I think it might be because it's cold here now and the charger compensates
for battery temp.

I'll check the controller manual again tho because I thought that voltage was
high too.



On Thursday, October 2, 2014, Eric Kuhnke via Af <af@afmug.com> wrote:

> 60V seems high, copied verbatim from the datasheet for a typical
> powersonic 12V AGM battery (12V):
>
> Limit initial current to 1.2A. Charge until battery voltage
> (under charge) reaches 14.4 to 14.7 volts at 68°F (20°C). Hold at 14.4 to
> 14.7
> volts until current drops to under 50mA. Battery is fully charged under
> these
> conditions, and charger should be disconnected or switched to “float”
> voltage.
> “Float” or “Stand-By” Service:
> Hold battery across constant voltage source of
> 13.5 to 13.8 volts continuously. When held at this voltage, the battery
> will seek its
> own current level and maintain itself in a fully charged condition
>
>
>
> so multiply by four, 14.4V x 4 = 57.6V max voltage at absorption charging
>
> or 14.7V x 4 = 58.8V
>
>
>
> On Thu, Oct 2, 2014 at 4:11 PM, Bill Prince via Af <af@afmug.com
> <javascript:_e(%7B%7D,'cvml','af@afmug.com');>> wrote:
>
>> Many new solar controllers will let you program the absorption voltage.
>> We just started using an MPPT controller from Midnite solar, and all the
>> different voltages are programmable per the battery manufacturer's
>> specification.
>>
>> bp
>>
>>
>> On 10/2/2014 12:50 PM, Sean Heskett via Af wrote:
>>
>>> Hi Gang,
>>>
>>> We have a 48Vdc Solar site that the solar charge controller when it goes
>>> into absorption mode the battery array voltage exceeds 60Vdc.  However we
>>> have some equipment that doesn't like more than 60Vdc.
>>>
>>> What product are you using to supply a clean 48Vdc (no more that 300
>>> Watts is needed)
>>>
>>> Thanks!
>>>
>>> -sean
>>>
>>>
>>
>

Reply via email to