R56 Chapter 5.
https://sites.auburn.edu/admin/facilities/spw-bid-calendar/11-150%20AU%20Regional%20Airport-Construct%20a%20Self-Supporting%20Radio%20Tower/Project%20Documents/1/Motorola_R56_2005_manual.pdf
""
Telecommunication cable metallic shields shall be bonded to the site’s
grounding electrode system as
described herein. Where outside facility telecommunication cables are
configured for a standard
entrance, the metallic members of all incoming telecommunication cables,
including paired-conductor
and optical fiber cable, shall be grounded (earthed) to the MGB, either
directly or through a SSGB at
the facility’s entrance point. Each metallic member shall be effectively
bonded to the grounding point
with a 16 mm2 csa (#6 AWG) or coarser green-jacketed grounding
conductor, or with a transmission
line ground kit, using bonding methods described within this chapter.
""
So they say #6 AWG.
I'm an unqualified rando on the internet, but I'd say if you grounded it
with anything at all then you did better than most.
------ Original Message ------
From: "Steve Jones" <thatoneguyst...@gmail.com>
To: af@afmug.com
Sent: 5/1/2018 11:40:15 AM
Subject: [AFMUG] Smallest gauge shield to ground
Whats the smallest gauge stranded ground i can use to bond bbdge copper
shield to the ground lug on surge suppressors? Ive been using #8 but it
gets cumbersome in a 12 port cross connect enclosure, i dont have
footprint for a larger enclosure and my contractors hate my design