R56 Chapter 5.
https://sites.auburn.edu/admin/facilities/spw-bid-calendar/11-150%20AU%20Regional%20Airport-Construct%20a%20Self-Supporting%20Radio%20Tower/Project%20Documents/1/Motorola_R56_2005_manual.pdf

""
Telecommunication cable metallic shields shall be bonded to the site’s grounding electrode system as described herein. Where outside facility telecommunication cables are configured for a standard entrance, the metallic members of all incoming telecommunication cables, including paired-conductor and optical fiber cable, shall be grounded (earthed) to the MGB, either directly or through a SSGB at the facility’s entrance point. Each metallic member shall be effectively bonded to the grounding point with a 16 mm2 csa (#6 AWG) or coarser green-jacketed grounding conductor, or with a transmission
line ground kit, using bonding methods described within this chapter.
""

So they say #6 AWG.

I'm an unqualified rando on the internet, but I'd say if you grounded it with anything at all then you did better than most.



------ Original Message ------
From: "Steve Jones" <thatoneguyst...@gmail.com>
To: af@afmug.com
Sent: 5/1/2018 11:40:15 AM
Subject: [AFMUG] Smallest gauge shield to ground

Whats the smallest gauge stranded ground i can use to bond bbdge copper shield to the ground lug on surge suppressors? Ive been using #8 but it gets cumbersome in a 12 port cross connect enclosure, i dont have footprint for a larger enclosure and my contractors hate my design