I have never had a 240 anything not work on 208.  240-24=216
Most things can handle +- 10% 216 is not too far off of 208 and some 208 three phase systems run high.

That is only a 5 amp circuit. A 208 to 30 volt 5 amp transformer can be wired in a boost config.
Or anything close.  240 to 24 or 36 would work.

Say you found a 240-24 5 amp or more transformer. It will give you 21 volts on 208. Adding that to the 208 and you will get a boost to 229. Pretty close to the 230 you are looking for.

-----Original Message----- From: Nate Burke
Sent: Tuesday, September 27, 2022 4:31 PM
To: Animal Farm
Subject: [AFMUG] IceQube Cabinet AC units

I got a couple used cabinets that have IceQube IQ 4000BTU ac units. The
Label says 230V 60hz, but most of my sites have 208V 3 phase power.
Will they still work?  Nothing on the IceQube site lists 208v as an
option for these units, nor does any documentation I found address
208v/230v.

Years ago we had some portable 24000 BTU Mov-N-Cool 230v units, and they
would work with 208v, but as they got older, they couldn't always start
the compressor with 208v.

--