Well, that call was enlightening.

I told the support guy about the 350kcmil reference ground and he laughed, then 
he said to someone next to him, "Doug! This guy's got a contractor telling him 
he needs a 350 reference ground! Hah!" They actually say to use the larger of 
10AWG or the largest power conductor on the system, which makes a hell of a lot 
more sense.  I told him the story from the former Comcast guy about every 
Comcast site having the honking big wire to MGB and 2AWG to earth, and he said 
Comcast can write whatever spec they want, and if they want to waste all that 
copper that's their business.

So yeah, people are doing this weird thing, and it sounds like Ken's option #5 
is the reason. They have no idea why they do it.

-Adam


________________________________
From: AF <[email protected]> on behalf of Ken Hohhof <[email protected]>
Sent: Thursday, February 5, 2026 1:25 PM
To: 'AnimalFarm Microwave Users Group' <[email protected]>
Subject: Re: [AFMUG] Reference ground sizes


I can think of 4 general explanations that might fit:



1)  current carrying capacity

2)  ground potential difference

3)  safety of equipment or personnel in some fault condition

4)  some regulation or code that may not make sense but you have to follow it 
just because



Our guesses are probably not going to be helpful, I would ask your low voltage 
guy where this spec comes from.  It seems very specific, it must come from 
somewhere.  If he says it’s in the GE installation manual, I would ask GE.



OK, there’s another possibility #5, it’s what they’ve always done and he 
doesn’t know why.



From: AF <[email protected]> On Behalf Of Steve Jones
Sent: Thursday, February 5, 2026 11:59 AM
To: AnimalFarm Microwave Users Group <[email protected]>
Subject: Re: [AFMUG] Reference ground sizes



My guess would be so that the fire starts aways from the rectifier and not at 
it. Not saying there is an inherent fire risk. But it takes the detrimental 
load away to a far off point of failure.



On Thu, Feb 5, 2026 at 9:44 AM Adam Moffett 
<[email protected]<mailto:[email protected]>> wrote:

When we get big rectifiers installed, the low voltage guy is running a 350kcmil 
to the MGB.  350kcmil is about 7/8" diameter including the jacket.



It feels kind of silly to have that on the bus bar and have a #2 to earth, but 
I'm told this is normal.  What's the point of having that anaconda from the 
rectifier to the bus bar?



These are GE Infinity systems by the way.  16KW to 32KW systems.



-Adam



--
AF mailing list
[email protected]<mailto:[email protected]>
http://af.afmug.com/mailman/listinfo/af_af.afmug.com
-- 