Franklin method proven once again...thanks Ben!!!  I have no qualms
recommending it to anyone...

Jaime Solorza

On Jul 25, 2017 11:55 AM, "George Skorup" <[email protected]> wrote:

We're on a tower that had no air terminal. We'd lose gear occasionally.
Owner added an air terminal bonded to the top section. The frequency of
lost gear didn't change much. They ran a conductor from the air terminal
all the way down to the grid and we haven't lost anything since, ~2 years.

We were on another tower for years and always lost gear. 500' FM, cell,
paging. Lots of shit. Halo air terminal on top, 2/0 coming down. We
abandoned it because every year, every single piece of copper on the ground
to about 10 feet up the tower would be missing. It would not be replaced
until the fall. Then it was all gone again the next spring. Lot of good it
does in the winter.


On 7/25/2017 12:38 PM, Paul McCall wrote:

Lewis,



On option 2, if you are just leasing space on a tower such as Crown Castle,
etc., I have doubts that they would allow me to install the 8’ rod at the
top and run the 2/0 down the tower.  So, would you, just do a 2/0 starting
at your equipment area, bond to the tower at that height, and go down from
there?



On the “bonding everything together” scenario, if the tower ground is not
as good as the other grounds going down the tower (mine, the cellular
companies, etc.) won’t the differential in impedance cause the lightning to
1) likely take the lesser impedance path down and/or 2) have the voltage
not rise and fall together and bad things happen from that?



Paul

*From:* Af [mailto:[email protected] <[email protected]>] *On Behalf
Of *Lewis Bergman
*Sent:* Monday, July 24, 2017 1:47 PM
*To:* [email protected]
*Subject:* Re: [AFMUG] Tower Top Grounding discussion



On 1. it will be really difficult to completely isolate a piece of
equipment unless it is designed to float but good luck. If you are truly
going to isolate everything from ground then you won't need to worry about
#2 as all will float. You should check that the antenna you are using don't
require a ground plane.

On 2. I Cadweld a 2/0 jacketed to an 8' rod at the top of the tower, not
isolated. I then bond (15 ton Hydraulic Crimp) it to a bus bar 5' below the
top for equipment grounds. Anywhere else there is a cluster of equipment I
also put a bus bar. I then take that 2/0 to the bottom to the last bus bar
and then into the ground ring.



   1. *Wondering what materials people are using to isolate their mounts?*
   What is sufficient?  Would the rubber from a thick radiator hose be enough
   to keep the lightning from coming through?  Double thicknesses?



One consultant recommended starboard, but I am not sure how I will craft
that into a work piece that would mold around a tower leg and be able to
grip it.



   1. *What size wire should be going down the tower to bond to my tower /
   electrical ground?   *

I am assuming it should be insulated but is normal THHN jacketing enough to
have it truly isolate from something jumping over or does it have be in
conduit.



Paul