Curious, how cold does it get, and what country are you in?

-----Original Message-----
From: Ron Johnson [mailto:[EMAIL PROTECTED] 
Sent: Monday, 5 February 2007 12:36
To: debian-user@lists.debian.org
Subject: Re: What UPS to buy

-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1

On 02/04/07 20:23, Kevin Coyner wrote:
> On Sun, Feb 04, 2007 at 08:11:12PM -0600, Ron Johnson wrote......
> 
>>> Some of APC's UPS units allow you to set the voltage sensitivity via dip
>>> switches, some of the units allow you to set it via software, and some
>>> don't let you adjust the sensitivity.  So if you plan to back up your
>>> battery powered UPS with an external generator, make sure to get a UPS
>>> with an adjustment for voltage sensitivity.
>> But then you're stepping out of the realm of SOHO UPSs, no?
> 
> Perhaps.  But depends on where you live and how often you experience power
> outages.  I live in the Northeast of the US, and we have power outages
> frequently, lasting anywhere from 30 min to 48 hrs.  So having a backup
> generator to keep the pipes from freezing and a few lights on is pretty

Isn't it obvious that God did not design people to live where their
peckers might freeze off?  Move south to God's Country!

> common.  Dedicating one circuit to a computer or two doesn't draw too many
> amps on the overall load so why not?  So if you live in a place that has
> frequent power outages, and you're in the market for a battery operated
UPS,
> why not get one with an ability to set voltage sensitivity just in case
you
> eventually add in an external generator.
> 

-----BEGIN PGP SIGNATURE-----
Version: GnuPG v1.4.6 (GNU/Linux)

iD8DBQFFxpf6S9HxQb37XmcRAsnCAJ9MGroJW/8IzoGEQ5nlk/2zHpi47ACbBCLt
WyIAgEjx1m7CiqvgTGYukdc=
=3Sxd
-----END PGP SIGNATURE-----


-- 
To UNSUBSCRIBE, email to [EMAIL PROTECTED] 
with a subject of "unsubscribe". Trouble? Contact
[EMAIL PROTECTED]




-- 
To UNSUBSCRIBE, email to [EMAIL PROTECTED] 
with a subject of "unsubscribe". Trouble? Contact [EMAIL PROTECTED]

Reply via email to