Those are identical to the Altech DC UPS.

bp
<part15sbs{at}gmail{dot}com>

On 3/9/2016 11:06 AM, [email protected] wrote:
We've been using these:

http://www.poweringthenetwork.com/din-ups/

12V, 24V and 48V options. Alarms when on battery so Sitemonitor is notified and let's know know of bad battery/change
battery as well. Pretty affordable too.

On Wed, Mar 9, 2016 at 1:52 PM, Chuck McCown <[email protected] <mailto:[email protected]>> wrote:

    A pair of power supplies that are capable of pulling the load and
    charging the battery.
    For example, if you needed 200 watts for your 24 volt loads, you
    need 8.3 amps.  Round that up to 10 amps.
    Then you have to decide how long you want this thing to last
without commercial power. I would think 24 hours is a minimum. So 10 amps x 24 hours is 240 amp hours of battery.
    It is always a safe figure to charge a battery at .1C or 10% of
    its capacity or less.  That would be 24 amps to charge the batts
after a power outage, plus 10 for load = 34 amps of power supply. You could get by with 20 amps, just will take a bit longer to charge.
    Lots of 20 amp 28VDC power supplies out there.
    Rule of thumb double your load power or more to size the charger.
    *From:* SmarterBroadband <mailto:[email protected]>
    *Sent:* Wednesday, March 09, 2016 11:45 AM
    *To:* [email protected] <mailto:[email protected]>
    *Subject:* [AFMUG] Small DC Site

    What are people using to power small DC sites.  Option 1 up to 150
    - 200 Watts, option 2 up to 300 – 400 Watts.  I’m looking for a DC
    UPS that can charge attached batteries.  Need to have 24 and 48 volt.



Reply via email to