That was what I thought, thank you all for confirming.
However, with it connected red+/black-, when our tech flipped the breaker it 
blew out the DC/DC converter. In fantastic order, I was told.
So I'm going to have them put a voltmeter to the wires and see what we are 
getting from the power supply, maybe the output wiring is wrong.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107 ext 9002

----- Original Message -----
From: ch...@wbmfg.com
To: "AnimalFarm Microwave Users Group" <af@af.afmug.com>
Sent: Monday, April 8, 2019 11:59:47 AM
Subject: Re: [AFMUG] DC/DC converter question

What Ken said.

Positive is always positive.
Neg is always neg.
48 volts is 48 volts.

If someone wants to say a load or source is -48 or +48 it just means the 
opposite polarity is tied to earth or chassis ground.

If they say a load needs -48, it could mean that the load has the positive 
power wire also connected to the case.
If a source says it is a -48 source, it could mean that the source has the 
positive lead connected to ground.

You can always test a source.  Ground to the wire.  If you measure 48 volts 
between ground and one of the power wires, then it is referenced to ground. 
If you are on the positive wire to ground and you see 48 volts, then it is a 
neg ground system.  If you are on the neg wire to ground and you see 48 
volts then you are on a positive ground system.

Positive Ground System  == -48 or whatever volt system
Neg Ground System == +48 or whatever
BUT many sources and loads are floating where neither power lead is 
connected to chassis/earth/ground

Sometimes they will call those 48 VDC system.  But sometimes they will call 
them a +48 VDC system when really it is simply a 48 VDC system.

Anytime -48 is printed on something, time to  take it seriously.  They 
probably mean it.

-----Original Message----- 
From: Christopher Tyler
Sent: Monday, April 8, 2019 9:54 AM
To: AnimalFarm Microwave Users Group
Subject: [AFMUG] DC/DC converter question

I have a Meanwell SD-350C-24 DC/DC converter for +48v in to +24v out. I just 
learned that our DC plant at this site is -48vdc.
I'm assuming that I can't just plug it in backwards. But we've never had to 
deal with -48vdc before, am I wrong in this assumption?

-- 
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107 ext 9002


-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com 


-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to