Hi Sebastian,

thanks fort he response, good to hear that it works now.
The stacktrace that you show could be related to the disconnect, indeed.
I remember that it was a bit tricky to get it right and if you would create a 
Jira I can try to look into it.

To your question regarding S7CommPlus (optimized datablocks):
We currently cannot but there is a long discussion around this topic (I would 
like it too).
The main issue is that we would need to reverse engineer some part of the TIA 
Libraries to extract private keys of a cryptographic challenge that is done 
during initial handshake which is illegal in Germany (“Hackerparagraph”).

But we are on the topic and have ideas for other ways around it as it would be 
really good to have this feature.

Julian

Von: Sebastian Wiendl <swie...@bhs-corrugated.de>
Antworten an: "dev@plc4x.apache.org" <dev@plc4x.apache.org>
Datum: Freitag, 8. November 2019 um 12:55
An: "dev@plc4x.apache.org" <dev@plc4x.apache.org>
Betreff: Antwort: Re: Antwort: Re: Configuring a S7-1500 for Access with PLC4J

Hi all,

news from my side: The logged exception happens during the disconnect phase. 
Connecting, pinging and reading values works just fine. Fun Fact: The 
communication works regardless of the specified rack/slot.

This is my updated program:


public static void main(String[] args) {
   try (PlcConnection plcConnection = new 
PlcDriverManager().getConnection("s7://172.30.74.65/0/0")) {
       System.out.println("connected");
       System.out.println(plcConnection);
       CompletableFuture<Void> ping = plcConnection.ping();
       ping.get(500, TimeUnit.MILLISECONDS);
       System.out.println("ping exception = " + 
ping.isCompletedExceptionally());

       // non optimized DB
       for (int i = 0; i < 3; i++) {
           PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
           final String fieldName = "field";
           builder.addItem(fieldName, "%DB101.DBW78:INT");
           PlcReadRequest readRequest = builder.build();
           LocalDateTime start = now();
           PlcReadResponse plcReadResponse = readRequest.execute().get();
           System.out.println("request took " + Duration.between(start, now()));
           System.out.println(fieldName + " response: " + 
plcReadResponse.getResponseCode(fieldName) + "; value: " + 
plcReadResponse.getInteger(fieldName));
       }

       try (BufferedReader br = new BufferedReader(new 
InputStreamReader(System.in))) {
           br.readLine();
       }
   } catch (Exception e) {
       e.printStackTrace();
   }
   System.out.println("disconnected");
}

The execution yields this output:

SLF4J: Failed to load class "org.slf4j.impl.StaticLoggerBinder".
SLF4J: Defaulting to no-operation (NOP) logger implementation
SLF4J: See http://www.slf4j.org/codes.html#StaticLoggerBinder for further 
details.
connected
org.apache.plc4x.java.s7.connection.S7PlcConnection@131276c2
ping exception = false
request took PT0.029S
field response: OK; value: 2
request took PT0.002S
field response: OK; value: 2
request took PT0.002S
field response: OK; value: 2

Nov 08, 2019 12:53:36 PM io.netty.channel.DefaultChannelPipeline 
onUnhandledInboundException
WARNUNG: An exceptionCaught() event was fired, and it reached at the tail of 
the pipeline. It usually means the last handler in the pipeline did not handle 
the exception.
java.io.IOException: Eine vorhandene Verbindung wurde vom Remotehost geschlossen
        at sun.nio.ch.SocketDispatcher.read0(Native Method)
        at sun.nio.ch.SocketDispatcher.read(SocketDispatcher.java:43)
        at sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:223)
        at sun.nio.ch.IOUtil.read(IOUtil.java:192)
        at sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:380)
        at 
io.netty.buffer.PooledUnsafeDirectByteBuf.setBytes(PooledUnsafeDirectByteBuf.java:288)
        at io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1125)
        at 
io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:347)
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:682)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:617)
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:534)
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:496)
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:906)
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
        at java.lang.Thread.run(Thread.java:748)

disconnected

The exception only shows after pressing enter, therefore during the disconnect. 
I think what i discovered is a non-issue. Not nice, but not stopping me.

BTW does PLC4J support reading optimized S7 DBs? If not, is support for this 
planned at some point in time?

Mit freundlichen Grüßen
Kind regards

Sebastian Wiendl
DSE / Digital Solutions Software Engineer
Phone: +49 9605 919 - 9341
E-Mail: swie...@bhs-world.com
Internet: www.bhs-world.com<https://www.bhs-world.com>
Shop: www.icorr.shop
________________________________
 [cid:_1_15253CC8152538CC00417B1CC12584AC]

BHS Corrugated Maschinen- und Anlagenbau GmbH
Paul-Engel-Straße 1
92729 WEIHERHAMMER
GERMANY

Management: Christian Engel, Lars Engel
Registered at Amtsgericht Weiden, HR B 1320

________________________________

[cid:_2_158FEFC0158FEE7000417B1CC12584AC]
[cid:_2_158FF6A4158FF2C000417B1CC12584AC]
[cid:_2_158FFC90158FF8AC00417B1CC12584AC]


[cid:_1_1590012C158FF9FC00417B1CC12584AC]




Von:        "Tim Mitsch" <t.mit...@pragmaticindustries.de>
An:        "dev@plc4x.apache.org" <dev@plc4x.apache.org>
Datum:        07.11.2019 17:47
Betreff:        Re: Antwort: Re: Configuring a S7-1500 for Access with PLC4J
________________________________



Hey Sebastian

Sorry for delayed answer – but first of all warm welcome on the list.

Just tested ur code-snippet vs our S7-1515 and is working fine.
U said u activated Put/Get.
Do u have the possibility to execute the scraper runner:
Plc4j/util/scraper/test/TriggeredScraperRunner

U need to adjust the ‘example_triggered_scraper.yml’ to ur needs (ip, field) …
Please take into account that the field to be read from must be a NON-optimized 
block

If there are still issue please write on the list and I can make a cross-check 
to the S7 Settings.

Best
Tim



Von: Sebastian Wiendl <swie...@bhs-corrugated.de>
Antworten an: "dev@plc4x.apache.org" <dev@plc4x.apache.org>
Datum: Donnerstag, 7. November 2019 um 16:29
An: "dev@plc4x.apache.org" <dev@plc4x.apache.org>
Betreff: Antwort: Re: Configuring a S7-1500 for Access with PLC4J

Hi Cesar,

thanks for your input.

s7://172.30.74.65/0/0 <http://172.30.74.65/0/2> is an illegal plc4j connection 
string. (The PLC's webserver is disabled btw.)

s7://172.30.74.65/0/0 yields the same exception as before.

I checked with our IT department in parallel - there is one router between me 
and the PLC and port 102 is open and reachable. No firewalls either.

Mit freundlichen Grüßen
Kind regards

Sebastian Wiendl
DSE / Digital Solutions Software Engineer
Phone: +49 9605 919 - 9341
E-Mail: swie...@bhs-world.com
Internet: 
www.bhs-world.com<https://www.bhs-world.com<https://www.bhs-world.com/>>
Shop: www.icorr.shop
________________________________
[cid:_1_150B9900150B9504005508A3C12584AB]

BHS Corrugated Maschinen- und Anlagenbau GmbH
Paul-Engel-Straße 1
92729 WEIHERHAMMER
GERMANY

Management: Christian Engel, Lars Engel
Registered at Amtsgericht Weiden, HR B 1320

________________________________

[cid:_2_150BB3DC150BAFF8005508A3C12584AB]
[cid:_2_150BB9C8150BB5E4005508A3C12584AB]
[cid:_2_150BBFB4150BBBD0005508A3C12584AB]


[cid:_1_150BC450150BBD20005508A3C12584AB]




Von:        "Cesar Garcia" <cesar.gar...@ceos.com.ve>
An:        "Apache PLC4X" <dev@plc4x.apache.org>
Datum:        07.11.2019 15:53
Betreff:        Re: Configuring a S7-1500 for Access with PLC4J
________________________________



Hello,

Try (*"s7://172.30.74.65/0/0 <http://172.30.74.65/0/2>")*

For S7-1200 and S7-1500 is Rack=0, Slot=0,

Best regards

El jue., 7 nov. 2019 a las 9:58, Sebastian Wiendl (<
swie...@bhs-corrugated.de>) escribió:

> Hello everyone,
>
> my sample program of PLC4J (very similiar to the hello world example)
> fails to connect to my test PLC (S7-1500):
>
> Nov 07, 2019 2:37:51 PM io.netty.channel.DefaultChannelPipeline
> onUnhandledInboundException
> WARNUNG: An exceptionCaught() event was fired, and it reached at the tail
> of the pipeline. It usually means the last handler in the pipeline did not
> handle the exception.
> java.io.IOException: Eine vorhandene Verbindung wurde vom Remotehost
> geschlossen
>         at sun.nio.ch.SocketDispatcher.read0(Native Method)
>         at sun.nio.ch.SocketDispatcher.read(SocketDispatcher.java:43)
>         at sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:223)
>         at sun.nio.ch.IOUtil.read(IOUtil.java:192)
>         at sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:380)
>         at
> io.netty.buffer.PooledUnsafeDirectByteBuf.setBytes(PooledUnsafeDirectByteBuf.java:288)
>         at
> io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1125)
>         at
> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:347)
>         at
> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>         at
> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:682)
>         at
> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:617)
>         at
> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:534)
>         at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:496)
>         at
> io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:906)
>         at
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
>         at
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>         at java.lang.Thread.run(Thread.java:748)
>
> "An existing connection was closed by the remote host"
>
> Thats my program at the moment:
>
>
>     *public static void *main(String[] args) {
>        *try *(PlcConnection plcConnection = *new *
> PlcDriverManager().getConnection(*"s7://172.30.74.65/0/2
> <http://172.30.74.65/0/2>"*)) {
>            System.*out*.println(*"connected"*);
>            System.*out*.println(plcConnection);
>            CompletableFuture<Void> ping = plcConnection.ping();
>            ping.get(500, TimeUnit.*MILLISECONDS*);
>            System.*out*.println(*"ping exception = " *+
> ping.isCompletedExceptionally());
>        } *catch *(Exception e) {
>            e.printStackTrace();
>        }
>        System.*out*.println(*"disconnected"*);
>    }
>
> I can both ping the PLC as well as connect to it with the Siemens TIA
> Portal. Does the PLC need some special configuration in the project to be
> reachable via S7Comm via ISO on TCP? nmap shows port 102 TCP as open.
>
> Any help is much appreciated!
>
> Mit freundlichen Grüßen
> Kind regards
>
>
> *Sebastian Wiendl *DSE / Digital Solutions Software Engineer
> Phone: +49 9605 919 - 9341
> <http://www.bhs-world.com<http://www.bhs-world.com/><http://www.bhs-world.com/>>E-Mail:
>  swie...@bhs-world.com
> Internet: www.bhs-world.com
> Shop: www.icorr.shop
> ------------------------------
>
>
>
> *BHS Corrugated Maschinen- und Anlagenbau GmbH *Paul-Engel-Straße 1
> 92729 WEIHERHAMMER
> GERMANY
>
> Management: Christian Engel, Lars Engel
> Registered at Amtsgericht Weiden, HR B 1320
> ------------------------------
>
>
>
>
>

--
*CEOS Automatización, C.A.*
*GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
*PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*

*FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
*Ing. César García*
*Cel: 0416-681.03.99*

*Cel: 0414-760.98.95*

*Hotline Técnica SIEMENS: 0800 1005080*

*Email: support.aan.automat...@siemens.com
<support.aan.automat...@siemens.com>*






Reply via email to