[Sprinklerforum] Re: FDC for Standpipe

2024-03-18 Thread Chris Dorn
Sent: Saturday, March 16, 2024 1:35 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Chris - I'm not following. Hydraulics does not influence the flow rate through the storz connection. The flow rate is limited by the size

[Sprinklerforum] Re: FDC for Standpipe

2024-03-16 Thread John Denhardt
esses have changed > > new email below > > > > chr...@tvfpinc.com > > > > *From:* Steve Leyton > *Sent:* Thursday, March 14, 2024 10:48 AM > *To:* Discussion list on issues relating to automatic fire sprinklers < > sprinklerforum@lists.firesprinkler.org>

[Sprinklerforum] Re: FDC for Standpipe

2024-03-16 Thread John Denhardt
0gpm because of the Storz connection size or > 500gpm because of the pipe? > > > > *From:* John Denhardt > *Sent:* Thursday, March 14, 2024 10:39 AM > *To:* Discussion list on issues relating to automatic fire sprinklers < > sprinklerforum@lists.firesprinkler.org>

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Chris Wilson
email addresses have changed new email below chr...@tvfpinc.com<mailto:chr...@tvfp.us> From: Steve Leyton Sent: Thursday, March 14, 2024 10:48 AM To: Discussion list on issues relating to automatic fire sprinklers Cc: Dewayne Martinez Subject: [Sprinklerforum] Re: FDC for Standpipe

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Steve Leyton
From: Dewayne Martinez Sent: Thursday, March 14, 2024 9:30 AM To: Discussion list on issues relating to automatic fire sprinklers Cc: Dewayne Martinez Subject: [Sprinklerforum] Re: FDC for Standpipe Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm because of th

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Dewayne Martinez
Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm because of the pipe? From: John Denhardt Sent: Thursday, March 14, 2024 10:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Here

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Brian Harris
John- Good to know….. Thank you, Brian Harris, CET BVS Systems Inc. From: John Denhardt Sent: Thursday, March 14, 2024 11:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Here is the reference: NFPA 14 - 2024

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread John Denhardt
Here is the reference: NFPA 14 - 2024 10.7.3.1.1 Where a 4 in. (100 mm) inlet is used, the assumed flow per inlet shall be 500 gpm (1900 L/min). 10.7.3.1.2 Where a 5 in. (125 mm) inlet is used, the assumed flow per inlet shall be 750 gpm (2850 L/min). *The above is my opinion and has not been

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread John Denhardt
To all - review NFPA 14 -2024 as it has new requirements for 4" and 5" storz connections. 4" is limited to 500 GPM per connection 5" is limited to 750 GPM per connection Unfortunately, I'm at a conference where my internet connection is very limited, otherwise I would give you a section

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Ken Wagoner
Brian, Yes, I have been required to provide such a connection in the past.  It has been rare, and it was a gorilla sized high rise building. For me arguing with the AHJ over this seemed pointless. sincerely, Ken Wagoner, SET