[Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri
Hi,

I have two types of UPS devices and one of them (APC) gave me a false low 
battery alert. I can't reproduce the problem... Also, there was nothing 
apparently wrong with the UPS at the time of the false alert. All I could do 
was grab the driver values within a minute after the low battery notification.

These are the values:

battery.runtime.low : 120
 
battery.voltage : 55.65
 
battery.voltage.nominal : 048
 
device.mfr : APC
 
device.model : SMART-UPS 5000 RM DL4
 
device.serial : CS0603110575
 
device.type : ups
 
driver.name : apcsmart
 
driver.parameter.pollinterval : 2
 
driver.parameter.port : /dev/UPS-1
 
driver.version : 2.6.3
 
driver.version.internal : 3.0
 
input.frequency : 50.00
 
input.quality : FF
 
input.sensitivity : H
 
input.transfer.high : 253
 
input.transfer.low : 196
 
input.transfer.reason : simulated power failure or UPS test 

input.voltage : 224.9
 
input.voltage.maximum : 224.9
 
input.voltage.minimum : 223.6
 
output.voltage : 224.9
 
output.voltage.nominal : 230
 
ups.delay.shutdown : 020
 
ups.delay.start : 000
 
ups.firmware : 112.1DL4.I
 
ups.id : UPS_IDEN
 
ups.load : 069.6
 
ups.mfr : APC
 
ups.mfr.date : 01/10/06
 
ups.model : SMART-UPS 5000 RM DL4
 
ups.serial : CS0603110575
 
ups.status : OL
 
ups.temperature : 027.4
 
ups.test.interval : 1209600
 
ups.test.result : NO 

The NUT version installed is 2.6.3 and I'm using a serial-to-USB hub (1 usb 
port and 4 serial ports). The brand is ATEN,

My upssched.conf contains:
AT LOWBATT INF-APC@127.0.0.1 EXECUTE lowbatt-now-apc
and my upssched custom script notified me of the LOWBATT event.

My ups.conf contains:

[INF-APC]
driver = apcsmart
port = /dev/UPS-1
desc = UPS Monitor - ATEN port 2 - APC UPS

If I were to update to nut 2.6.5 (I can't do it for now) would I solve this 
issue (ie. is it a known issue?)?

Thanks,

Vieri



___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


[Nut-upsuser] NUT on Windows Clients

2013-02-28 Thread Ilia Shapira
I want to try to use NUT on Linux server, but most of the servers I need to
shutdown are Windows.

Before I try to install I wanted to ask you how stable is the Windows Beta
of NUT ?

I need only the client part of the Windows port, only to shut down the
Windows servers

 

 

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] NUT on Windows Clients

2013-02-28 Thread Douglas Parsons
Although I am not on the latest version, actually it has been two years
since I upgraded, I have several Windows clients running against a Linux
master that monitors multiple UPS units.
On Feb 28, 2013 4:12 AM, Ilia Shapira i...@logicnet.co.il wrote:

 I want to try to use NUT on Linux server, but most of the servers I need
 to shutdown are Windows.

 Before I try to install I wanted to ask you how stable is the Windows Beta
 of NUT ?

 I need only the client part of the Windows port, only to shut down the
 Windows servers

 ** **

 ** **

 ___
 Nut-upsuser mailing list
 Nut-upsuser@lists.alioth.debian.org
 http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Charles Lepple
On Feb 28, 2013, at 4:10 AM, Vieri wrote:

 input.transfer.reason : simulated power failure or UPS test 

Sounds like it was the UPS self test?

 ups.mfr.date : 01/10/06

If this is the original battery, it is certainly possible that it has built up 
enough internal resistance that the voltage reads normal when idle, but it dips 
too low during a test.

 ups.test.interval : 1209600

1209600 seconds = 14 days, so if it does it again in two weeks...

-- 
Charles Lepple
clepple@gmail




___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri


--- On Thu, 2/28/13, Charles Lepple clep...@gmail.com wrote:

 wrote:
 
  input.transfer.reason : simulated power failure or UPS
 test 
 
 Sounds like it was the UPS self test?
 
  ups.mfr.date : 01/10/06
 
 If this is the original battery, it is certainly possible
 that it has built up enough internal resistance that the
 voltage reads normal when idle, but it dips too low during a
 test.
 
  ups.test.interval : 1209600
 
 1209600 seconds = 14 days, so if it does it again in two
 weeks...

Thanks for the explanation.

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri


--- On Thu, 2/28/13, Charles Lepple clep...@gmail.com wrote:

  ups.mfr.date : 01/10/06
 
 If this is the original battery, it is certainly possible
 that it has built up enough internal resistance that the
 voltage reads normal when idle, but it dips too low during a
 test.

BTW, would you suggest changing the battery or is it an overreaction?

Thanks,

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Manuel Wolfshant

On 02/28/2013 04:12 PM, Vieri wrote:


--- On Thu, 2/28/13, Charles Lepple clep...@gmail.com wrote:


ups.mfr.date : 01/10/06

If this is the original battery, it is certainly possible
that it has built up enough internal resistance that the
voltage reads normal when idle, but it dips too low during a
test.

BTW, would you suggest changing the battery or is it an overreaction?
Good batteries ( for instance Yaesu, as seen in APC UPSes ) last 4 
years. Normal ( usual ) ones last 2. Do the math yourself


Manuel

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri

--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro wrote:

 Good batteries ( for instance Yaesu, as seen in APC UPSes )
 last 4 
 years. Normal ( usual ) ones last 2. Do the math yourself

Thanks for that information.
Just a side question:
Will the ups.mfr.date value be updated automatically by the APC ups firmware 
when I change the battery or will I need to set it manually? I'm asking because 
I'm not sure if the current battery was really installed at the time indicated 
by this field.

I also have another (maybe related) problem. I have another 2 APC devices I'd 
like to monitor (apparently same model and serial numbers). However, whenever I 
connect a serial cable to the port on the UPS, the whole device shuts down 
immediately. This happens only if I connect the other end of the serial cable 
to either a ttyS0 port on a running motherboard or a port on a rs232-to-usb 
adapter (even if the usb end ISN'T connected to a NUT monitoring server). What 
could be happening here?
This is obviously slightly off-topic because it doesn't seem to be related to 
the nut ups drivers.
I'm just wondering what could be happening and if old batteries on relatively 
high load (approx. 75%) could be a reason the UPS shuts down abruptly on 
connecting a serial cable on both ends. IT sounds really strange though.
Also, the UPS won't switch on while the serial cable is connected even if I 
press the UPS power-on button several times.
I have to disconnect it (or at least the far end of it) in order to boot the 
ups.

Thoughts greatly appreciated.

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Kris Jordan

Vieri wrote, On 2/28/2013 9:41 AM:

--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro wrote:


Good batteries ( for instance Yaesu, as seen in APC UPSes )
last 4
years. Normal ( usual ) ones last 2. Do the math yourself

Thanks for that information.
Just a side question:
Will the ups.mfr.date value be updated automatically by the APC ups firmware 
when I change the battery or will I need to set it manually? I'm asking because 
I'm not sure if the current battery was really installed at the time indicated 
by this field.


Where APC has provided a value for battery mfg date, it has always been 
the same as the UPS mfg date. The value isn't automatically updated and 
NUT doesn't (from what I've seen) provide a way to update it manually.


Before getting new batteries, you might want to check the float voltage 
with a good multimeter. 55.65 is rather high (~2.32/cell), but I 
wouldn't trust what the UPS says. Smart-UPS's can be bad about 
overcharging their batteries. It can be adjusted by software in some cases.



I also have another (maybe related) problem. I have another 2 APC devices I'd 
like to monitor (apparently same model and serial numbers). However, whenever I 
connect a serial cable to the port on the UPS, the whole device shuts down 
immediately. This happens only if I connect the other end of the serial cable 
to either a ttyS0 port on a running motherboard or a port on a rs232-to-usb 
adapter (even if the usb end ISN'T connected to a NUT monitoring server). What 
could be happening here?
This is obviously slightly off-topic because it doesn't seem to be related to 
the nut ups drivers.
I'm just wondering what could be happening and if old batteries on relatively 
high load (approx. 75%) could be a reason the UPS shuts down abruptly on 
connecting a serial cable on both ends. IT sounds really strange though.
Also, the UPS won't switch on while the serial cable is connected even if I 
press the UPS power-on button several times.
I have to disconnect it (or at least the far end of it) in order to boot the 
ups.


Are you using APC's supplied serial cable? They have special wiring and 
it varies depending on UPS model.


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri


--- On Thu, 2/28/13, Kris Jordan nut...@sagebrushnetworks.com wrote:

 Are you using APC's supplied serial cable? They have special
 wiring and it varies depending on UPS model.

The 3 APC ups devices are identical (same model/serial number) and I'm 
successfully monitoring one of them with a serial cable connected to an 
RS232-USB adapter. I'm using the exact same serial cable (checked the pin 
layout) and the other 2 are dying on me. I DON'T have the original cables 
because these ups devices were already installed when I got there and noone 
bothered storing those cables somewhere. Maybe I could find the serial cable 
pin outs on the manufacturer's web site but I'm supposing the cable I'm using 
is fine since it's working with an identical model.

Nevertheless I'll take some extra time to search for the ups cables just in 
case I do find them and they really are different.

Thanks for the hint.

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Manuel Wolfshant

On 02/28/2013 07:55 PM, Kris Jordan wrote:

Vieri wrote, On 2/28/2013 9:41 AM:

--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro wrote:


Good batteries ( for instance Yaesu, as seen in APC UPSes )
last 4
years. Normal ( usual ) ones last 2. Do the math yourself

Thanks for that information.
Just a side question:
Will the ups.mfr.date value be updated automatically by the APC ups 
firmware when I change the battery or will I need to set it manually? 
I'm asking because I'm not sure if the current battery was really 
installed at the time indicated by this field.


Where APC has provided a value for battery mfg date, it has always 
been the same as the UPS mfg date. The value isn't automatically 
updated and NUT doesn't (from what I've seen) provide a way to update 
it manually.

I had to use apctest from the apcupsd suite to do that




Before getting new batteries, you might want to check the float 
voltage with a good multimeter. 55.65 is rather high (~2.32/cell), but 
I wouldn't trust what the UPS says. Smart-UPS's can be bad about 
overcharging their batteries. It can be adjusted by software in some 
cases.


I also have another (maybe related) problem. I have another 2 APC 
devices I'd like to monitor (apparently same model and serial 
numbers). However, whenever I connect a serial cable to the port on 
the UPS, the whole device shuts down immediately. This happens only 
if I connect the other end of the serial cable to either a ttyS0 port 
on a running motherboard or a port on a rs232-to-usb adapter (even if 
the usb end ISN'T connected to a NUT monitoring server). 
my APC SmartUPS 1000 -/SU1000I/ shuts down the very instant I connect it 
to my workstation using a serial cable that I had handy ( received 
together with a switch ). I guess that the incorrect wiring makes the 
UPS go nuts.



What could be happening here?
This is obviously slightly off-topic because it doesn't seem to be 
related to the nut ups drivers.
I'm just wondering what could be happening and if old batteries on 
relatively high load (approx. 75%) could be a reason the UPS shuts 
down abruptly on connecting a serial cable on both ends. IT sounds 
really strange though.
Also, the UPS won't switch on while the serial cable is connected 
even if I press the UPS power-on button several times.
I have to disconnect it (or at least the far end of it) in order to 
boot the ups.


Are you using APC's supplied serial cable? They have special wiring 
and it varies depending on UPS model.


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri


--- On Thu, 2/28/13, Ben Kamen bka...@benjammin.net wrote:

 No. The mfr date is a constant.
 
 There IS a user modifiable field for the last battery
 changeout date. It's only edited by you (the user/admin)

OK, thanks. I'll look for it.

 You batteries have died.

If I cut the main power supply then the UPS batteries seem to work fine and 
serve the devices behind it for a few minutes (normal load: 75%).
I'm not an expert in this field so I don't understand why the batteries die 
when connecting a serial cable but don't die when they're not powered anymore 
and the UPS is on battery. Maybe it's a wiring/short circuit issue or maybe 
it really is related to the batteries or both.

 It's wise to run a calibration once or twice a month with a
 self test filling in the weeks between (maybe once a week).

I did more then a self test. I cut the main power off. But I'll perform another 
one soon just to make sure the batteries are ok.

Thanks for all the feedback.

Vieri



___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


[Nut-upsuser] (no subject)

2013-02-28 Thread Will Sutton
I am working with a Middle Atlantic IP controllable UPS. I have found that
it is made by CyberPower and is controlled via SNMP. There are some
controls using the auto SNMP driver that do not show up with uspcmd -l
$UPSNAME. Is there a way to use a manufacturer supplied .mib file to
control this piece?
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri

--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro wrote:

 my APC SmartUPS 1000 -SU1000I shuts down
  the very instant I connect it to my workstation using a
serial cable that I had handy ( received together with a switch ). I
guess that the incorrect wiring makes the UPS go nuts.

Ah... great, well sort of. At least now I know it could be a serial cable 
wiring issue. Still, I can't understand why the serial cable I'm using on 1 APC 
model works fine but if I use that same cable on another (identical) APC then 
it shuts down immediately. (I double-checked model name and serial numbers 
behind the UPS devices)
Anyway, I'll try to get the official serial cables just to rule out wiring 
issues.

Thanks for helping.

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Kris Jordan

Ben Kamen wrote, On 2/28/2013 10:08 AM:

On 2013-02-28 11:55 AM, Kris Jordan wrote:

Vieri wrote, On 2/28/2013 9:41 AM:

--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro wrote:

Will the ups.mfr.date value be updated automatically by the APC ups 
firmware when I change the battery or will I need to set it 
manually? I'm asking because I'm not sure if the current battery was 
really installed at the time indicated by this field.


Where APC has provided a value for battery mfg date, it has always 
been the same as the UPS mfg date. The value isn't automatically 
updated and NUT doesn't (from what I've seen) provide a way to update 
it manually.




The Nut Gnome client does allow updating the battery changeout value.

the field in question is: battery.date


I've only seen it as a read-only value (not in upsrw). Have you tried 
changing it in that client?


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Kris Jordan

Ben Kamen wrote, On 2/28/2013 11:52 AM:

On 2013-02-28 1:48 PM, Kris Jordan wrote:

Ben Kamen wrote, On 2/28/2013 10:08 AM:

On 2013-02-28 11:55 AM, Kris Jordan wrote:

Vieri wrote, On 2/28/2013 9:41 AM:
--- On Thu, 2/28/13, Manuel Wolfshant wo...@nobugconsulting.ro 
wrote:


Will the ups.mfr.date value be updated automatically by the APC 
ups firmware when I change the battery or will I need to set it 
manually? I'm asking because I'm not sure if the current battery 
was really installed at the time indicated by this field.


Where APC has provided a value for battery mfg date, it has always 
been the same as the UPS mfg date. The value isn't automatically 
updated and NUT doesn't (from what I've seen) provide a way to 
update it manually.




The Nut Gnome client does allow updating the battery changeout value.

the field in question is: battery.date


I've only seen it as a read-only value (not in upsrw). Have you tried 
changing it in that client?


Yep.

 Just did it again now as a sanity check. Seems to work (barring a 
complete shutdown of my web/dns/mail server and all systems to make 
sure it sticks in the UPS too)


Restarting NUT should be enough to check. So NUT probably does support 
it on certain models. I have a bunch of APC RS's that can have their 
battery date updated using apctest, but not with NUT. Not a big deal though.


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Kris Jordan

Vieri wrote, On 2/28/2013 10:17 AM:

--- On Thu, 2/28/13, Kris Jordan nut...@sagebrushnetworks.com wrote:

Are you using APC's supplied serial cable? They have special
wiring and it varies depending on UPS model.

Nevertheless I'll take some extra time to search for the ups cables just in 
case I do find them and they really are different.


Look for a code on the cable, like 940-0024C.

http://www.networkupstools.org/cables.html
http://www.apcupsd.com/manual/manual.html#cables

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] false low battery alarm

2013-02-28 Thread Vieri


--- On Thu, 2/28/13, Kris Jordan nut...@sagebrushnetworks.com wrote:

 Oh, same cable from another identical UPS that works. Try
 resetting that UPS; it goes something like this: Unplug,
 disconnect the batteries, and press/hold the buttons to make
 sure the ups is completely dead. Does that help?

I'm going to have to move the production servers to another UPS (actually most 
servers have dual power supplies each connected to a different UPS but network 
switches don't).
I'll try that asap in a few days.
Thanks for pointing that out.

Vieri


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] UPS Liebert GXT-3

2013-02-28 Thread Marcelo Roccasalva
On Tue, Feb 26, 2013 at 10:56 PM, Charles Lepple clep...@gmail.com wrote:

 On Feb 21, 2013, at 6:21 PM, Marcelo Roccasalva wrote:

  I'll try the windows monitoring program tomorrow...

 Any luck?

Haven't tried... An Emerson support person sent me an updated version
of their software, which offers me an USB port to connect but it fails
to communicate with the UPS... Tomorrow will be windows tested...


 --
 Charles Lepple
 clepple@gmail






--
Marcelo

¿No será acaso que esta vida moderna está teniendo más de moderna que de
vida? (Mafalda)

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org