That's called a Static bypass and most commercial UPS setup's incorporate one. These days its the only way you can legally do maintenance inside the UPS without dropping the load. It's also another reason why the UPS inverter stays insync with the mains. So the static bypass can be switched without a big bang.  Most Static Bypass systems also incorporate an interlock that stops you switching to bypass unless the inverter is in sync with the load or the inverter is shut down and internal bypass is activated.

It's also sometimes refereed to as an external bypass. Unlike an ATS they are not usually Automatic and they do not switch the neutral and earth which remain in parallel only the Active phases are switched.

Matt


On 26/2/21 2:30 pm, John Edwards wrote:
For a truly paranoid setup, you can put an additional ATS *after* the UPS.

This potentially lets you replace a failed or failing UPS without downtime.

One time, this saved me because the UPS took a catastrophic surge to its input side, but the inverter and batteries kept powering the network.

We were able to switch over to mains without downtime and install a new UPS.

John




On Fri, 26 Feb 2021 at 13:33, Matthew Perkins <m...@spectrum.com.au <mailto:m...@spectrum.com.au>> wrote:

    A generator ATS and UPS setup are not trivial configurations. The
    whole
    system needs to be engineered by a qualified engineer with
    experience in
    those sorts of setups.  Both for Australian Wiring rules and also to
    ensure all your earth/neutral bonds are at the same potential.  If
    you
    end up with a floating neutral loosing power will be the least of
    your
    worries. Replacing all the PSU's in all your equipment will be.

    Typically in a Generator / ATS / UPS setup the UPS is of the double
    conversion type. The UPS output is always in sync with the mains
    and the
    output of the inverter is always running the load. This is to
    cover the
    situation where the inverter fails and the UPS goes into bypass.

    If the mains fail the UPS Sends a signal to the ATS that sends a call
    for the generator to start. The Controller in the ATS then executes a
    per-progamed set of make/break commands

    With respect of output of ATS

    The Mains active is broken

    The Generator Neutral is made

    The Mains Neutral is broken

    The Generator Active is made

    In that sequence you will note the mains and generator neutrals
    overlap
    this is extremely important if you dont want to let the smoke out.

    The UPS  then detects input from the generator and that the
    inverter is
    unsynchronized  It then starts to slowly adjust the phase to align
    the
    inverter output within 1% of the generator and and at that point the
    whole thing is shoved back into line.

    When mains is restore the process above is reversed.

    Key things are Earth bonding of generator and neutral overlap is of
    extreme importance a floating neutral even on single phase UPS
    systems
    can see potential differences of many hundreds of volts to earth.

    take care

    Matt.




    On 26/2/21 1:41 pm, James Andrewartha wrote:
    > Has anyone fed a generator into an automatic transfer switch? We
    got a
    > generator recently, which is hooked up to some circuits in our
    server
    > room, that can be manually switched between mains and a
    generator. We also
    > have an existing UPS that most of the room runs on, and has a
    runtime of
    > about an hour at the moment. I want to have the ATS fed by the
    UPS and the
    > mains/generator circuit, so they will be able to use the UPS
    until we get
    > the generator running.
    >
    > I ask because I was reading APC's documentation which has these
    notes:
    >
    >> Do not plug an ATS into a generator without the protection of a
    Double
    >> Conversion On-Line Uninterruptible Power Supply (UPS).
    >> **Using the Rack ATS with a Generator**
    >> APC recommends placing a UPS between the generator and the ATS
    input.
    >> The UPS will condition the input voltage to the ATS to prevent
    >> thrashing. A second UPS should be used between the power
    utility and the
    >> other input of the ATS. This UPS will power the load while the
    generator
    >> starts and stabilizes. The UPS should be sized to allow time
    for the
    >> generator to be started and the time needed for the UPS
    attached to the
    >> generator to operate normally. While the generator is starting, the
    >> generator voltage and frequency are not stable. If the ATS is
    connected
    >> directly to the generator, the ATS can switch to the generator
    input
    >> before the generator has stabilized. The load of the ATS will
    cause the
    >> generator voltage to dip. This dip can also shift the frequency
    of the
    >> voltage. Either of these issues can cause the ATS to switch to
    the other
    >> input.
    > Whereas Eaton says:
    >> However, the STS module can also be supplied by one UPS and
    another type
    >> of source, or by two non-UPS sources providing a sinusoidal
    output (AC
    >> system, engine generator set, etc.).
    > I'm thinking the scenario listed by APC is less likely in my
    situation
    > since the switch to generator power will be manual, only after
    we start it
    > up, and that even if the ATS does switch back to the UPS then
    the other
    > loads (dual-input ones) will remain on the generator, so the ATS
    load
    > won't be as significant the second time it tries to switch back.
    Thoughts?
    >
    >
    _______________________________________________
    AusNOG mailing list
    AusNOG@lists.ausnog.net <mailto:AusNOG@lists.ausnog.net>
    http://lists.ausnog.net/mailman/listinfo/ausnog
    <http://lists.ausnog.net/mailman/listinfo/ausnog>

_______________________________________________
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog

Reply via email to