I’ve never used the Tripp Lite APC series, but I believe their main purpose is 
emergency vehicles, RVs, boats, etc. where they switch automatically between 
battery and shore power.  Using similar units in the past, I have found one 
thing to look for is how low the shore (commercial) power has to be for the 
transfer switch to switch to batteries.  They may just use a relay, assuming 
commercial power is either there or it isn’t.  But we get a lot of partial 
voltage situations like 60 or 80 volts, and a lot of our electronics won’t run 
on that.  It’s very frustrating to drive out to a site that is down, and find a 
fully charged battery string that isn’t being used because the ATS thinks 80 
volts is plenty.

 

 

From: Af [mailto:[email protected]] On Behalf Of Josh Corson
Sent: Tuesday, December 27, 2016 11:48 AM
To: [email protected]
Subject: Re: [AFMUG] Battery backup at large sites

 

How about a APC750 or APC1250 tripplite inverter/charger? 

Also I wanted to have a way to monitor how long of runtime the batteries have 
remaining...like the APC smart UPS units. 


On Dec 27, 2016, at 2:52 AM, Forrest Christian (List Account) 
<[email protected] <mailto:[email protected]> > wrote:

The tool you're looking for in relation to the monitoring is a packetflux 
sitemonitor base unit.  

 

Others can point you toward the chargers.

 

On Dec 26, 2016 11:36 PM, "Josh Corson" <[email protected] 
<mailto:[email protected]> > wrote:

What is everyone using as a battery backup at sites that cannot use a
standard off the shelve UPS?
The site in mention is probably using 500 watts max. The battery side
of things is a no brainer - calculate run time, determine your bank,
buy batteries.
However, what are you using for:

1. Inverter / charger
2. Network monitoring capability when AC goes out with SNMP.

The hardest challenge I've found is sourcing something for network
monitoring that isn't an all in one charger/inverter like the ICT
models at 1k.

Always wondered if you could rig a APC network card to work in a battery bank...

If anyone could share the layout of their system I'd appreciate it!

Josh

Sent from my iPhone