hi john, you are similar to us here in the uk. the only diffirence is that you 
are 60 hz and we are 50. but that wont make any diffirence in what you want to 
do.

from my point of view, if it were me i would run in at least a 
30 amp radial circuit (sometimes known as a sub main, 
but you may consider a 45 amp sub main to give you capacity for further 
development.
from this you can then take of a  20 amp dedicated circuit  for the saw and 
dust extractor, and a further 15 amp circuit for your heater,   and a further 
circuit for your lights.

not sure what you are allowed to do in  australia as regards the size of 
cables, 
but what you need to take into consideration is the distance away from the 
supply line you are going to run your saw.   because the further away you are, 
the more cable you need to use, and the more the voltage drop will be under 
load.

for cost effectiveness, for a short run of cable under  5 metres, it will   
probably be cheaper and easier for you to run in  your sub main with a 6mm  
twin and earth cable. similar to what you would put in for a small  electric 
cooker or a 8.5 kw electric shower. 

however, if the run is extrimely long you will   need to use a 10mm cable, as 
this will have less voltage drop, and allow you for future expansion. 

your saw and extractor will draw maximum load on start up, and going on the 
figures you gave me this will be  around  14 or 15 amps, but you will be right 
at the limit of your fuze if you put in a 15 amp breaker. so this is why i 
would put in a 20 amp  on this circuit. 
it all depends on your heater, but if it is a 3 kw heater, you will need a 
further 15 amps for this. 
 and your 6 lights will need around 5 amps.
so adding this up, you have the potential to use around 35 amps when evrything 
is on. 
so for safety sake and allowing for future development, your instilation should 
be capable of taking around 45 amps on maximum load, so you should fuse your 
isolator   switch accordingly.

giving a choice i would get your spark to put in a 4 way board close to your 
saw, 
fused as follows. 
a 20 amp for your saw and extractor, 
a 15 amp circuit for your power outlets 
and a 10 amp circuit for your lighting.
the spare would be for future development such as drills and other power tools.
the other thing to take into consideration is how are you going to run your 
cable. is it overhead, or is it underground. 

there are specialist underground cables for this job, 
you can use what we call pyro, this is a special cable with a solid copper 
outer which is used as the earth conductor, but may not be a good idea if you 
are putting it anywhere it can get damaged. it also needs specialist crimping 
tools to make the ends.

my choice for underground would be either steel wire armoured, or twin pvc hi 
tuf.
if you are not sure what these are, please ask me for more details. 

best of luck, and if there is anything you  are not sure off, please email me 
back.
Dave & Sally. 
buy and sell your surplus free, join the new mailing group by sending a blank 
email to. [EMAIL PROTECTED]

or find more details here. 
http://www.secretsthatwekeep.com/thebargainstore/invite.htm


----- Original Message ----- 
From: John M 
To: blindhandyman@yahoogroups.com 
Sent: Friday, September 14, 2007 9:35 AM
Subject: [BlindHandyMan] 240Volt, 15Amp power supply for 3HP Table Saw+1½HP 
dust extractor.


G'day Dave & Sally,

John in Melbourne Australia here, I'm also a newboy to the list and I have 
enjoyed reading your, and all other Blind Handyman posts.  Good luck with 
that new lawn and petrol mower. Here, because we've been in severe drought 
for 10 years, I'm digging up my old brown weed crop and re-planting the 
front garden with flagstone!  :)


Dave, in a month or so I'm taiking delivery of a 10 inch, 3HP induction 
motor Cabinet Saw and a 1½Hp dust extractor.  They'll be set up to start 
together at switch on, and at switch off the Cabinet saw shuts down, while 
the dust extractor continues to run, on a time delay, for a further 30 
seconds or so.  Thus at switch on I'll be trying to pull 4½HP, or approx 
3,350Watts through my household wiring.
Moreover, if I should happen to have a sighted mate working with me at the 
time, and it's Winter, then I'll also have 6 fluorescent light tubes and an 
electric blow heater running.

Here, in Australia we're just like the UK and run a 240Volt 60hZ electrical 
power system, and all standard household power outlet sockets and plugs are 
3 pin.
 The household lighting circuits are rated at 10Amps and the power circuits 
are rated at 15Amps.  I don't know, but I think the safety switchboard is 
designed to trigger shutoff at 15Amps.  I certainly remember as a kid having 
to replace burnt out 15Amp fuse wires for me old Mum.  It was usually on 
wash days in mid Winter while she was doing the family Ironing, running the 
washing machine, the clothes dryer, the 2bar electric radiator while 
watching the Telly and making us kids cheesie toast under the electric 
grille.  And, mostly all of this power was taken off 1 power point with 
several piggy-backed double adaptors!  :)

OK Dave, so my questions are, what do I need to get a Sparky to do in my 
garage to avoid similar overload problems?  Would 1 dedicated 15Amp circuit 
be sufficient to run my Cabinet saw & dust extractor, or should I get 2 
separate dedicated 15Amp lines put in? Or, perhaps I should ask for a 
dedicated 20Amp line, or two to be installed?
:)

As you see from my words, while I'm OK at cutting, moulding, bending and 
shaping wood to my will, when it comes to electricity, I'm a total drongo. 
Thanks Dave, any advice would be much appreciated...see you in the Soup,

John M

Melbourne Australia.

From: dave and sally
To: blindhandyman@yahoogroups.com
Sent: Thursday, September 13, 2007 6:28 PM
Subject: [BlindHandyMan] electrical safety when plumbing with plastic


hi all,
forgive me as a new kid on the block for telling some of you how to suck 
eggs, and what i am about to point out may not apply in north america or 
canada, but it certainly applys here in the uk where our supply line is 
between 230 and 240 volts. so in case someone is on the list that this may 
effect, i feel i should point out a potential hazard of using plastic pipe.
living in northern ireland, we have used something similar to pex for a few 
years now. however there is one big disadvantage in using plastic piping of 
any kind, especially in europe.

i am not sure what the situation is in north america with the electrical 
supply, do you use an electrical earth connection? and if so how do you get 
this connection?
i know most of your supply lines are around 110 volts, and in some cases for 
cookers or stoves it may be in the region of 240 volts, but here in this 
part of the uk all our appliences that have a metal frame must be connected 
to an electrical safety earth.
for those who dont know what this is, it is a common wire that connects to 
the frame of evrything metal that has an electrical supply throughout the 
house. this includes dish washers, washing machines, stoves, water heaters 
and centeral heating, centeral air etc. this is to allow a faulty applience 
to be able to blow a fuze or trip before it kills someone.
now if the wireing has been done properly, there should be no problem, but 
the potential for electrical shock is high if someone who doesnt know what 
they are doing comes along and does a bit of handy work either to the 
plumbing or the electrical instillation.
heres why.

because all appliences and instilations with metal caseings need an 
electrical safety earth connection attached to them, here in the u.k. it is 
regulation that all metal pipes throughout the building is bonded together 
with at least a 6 mm copper wire. as i said earlier, if this is done 
properly and left alone , there should never be any problem. this is because 
on modern instillations the earth is taken from the supply cable at the 
meter board, and is common with the neutral return wire. however on old 
instillations, especially in the country areas where overhead supply cables 
are a common sight, more often than not the earth return path is made by 
either an earth spike, which in some instances is just connected to the 
water pipe at the point where it entered the house, or dread the thought, 
even by just relying on the old water main itself, which in days gone by was 
either copper or lead.
this worked well for many years, that was untill someone invented plastic 
pipe. because by breaking the continuity of the earth by replaceing a piece 
of damaged lead or copper pipe with plastic, they take away the safety 
aspect of having an earth connection which goes to earth, and subsiquently 
back to the municipal supply. in lots of cases this was never noticed untill 
someone developed a fault on the system. lets say you got a falty water 
heater that decided to short to the copper cylinder that it was enclosed in. 
if the earth was working properly, this would normally blow the fuse or trip 
switch. however because it now cant find a path back to earth via the old 
copper or lead pipe, it just sits there and looks for the path of least 
resistance to earth. hopefully this is not you! the applience may still 
work, however because the pipework in the house is acting as an electrical 
conductor, evrything else in the building on the household side of the 
plastic join will become live and have the potential of causing serious 
shock or death. this can happen if you dont know there is a problem and you 
grab onto something metal, such as your cooker or sink.
or if you disconnect any of the metal pipework at your hot water cylindar 
that is not cross bonded to all the other pipes that are close by.
this is only a couple of sinarios, there are of corse many other instances 
on how electrical shock can happen if there is not the proper care taken.
there is of corse an easy resolution to this potential problem, and that is 
should you ever have the need to replace a piece of metal pipe with plastic, 
you should also run a piece of 6 mm earth wireing along side it, and clamp 
it to the metal pipe on each side of the join. this ensures that the earth 
protection is not broken.
however if you are not sure where you get your earth supply from, just in 
case there is a fault that may not be evident, if possible you should 
consider switching off your electric supply when replaceing a section of 
existing metal pipework with plastic.
on no account should you grab on to both ends of the old pipework with both 
hands once it has been cut.
as i said earlier, forgive me if this does not apply to you, but it 
certainly will apply in some countrys throughout the world.
it is known for a voltage as low as 50 volts to cause serious damage to 
anyone who is not in good health, should they get it going to earth across 
their chest.
and if you must work on wireing that is live, do it with the knowlege that 
electricity is silent but deadly, so always have someone else around you 
when you are doing this..

heres a safety quote from a sparks point of view.

its the volts that jolt, its the mils that kill.
be safe, stay safe, and ask questions before you start working with plumbing 
or electric.
i can answer any questions on this subject should you wish to ask them.
best wishes to all,
Dave & Sally. 



To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

Visit The Blind Handy Man Files Page To Review Contributions From Various List 
Members At The Following address:
http://www.jaws-users.com/handyman/

Visit the archives page at the following address
http://www.mail-archive.com/blindhandyman@yahoogroups.com/  

If you would like to join the Blind Computing list, then visit the following 
address for more information:
http://jaws-users.com/mailman/listinfo/blind-computing_jaws-users.com

For a complete list of email commands pertaining to the Blind Handy Man list 
just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links




[Non-text portions of this message have been removed]

Reply via email to