Got a weird persistent issue which I'd like to know if anyone else has seen. We 
have a site with a 6503-E chassis, with a 720-3bxl in slot 1 and a 6516A-gbic 
in slot 3. It had been running fine (for 310 days) until recently the facility 
it's hosted at got very cold (supply air @ 15 degrees, hitting the base of the 
chassis through the in-rack floor vent). Then it started crashing until it 
warmed up and it was fine again.

It crashed each time with the same SP error:

%FABRIC-SP-3-DISABLE_FAB: The fabric manager disabled active fabric in slot 1 
due to the error (2) on this channel (FPOE 4) connected to slot 1

The most useful commands I found were:

#show fabric fpoe map
slot   channel   fpoe
 1        0       4
 1        1       0
 2        0       5
 2        1       14
 3        0       2
 3        1       11

#show fabric fpoe interface gi1/1
fpoe for GigabitEthernet1/1 is 4

#show fabric fpoe interface gi1/2
fpoe for GigabitEthernet1/2 is 4

Suggesting that the channel in question is for the supervisors' own onboard 
ports.

Now, once we realised it was temperature related, we decided to get it back to 
our lab and test it to see which component it was. So we simply swapped the 
whole unit out in one go - the chassis, line card, sup, both PSUs and PEMs 
included, even the fan tray. Only the 6 GBICs remained and were connected back 
into the new line card.

In the lab, we made it consistently fail around 17 degrees (it would last 
around 3 minutes at that temperature before crashing). If you took it to about 
21 degrees it would run all day just fine.

Then 2 days later, the new chassis we had installed back at the same site 
suddenly crashed. Believe it or not, with, you guessed it, exactly the same 
error!

It's running 15.1(1)SY1, doing full-table BGP to 5 other iBGP peers and has 
around 10 vlans and not a lot else. Average traffic around 500mbit/s total.

Previously to this failure, the (original) chassis had an uptime of 310 days 
(running an older IOS, we upgraded it when it got replaced).

Is it possible that a GBIC (the only component 'not' swapped) could cause this?

Any ideas or suggestions most welcome, as we've literally run out of components 
to swap over!

Cheers,


Robert Williams