FM200 is still used in a few DC’s in Sydney and Brisbane to my knowledge. But 
is costly to replace due to environmental charges.

In Polaris we check all our bottles in accordance to the fire program (which 
was approved upon completion with the fire code of that time) which is every 
year, bottles are check and every month, fire tech comes out to inspect gauges 
release valves and all control boards. All bottles are to be replaced every 10 
years of less and  Co2 bottles to replaced every 3 years.

In my opinion, fire is something that is neglected a lot in DC’s.

AG

Adam Gibson
Head of Data Centres
Springfield City Group

t: +61 7 3819 9999
f: +61 7 3819 9900
m: +61 4 00 807 822
e: mailto:a.gib...@springfieldcitygroup.com

From: AusNOG <ausnog-boun...@lists.ausnog.net> On Behalf Of Bruce Forster
Sent: Thursday, 13 December 2018 10:36 AM
To: chris.f...@inaboxgroup.com.au
Cc: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] [AUSNog] : Re Data Centre Fire Suppression Safety

Pretty sure halon is banned, but fm200 is the gas used these days?

https://www.safelife.az/en/index.php/services/firefighting-by-gas.html<https://www.safelife.az/en/index.php/services/firefighting-by-gas.html>

Firstly, the most important advantage of the use of chemical gas - it is safe 
for people and electronic equipment. During fire fighting gas is used in a 
concentration not to be harmful to human health and life. When using the FM200 
gas concentration of oxygen in the room is reduced by 3%. Along with the fact 
that such a composition of the air is not sufficient to continue the fire, it 
allows people who are there to breathe.

On Thu, Dec 13, 2018 at 10:01 AM Chris Ford 
<chris.f...@inaboxgroup.com.au<mailto:chris.f...@inaboxgroup.com.au>> wrote:
As a university cadet working for IBM in the late 80s I remember getting 
inducted into the Westpac data centres and getting a long explanation of what 
to do when the halon system went off – where the breathing gear was, where the 
exits were, to basically just drop everything and run.

Have been inducted into a few DCs in the last 3 years and can’t remember that 
being part of the induction at all – although given I already knew it I may 
have just glossed over that part.

--
Chris Ford
Chief Technology Officer

INABOX GROUP
m 0401 988 844 e 
chris.f...@inaboxgroup.com.au<mailto:chris.f...@inaboxgroup.com.au>
t 02 8275 6871 w www.inaboxgroup.com.au<http://www.inaboxgroup.com.au>

From: AusNOG 
<ausnog-boun...@lists.ausnog.net<mailto:ausnog-boun...@lists.ausnog.net>> On 
Behalf Of Paul Wilkins
Sent: Thursday, 13 December 2018 10:53 AM
To: AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>
Subject: [AusNOG] [AUSNog] : Re Data Centre Fire Suppression Safety

Every data centre has a fire suppression system. We're not used to thinking of 
this as a hazardous environment, but consequent to two techs being found dead 
working on a fire suppression system in 
Antarctica<https://www.theguardian.com/world/2018/dec/12/antarctica-two-technicians-dead-mcmurdo-station-ross-island>,
 I find myself wondering yet again, why there aren't more stringent controls 
around the fire suppression systems in data centres: viz - when you enter a 
data centre, how confident can you be you're not going to be quietly 
asphyxiated?

Kind regards

Paul Wilkins
_______________________________________________
AusNOG mailing list
AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>
http://lists.ausnog.net/mailman/listinfo/ausnog<http://lists.ausnog.net/mailman/listinfo/ausnog>


--
Regards,

Bruce
_______________________________________________
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog

Reply via email to