[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread BRUCE VERHEI
I agree with all in this case. Low point drains and inspection’s test can cause water damage in earthquakes. In Anthony C.’s home turf the most common break I saw in what our E-376 calls tilt-up town were in these lines. 1” tee’d over to wall, a 90 down, and almost immediately a 4” piece of

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Anthony Carrizosa
Yes Steve, you made us all think and use our brains today.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA7619.DC46AC10]

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Steve Leyton
Yeah, I coulda/shoulda just called Ken, but it’s for the good of the order, right? SL From: Anthony Carrizosa Sent: Thursday, March 14, 2024 2:09 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Gang drain crossing seismic joint Well

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Anthony Carrizosa
Well summed up Ken.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA7619.39384560]

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Ken Wagoner
Steve, three points here. §18.4.1 requires clearance for a drain extending through a wall, floor, platform, foundations.   §18.5.1.6 omits any bracing requirements for drain piping downstream of the drain

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Aaron Murg
I’m sorry for finicky AHJ’s Steve, I’m trying! Aaron MurgSent from my iPhoneOn Mar 14, 2024, at 13:20, Steve Leyton wrote: No, and that’s exactly my reasoning too.   I should have said in my post that I’m not 100% certain because it’s being submitted to a preposterously fickly AHJ and

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Prahl, Craig
If the life safety system will operate with or without the drain and if it being damaged won't cause damage to the primary life safety system and there is no text stating such ancillary piping is required to be braced, I'd say stick a fork in it, you're done. Sign, seal and deliver. Craig

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Steve Leyton
No, and that's exactly my reasoning too. I should have said in my post that I'm not 100% certain because it's being submitted to a preposterously fickly AHJ and they're historically very subjective, but my personal opinion is that it's not required for the reason that you mention. Steve

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Prahl, Craig
If the section that crossed the expansion joint were to be torn apart would it have any functional effect on the bldg. sprinkler or standpipe systems? Craig Prahl | Jacobs | Fire Protection SME - Special Hazards | craig.pr...@jacobs.com |

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Travis Mack
I would say that drain piping downstream of the valve is not required to be braced. One of the things I like to impress upon people when teaching seismic is that you brace and secure the pipe to keep the water in the piping. It is also to insure that piping required for the operation of the

[Sprinklerforum] Gang drain crossing seismic joint

2024-03-14 Thread Steve Leyton
All (especially Californicators): We have to cross a seismic joint with the piping that supplies a combination standpipe in a mid-rise building (no PRV's to test). As a combo, there's a collection pipe for sectional test and drain discharge, and for reasons peculiar to this building, our

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Chris Wilson
I would hope there would be a provision that if you hydraulicly prove it whit one connection that should be acceptable. Christopher S. Wilson SET Project Design Manager Treasure Valley Fire Protection 2731 S. Saturn Way Boise, ID 83709 Phone: 208-362-1888 Fax: 208-362-2207 please note all TVFP

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Steve Leyton
That’s hydraulics. If you can deliver the demand with no more inlet pressure than the FD is willing to accept, I think you can use 4” for the FDC. The foregoing is my opinion only and does not represent NFPA or the NFPA 14 Technical Committee, nor intended to serve as an interpretation of the

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Dewayne Martinez
Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm because of the pipe? From: John Denhardt Sent: Thursday, March 14, 2024 10:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Here is the

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Brian Harris
John- Good to know….. Thank you, Brian Harris, CET BVS Systems Inc. From: John Denhardt Sent: Thursday, March 14, 2024 11:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Here is the reference: NFPA 14 - 2024

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread John Denhardt
Here is the reference: NFPA 14 - 2024 10.7.3.1.1 Where a 4 in. (100 mm) inlet is used, the assumed flow per inlet shall be 500 gpm (1900 L/min). 10.7.3.1.2 Where a 5 in. (125 mm) inlet is used, the assumed flow per inlet shall be 750 gpm (2850 L/min). *The above is my opinion and has not been

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread John Denhardt
To all - review NFPA 14 -2024 as it has new requirements for 4" and 5" storz connections. 4" is limited to 500 GPM per connection 5" is limited to 750 GPM per connection Unfortunately, I'm at a conference where my internet connection is very limited, otherwise I would give you a section

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Ken Wagoner
Brian, Yes, I have been required to provide such a connection in the past.  It has been rare, and it was a gorilla sized high rise building. For me arguing with the AHJ over this seemed pointless. sincerely, Ken Wagoner, SET

[Sprinklerforum] FDC for Standpipe

2024-03-14 Thread Brian Harris
Anybody ever had an AHJ required a 4-way FDC with (4) Storz connections to feed a standpipe? I get the (1) 2-1/2" connection per 250 gpm but you're also allowed a "large diameter" hose connection. In this case the current FDC is a 5" Storz on 6" underground. Thank you, Brian Harris, CET BVS