot - Shut down the load briefly while rebooting the UPS
> shutdown.stop - Stop a shutdown in progress
> test.battery.start.deep - Start a deep battery test
> test.battery.start.quick - Start a quick battery test
> test.battery.stop - Stop the battery test
> 
> 
> 
> root@host:~# upsrw -s ups.delay.shutdown=60 TrippLiteUPS@localhost
> Username (root): upsmon
> Password:
> OK
> 
> root@host:~# upscmd TrippLiteUPS shutdown.return
> Username (root): upsmon
> Password:
> Unexpected response from upsd: ERR CMD-NOT-SUPPORTED
> 

log trimmed; appears to be the same as before?




___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] TrippLite SMART1500LCD no delay before ups shutdown.

2017-08-21 Thread Whiteshell Tech

On Aug 21, 2017, at 12:45 AM, Whiteshell Tech  wrote:

I have attempted to set the delay higher using "upsrw -s ups.delay.shutdown=120 
TrippLiteUPS@localhost" and confirmed the value with "upsc TrippLiteUPS@localhost" 
Still the UPS switches off right away.

Due to the way that the HID PDC shutdown sequence works, the value you see from 
"upsc ups.delay.shutdown" is just a variable in the driver. It does not write 
that to the UPS until the delayed shutdown command is sent, since the shutdown timer in 
the UPS starts when that value is written.

That makes sense. Thanks for pointing that out I did not realize that.

That said, it looks like the TrippLite HID mappings (in v2.7.4 as well as master) are 
missing the "shutdown.return" command. I'd look into it further, but 
ironically, the local power company has scheduled maintenance coming up soon, and I am 
typing this on a machine with a Tripp Lite UPS that doesn't play well with NUT. Should 
have more time later today or this week.


At first after installing the debian nut packages with apt-get and setting up the config 
files I had to setup a systemd service to exeu "upsdrvctl shutdown" on shutdown 
or else the ups would not turn off at all. Now after setting up that service is when I 
discovered the issue, that the ups does not delay in shutting down.


This sounds like a bug in the Debian packaging (or Proxmox? Not sure where the 
dividing line is.) Can you check their bug trackers?
Okay, I will check the bug trackers. Also I will setup a fresh Debian 9 
install on another system and see if the problem still happens.


Thanks, Good luck with the power company. :)

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] TrippLite SMART1500LCD no delay before ups shutdown.

2017-08-21 Thread Charles Lepple
On Aug 21, 2017, at 8:33 AM, Charles Lepple  wrote:
> 
> That said, it looks like the TrippLite HID mappings (in v2.7.4 as well as 
> master) are missing the "shutdown.return" command. I'd look into it further, 
> but ironically, the local power company has scheduled maintenance coming up 
> soon, and I am typing this on a machine with a Tripp Lite UPS that doesn't 
> play well with NUT. Should have more time later today or this week.

My mistake, should be handled by the main driver code here:

https://github.com/networkupstools/nut/blob/v2.7.4/drivers/usbhid-ups.c#L558-L583

Can you grab a log as before, but with upsd running? You can send the upsrw 
command to set the timer, then get upscmd to run the "shutdown.return" command 
(might need to be on battery for this to work). It might also be best to power 
the server from another outlet or UPS.
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] TrippLite SMART1500LCD no delay before ups shutdown.

2017-08-21 Thread Charles Lepple
[when responding, please use reply-all - the list does not mangle the reply-to 
header]

> On Aug 21, 2017, at 12:45 AM, Whiteshell Tech  
> wrote:
> 
> I have attempted to set the delay higher using "upsrw -s 
> ups.delay.shutdown=120 TrippLiteUPS@localhost" and confirmed the value with 
> "upsc TrippLiteUPS@localhost" Still the UPS switches off right away.

Due to the way that the HID PDC shutdown sequence works, the value you see from 
"upsc ups.delay.shutdown" is just a variable in the driver. It does not write 
that to the UPS until the delayed shutdown command is sent, since the shutdown 
timer in the UPS starts when that value is written.

That said, it looks like the TrippLite HID mappings (in v2.7.4 as well as 
master) are missing the "shutdown.return" command. I'd look into it further, 
but ironically, the local power company has scheduled maintenance coming up 
soon, and I am typing this on a machine with a Tripp Lite UPS that doesn't play 
well with NUT. Should have more time later today or this week.

> At first after installing the debian nut packages with apt-get and setting up 
> the config files I had to setup a systemd service to exeu "upsdrvctl 
> shutdown" on shutdown or else the ups would not turn off at all. Now after 
> setting up that service is when I discovered the issue, that the ups does not 
> delay in shutting down. 
> 
This sounds like a bug in the Debian packaging (or Proxmox? Not sure where the 
dividing line is.) Can you check their bug trackers?
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


[Nut-upsuser] TrippLite SMART1500LCD no delay before ups shutdown.

2017-08-21 Thread Whiteshell Tech

Hello,

I am hoping someone can point me in the right direction. I am setting up 
a new UPS, most things seem to be working except the UPS turns off 
immediately during a test shutdown using///"//upsmon -c fsd".//No delay 
before the UPS turns itself off leaving no time for the server to 
shutdown properly.


I have attempted to set the delay higher using "upsrw -s 
ups.delay.shutdown=120 TrippLiteUPS@localhost" and confirmed the value 
with "upsc ///TrippLiteUPS@localhost/" Still the UPS switches off right 
away.


At first after installing the debian nut packages with apt-get and 
setting up the config files I had to setup a systemd service to exeu 
"upsdrvctl shutdown" on shutdown or else the ups would not turn off at 
all. Now after setting up that service is when I discovered the issue, 
that the ups does not delay in shutting down.


Only occasional errors in syslog I can see are
"upsd[1018]: fopen /var/run/nut/upsd.pid: No such file or directory"
and
"systemd[1]: nut-monitor.service: PID file /var/run/nut/upsmon.pid not 
readable (yet?) after start: No such file or directory"

Might be just because services are slow to start?


Some details:

TrippLite SMART1500LCD
Dell PowerEdge T130


Proxmox on Debian 9
Linux host 4.10.17-2-pve #1 SMP PVE 4.10.17-20 (Mon, 14 Aug 2017 
11:23:37 +0200) x86_64 GNU/Linux



root@host:~# upsd -V
Network UPS Tools upsd 2.7.4


root@host:~# lsusb | grep "Tripp Lite"
Bus 001 Device 002: ID 09ae:2012 Tripp Lite


root@host:~# cat /etc/nut/nut.conf
MODE=standalone


root@host:~# cat /etc/nut/ups.conf
[TrippLiteUPS]
driver = usbhid-ups
port = auto
vendorid = 09ae
productid = 2012
desc = "Proxmox server"
offdelay = 120
ondelay = 140


root@host:~# cat /etc/nut/upsd.conf
LISTEN 127.0.0.1 3493
LISTEN ::1 3493


root@host:~# cat /etc/nut/upsd.users
[upsmon]
password = password
upsmon master
actions = SET
instcmds = ALL


root@host:~# cat /etc/nut/upsmon.conf
MINSUPPLIES 1
SHUTDOWNCMD "/sbin/shutdown -h +0"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5
MONITOR TrippLiteUPS@localhost 1 upsmon password master
NOTIFYFLAG COMMBAD  SYSLOG+EXEC
NOTIFYFLAG COMMOK   SYSLOG+EXEC
NOTIFYFLAG FSD  SYSLOG+WALL+EXEC
NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC


root@host:~# cat /etc/nut/upssched.conf
CMDSCRIPT /bin/upssched-cmd


root@host:~# cat /etc/systemd/system/nut-delayed-ups-shutdown.service
 [Unit]
 Description=Initiate delayed UPS shutdown
 Before=umount.target
 DefaultDependencies=no

 [Service]
 Type=oneshot
 ExecStart=/usr/bin/logger -t upsdrvctl 
"nut-delayed-ups-shutdown.service calling upsdrvctl to shut down UPS unit"

 ExecStart=/sbin/upsdrvctl shutdown

 [Install]
 WantedBy=final.target


root@host:~# upsc TrippLiteUPS
Init SSL without certificate database
battery.charge: 100
battery.runtime: 3840
battery.type: PbAC
battery.voltage: 27.1
battery.voltage.nominal: 24.0
device.mfr: Tripp Lite
device.model: Tripp Lite UPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 120
driver.parameter.ondelay: 140
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 2012
driver.parameter.synchronous: no
driver.parameter.vendorid: 09ae
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 59.9
input.voltage: 116.2
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage: 116.2
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 120
ups.load: 0
ups.mfr: Tripp Lite
ups.model: Tripp Lite UPS
ups.power: 0.0
ups.power.nominal: 1500
ups.productid: 2012
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0


root@host:~# /lib/nut/usbhid-ups -DD -a TrippLiteUPS
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.00debug level is '2'
   0.000242upsdrv_initups...
   0.115372Checking device (1D6B/0003) (002/001)
   0.115817- VendorID: 1d6b
   0.115821- ProductID: 0003
   0.115822- Manufacturer: unknown
   0.115824- Product: unknown
   0.115825- Serial Number: unknown
   0.115826- Bus: 002
   0.115827- Device release number: 0410
   0.115829Trying to match device
   0.115832Device does not match - skipping
   0.115835Checking device (09AE/2012) (001/007)
   0.119620- VendorID: 09ae
   0.119625- ProductID: 2012
   0.119626- Manufacturer: Tripp Lite
   0.119627- Product: Tripp Lite UPS
   0.119629- Serial Number: unknown
   0.119630- Bus: 001
   0.119631- Device release number: 0009
   0.119632Trying to match device
   0.119646Device matches