Like I suggested, it does require attention... better be safe than
sorry...but I do enjoy your style Steve...BTW..as soon as wife makes
Tamales I will send you a dozen ..

Jaime Solorza

On Aug 2, 2017 7:36 PM, "Chuck McCown" <ch...@wbmfg.com> wrote:

> GFI simply looks at the current going out on the hot wire and the current
> coming back on the neutral.  If the currents are not identical, the little
> transformer they pass through creates an output voltage that trips the
> unit.  The transformer is wired such that the two currents cancel each
> other.  So when they are the same, they totally and perfectly cancel.  If
> more current is on the  hot than the neutral (or the unlikely situation
> where there is more on neutral than hot) it trips..
>
> If it is tripping, somewhere current is leaking out of the circuit and
> returning via earth ground.  You can always put an isolation transformer on
> the output which will stop the tripping and make it safe at the same time.
> Best to fix the leakage.
>
> *From:* Steve Jones
> *Sent:* Wednesday, August 02, 2017 7:29 PM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Gfi kicking on portable generator
>
> I dont know what actually is happening when a leg is out at a grain
> elevator that drops to the 60-80, something at the transformer i assume.
> This is the site i went to swap a ptp500 to a 650 last week and broke
> their manlift, this site and i have.... history, will probably be where i
> die, i made it my bitch once and had to climb up in an ice storm with two
> inches of ice on everything, 6 inch horizontal icicles, still got that up
> and running wearing khakis and a jacket.
> Ever since i took its manhood, that place has treated me like its a psycho
> ex wife.
>
> Ill rewire the cutover switch in the morning when the power company gets
> it fixed up.
>
> I do have to have a solution for knucklehead techs though, i think i could
> have achieved the same thing with a two prong adapter. Just dont want to
> deal with osha and paperwork if i play croakamope with a tech picking up a
> generator
>
> On Aug 2, 2017 8:14 PM, "George Skorup" <george.sko...@cbcast.com> wrote:
>
>> I see 60-80VAC at grain sites all the time when a phase is out. Pain in
>> the ass. The GFI recept on the gen could just be going bad. Could also be
>> something as simple as noise/surge suppression in your UPS causing it. I
>> wouldn't worry about it.
>>
>> On 8/2/2017 7:12 PM, Steve Jones wrote:
>>
>> Millivolts not amps
>>
>> On Aug 2, 2017 7:08 PM, "Steve Jones" <thatoneguyst...@gmail.com> wrote:
>>
>>> Milliamps. But its a brownout/power outage
>>>
>>> On Aug 2, 2017 6:57 PM, "Jaime Solorza" <losguyswirel...@gmail.com>
>>> wrote:
>>>
>>> Did it read zero? If not , have that checked...we spent all morning with
>>> engineers, electricians and us chasing a weird diesel generator to UPS
>>> issue...Fluke meters galore...
>>>
>>> Jaime Solorza
>>>
>>> On Aug 2, 2017 5:51 PM, "Steve Jones" <thatoneguyst...@gmail.com> wrote:
>>>
>>>> At a grain elevator right now, brownout type issue, 60v some places
>>>> none at others. Not our chair, not our problem, except our portable
>>>> generator gfi trips every time the cutover switch engages.
>>>> We ended up just bypassing the cutover and only wiring phase and
>>>> neutral to the generator outlet, leaving ground disconnected. I suppose we
>>>> could have left everything intact and disconnected ground from the panel, i
>>>> dont know
>>>>
>>>> But what we have now is phase and neutral on generator feeding the
>>>> outlet up top, the ground is still connected to the service ground up top.
>>>> We dont have access to a panel its connected at
>>>>
>>>> I did measure between the ground at the panel and a known good earth
>>>> ground. No voltage, i assume that means no hot ground.
>>>>
>>>> The concern here is if im missing something and the gfi is kicking
>>>> because of something i dont have capacity to verify, is running this
>>>> generator this way a risk of electrocuting somebody who touches the frame?
>>>>
>>>> Its ground is not connected in the circuit, same as if id just
>>>> connected a 2 prong adapter
>>>>
>>>>
>>>
>>>
>>
>>