Ok we have a project where we will be installing and ESFR system in a 32' high
warehouse. A majority of the racks will be open but a few will have solid
shelving. I'm a little confused on chapter 25. Do I follow ceiling
sprinkler design from chapter 23 table 23.3.1 and then for the racks
I can't seem to find the required minimum clearance around an FDC.
I could swear I seen it in the past and believe it's 36" but can't seem to find
it now?
Anthony Carrizosa | Fire Protection Estimator / Project Manager
7855 S 206th St Kent, WA 98032
Direct: 253-341-4593 | Mobile: 206-679-5283
In our area they don’t make us perform the test but we are required to have a
sign at the fdc with the flow and pressure needed to get the 100 psi at the
remote hose conecttion.
Christopher S. Wilson SET
Project Design Manager
Treasure Valley Fire Protection
2731 S. Saturn Way
Boise, ID 83709
Good morning,
We’ve found it all depends on the district and individual AHJ…
We do a number of manual wet/dry standpipes in our area and each one comes with
it’s own challenges.
One of my colleagues just invested in a used fire truck figuring the best
course of action is to be over prepared