My electric car loses significant range at temps below 35F and as a double 
whammy, will not accept a full charge at low temps either.  

Lead acid work at low temps but if they get too far discharged they will 
freeze.  Gates Cyclons were advertised to be able to be fully charged and 
discharged when frozen.  

From: Mathew Howard 
Sent: Thursday, August 17, 2023 2:13 PM
To: AnimalFarm Microwave Users Group 
Subject: Re: [AFMUG] battery nerd question

Yeah, temperature is the main problem I'm seeing with going to lithiums. I can 
throw an SLA battery in an unheated box at our towers and it's going to work 
good enough, even in the middle of winter, but the minimum charging temperature 
for LFP batteries is 32F, which we're going to be below for a good part of the 
year.

On Thu, Aug 17, 2023 at 3:08 PM Bill Prince <part15...@gmail.com> wrote:

  Things have evolved. You can get LFP batteries for "almost" the same price as 
lead acid. Sometimes less even. They occupy less than half the space as lead 
acid, and will last at least twice as long. There is the issue of temperature 
sensitivity and they will need help for extremely cold environments.



bp
<part15sbs{at}gmail{dot}com>On 8/17/2023 12:36 PM, dmmoff...@gmail.com wrote:

    Ooh What lithium batteries are we talking about?  

    Last time I checked (a number of years ago), it was around 5x the $/Wh to 
buy Lithium.  





    From: AF mailto:af-boun...@af.afmug.com On Behalf Of Mathew Howard
    Sent: Thursday, August 17, 2023 10:51 AM
    To: AnimalFarm Microwave Users Group mailto:af@af.afmug.com
    Subject: Re: [AFMUG] battery nerd question



    Well, right. It doesn't scale well, because battery costs and space 
requirements will quickly become a problem. Batteries don't last forever, so 
you have to factor in replacement costs too, which will be a significant 
ongoing cost for a larger system. I'm pretty sure that lithium batteries would 
be cheaper long term now, since they should have a lot longer life span and the 
initial cost isn't a lot higher, but then heating is required, which means you 
need more power.



    On Wed, Aug 16, 2023 at 7:02 PM <dmmoff...@gmail.com> wrote:

      That’s building strictly for a 20W load though.  Building for a tiny load 
does make the costs easier.  But if you wanted a second AP, bigger backhaul, or 
anything else you can’t do it without growing the whole power system 
proportionally.



      Steve was talking a 50W load today.  The real high end hardware now is 
using a lot of signal processing either to reassemble useful data out of 
garbage or for beam steering, or both.  So you end up needing 100-150W for an 
AP.  You’d be hard pressed to find a licensed backhaul under 35W, and most of 
them are 50W+.  We could say we won’t deploy that equipment….but building for a 
20W load takes the choice away.  



      A 20A 240v circuit is 4800W.  Or a 20A 120V circuit is 2400W.  Even 2400W 
would power almost any WISP deployment.  Building solar to handle any load you 
might have is expensive, and building for only low power handcuffs you.    

      You do your thing your way, no judgement.  If it’s working for you then 
it’s good, but I can’t see myself going that direction.



      -Adam







      From: AF <af-boun...@af.afmug.com> On Behalf Of Mathew Howard
      Sent: Wednesday, August 16, 2023 5:01 PM
      To: AnimalFarm Microwave Users Group <af@af.afmug.com>
      Subject: Re: [AFMUG] battery nerd question



      I'm at about the same latitude as you. My experience is that having extra 
battery capacity is more helpful than oversizing the solar panels, so I'd 
probably go with Chuck's numbers for batteries if I was putting something 
together now, and solar panels are cheap now anyway, so figure 400 watts (if 
mounting space allows for it, which could be an issue if we're trying to fit it 
on a pole). 



      A quick check on Amazon shows 100ah SLA batteries for $160, so 6 of those 
would give me 7200 watt hours, for just under $1k. At $1500 (which is mostly 
just adjusting battery and panel sizes from where I started at $1k), I'm right 
in line with Chuck's estimate, aside from the battery costs.



      On Wed, Aug 16, 2023 at 3:33 PM <dmmoff...@gmail.com> wrote:

        I end up closer to Chuck’s estimate.  In Southern or Central NY State 
I’m 2 degrees north of Salt Lake City.  42N

        What’s your latitude?



        From: AF <af-boun...@af.afmug.com> On Behalf Of Mathew Howard
        Sent: Wednesday, August 16, 2023 4:11 PM
        To: AnimalFarm Microwave Users Group <af@af.afmug.com>
        Subject: Re: [AFMUG] battery nerd question



        Yeah, that's what I'd do in a difficult to access location. I did a 
site like that here (Wisconsin) with 200 watts of panel (I think the actual 
load is around 15 watts, so a bit more than 10x), and ~4kwh of battery. It had 
some issues in January a couple years, but I attributed that more to using 
cheap flooded deep cycles, rather than not enough capacity. With AGMs, it's 
gotten through the last couple of winters without issues. 4kwh of AGMs can be 
had for around $800, last I checked. Probably looking at closer to $1500 when 
you add in enclosures and mounts, but some of that is replacing parts that are 
needed with AC power anyway (smaller enclosure, backup batteries, power 
supply), so that offsets it a bit.



        On Wed, Aug 16, 2023 at 2:50 PM Chuck McCown via AF <af@af.afmug.com> 
wrote:

          Using my historical rules of thumb for off grid, snowed in mountain 
top location for a 20 watt load I would do the following that has never failed 
me:



          Load X 20 so 400 watts of panel.  So less than $200 these days.  

          2 weeks of battery autonomy.  

          20 x 24 x 14= 6720 watt hours.  $2K of batts

          Plus enclosures, mounts, charge controllers.



          $2500 and it will never go down in the winter.  At my Utah latitude 
on top of Utah mountains.  







          From: Mathew Howard 

          Sent: Wednesday, August 16, 2023 1:07 PM

          To: AnimalFarm Microwave Users Group 

          Subject: Re: [AFMUG] battery nerd question



          It depends on how much stuff you're trying to run. A minimal micropop 
can be done with less than 20 watts of load (single AP and backhaul). I can put 
together a solar setup for around $1000 that will power that.



          On Tue, Aug 15, 2023 at 12:50 PM <dmmoff...@gmail.com> wrote:

            I can save you the suspense.  If you have access to electric 
that’ll be cheaper than solar.  The problem is the need to run 24/7.  You have 
to design around the December-January months.  I’m in NY State, and at our 
latitude we only get a few hours of average production per day during those 
months.  And obviously if it’s snowing for a week you need to be able to ride 
through that on mostly battery power.  Even with a modest load it takes a silly 
amount of panels and batteries to stay up 24/7 in the winter.  More than you’d 
ever be allowed to put on a utility pole. 



            Talk to your electric co about the smallest service you can get.  
Explain what you’re trying to do and that your max load is very low.  

            NYSEG normally doesn’t do less than 100A, but they made an 
exception and let us do 60A.  You need a meter can, a service rated panel, a 
conduit up the pole and a weatherhead.  Then you either have an outdoor outlet, 
or have an outlet inside your enclosure.  You’ll want the smallest service 
they’ll let you do because of the wire size on the service cable.  A 20A (if 
they’d allow it) would only need a 12/3 with ground, and that’s up to 4800 
Watts (240x20) so it’s still more than you’d ever need.   A 12/3 is way cheaper 
than a 100A service entrance cable.



            My figure is 8 years old, and obviously there’s been inflation 
since then, but I went to the same contractor who does electric installs for 
the cable company and they quoted me about $1000.  Even if it’s 3x that for you 
today you’d still never beat that with a solar installation even if they’d let 
you do it.  And I’m not some knee-jerk anti-solar lunatic, I’m just saying I’ve 
run the numbers and it doesn’t add up.   People do it when they’re off grid, or 
when the electric service is unreliable in the area, or sometimes just for the 
PR/marketing power of being “solar powered”.  Those are all fine reasons, but 
doing it for cost savings isn’t going to work out.



            -Adam





            From: AF <af-boun...@af.afmug.com> On Behalf Of Steve Jones
            Sent: Tuesday, August 15, 2023 10:27 AM
            To: AnimalFarm Microwave Users Group <af@af.afmug.com>
            Subject: Re: [AFMUG] battery nerd question



            we have a dozen or so, but are looking at pole mount micropops (our 
own poles). We are losing a grain elevator site because they decommissioned the 
elevator and theres no real options for the customers in some of the areas. Im 
just trying to get to something we can get solar power with enough battery to 
last through overcast. So Im calculating per battery runtimes, then will look 
at number of batteries we would need to survive vs paying for a ROW meter vs 
losing the customers. Just have to get to the cost per customer to retain them 
and the benefit gained per pole





            On Tue, Aug 15, 2023 at 8:53 AM Brian Webster 
<i...@wirelessmapping.com> wrote:

              How many of the batteries do you have? Do you need any voltages 
other than the 48 volts? If you have 4 batteries and only need 48 volts then 
wire them in series and not have to deal with the converter.



              Thank you,

              Brian Webster





              From: AF [mailto:af-boun...@af.afmug.com] On Behalf Of 
dmmoff...@gmail.com
              Sent: Tuesday, August 15, 2023 6:59 AM
              To: 'AnimalFarm Microwave Users Group'
              Subject: Re: [AFMUG] battery nerd question



              *You’re around C/30 which should be on the high end of capacity.  

              Lower load usually means a little extra capacity out of the 
battery.  I realized that sentence might have been ambiguous.





              From: dmmoff...@gmail.com <dmmoff...@gmail.com> 
              Sent: Tuesday, August 15, 2023 6:56 AM
              To: 'AnimalFarm Microwave Users Group' <af@af.afmug.com>
              Subject: RE: [AFMUG] battery nerd question



              You can do the whole thing in Watts.



              12V * 150ah = 1800 Watt-hours

              1800Wh / 50W = 36 hours



              If they’re telling me 95% efficiency, I’d assume 50W out needs 
53W in (50 / 0.95).   

              There’s usually an efficiency curve for the device based on load 
and temperature so it wouldn’t be 95% in all circumstances.  Your system should 
be drawing less than 5A off the battery, and if your multimeter has a 10A fuse 
like most do, then you could put the meter in line and actually measure the 
amperage before and after the converter.  Then you’d know for sure.



              And the battery’s total capacity will have a curve based on 
C-rate so there’s some variability there too.  Usually it lasts longer when 
you’re drawing lower amperage.  You’re around C/30 which should be on the high 
end.  



              Age and maintenance of the battery affect runtime as well.  If I 
want 6 hours of runtime then I plan Ah for 12 hours runtime. When my batteries 
are halfway toasted I’m still getting useful life out of them.





              From: AF <af-boun...@af.afmug.com> On Behalf Of Steve Jones
              Sent: Monday, August 14, 2023 9:57 PM
              To: AnimalFarm Microwave Users Group <af@af.afmug.com>
              Subject: [AFMUG] battery nerd question



              Just trying to cipher runtimes

              I have on hand 150ah 12 volt batteries, so thats what id be 
looking to use.

              Excluding the conversion loss of a 12v to 48v step up converter 
is the math correct here?

              12v 150ah=1800 watt hours
              1800 watt hours at 48v = 37.5ah
              50 watts of radio running 48v = 1.04 amps
              37.5ah @ 1.04 amps = 32.77 hours runtime



              does a step up that claims 95% efficiency mean 95% of the watt 
hours?

              -- 
              AF mailing list
              AF@af.afmug.com
              http://af.afmug.com/mailman/listinfo/af_af.afmug.com

            -- 
            AF mailing list
            AF@af.afmug.com
            http://af.afmug.com/mailman/listinfo/af_af.afmug.com


----------------------------------------------------------------------

          -- 
          AF mailing list
          AF@af.afmug.com
          http://af.afmug.com/mailman/listinfo/af_af.afmug.com

          -- 
          AF mailing list
          AF@af.afmug.com
          http://af.afmug.com/mailman/listinfo/af_af.afmug.com

        -- 
        AF mailing list
        AF@af.afmug.com
        http://af.afmug.com/mailman/listinfo/af_af.afmug.com

      -- 
      AF mailing list
      AF@af.afmug.com
      http://af.afmug.com/mailman/listinfo/af_af.afmug.com


     
  -- 
  AF mailing list
  AF@af.afmug.com
  http://af.afmug.com/mailman/listinfo/af_af.afmug.com



--------------------------------------------------------------------------------
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to