Carling is another manufacturer of DC breakers.
The Altech V-EA series (part numbers end in UM) are rated 80VDC for the lower amp ratings and 42VDC for the higher amp ratings. They are actually made by Sursum, in Germany maybe, and are sturdier than other Altech breakers. For high current applications, like protecting large battery strings, I use a dual pole breaker for both sides of the batteries, this increases the DC voltage rating because you are interrupting the current in 2 places at once. From: AF <af-boun...@af.afmug.com> On Behalf Of Bill Prince Sent: Friday, December 28, 2018 10:37 AM To: af@af.afmug.com Subject: Re: [AFMUG] DC Breakers We get breakers that are specifically DC rated for the current we need. If they are DC rated, they will also indicate the maximum operating voltage (typically 48 volts) but you sometimes see higher voltages. Just be sure the ones you get are rated above the voltage you'll be using them at. 2X is a good place. bp <part15sbs{at}gmail{dot}com> On 12/28/2018 7:37 AM, Jason McKemie wrote: Do you generally size these about double the expected load? I see a lot of them rated at higher voltages than I need, will these still be effective?
-- AF mailing list AF@af.afmug.com http://af.afmug.com/mailman/listinfo/af_af.afmug.com