Hi Jonas,

I think I can possibly help you now … as I worked on the new Beckhoff driver I 
finally got to working with the ADS protocol.
I think the problem you are having is that the address you are using is simply 
not correct.

The PLC doesn’t find an address called “BOOL1” … After discussing things with 
the Beckhoff Tech-Staff I learned, that you should address resources with 
symbolic addresses like:

main.f_trigDateiGelesen.M:BOOL

Please note that there seems to be differences between TwinCat2 and TwinCat3 
devices regarding this symbolic address format. The older ones seem to simply 
start without the module name. Like: “.f_trigDateiGelesen.M:BOOL” (But I 
haven’t been able to verify this)

The other option would be to use fixed addresses, like:

0x0000f005/0x1a800000:BOOL

Which is however considered bad practice, as adding one single byte to the PLC 
could ruin all of your addesses.

Hope this helps a little more.

Chris



Von: "Hillenbrand, Jonas (wbk)" <[email protected]>
Antworten an: <[email protected]>
Datum: Mittwoch, 29. Juli 2020 um 11:25
An: "[email protected]" <[email protected]>
Betreff: How to compose Read requests for ADS Protocol with PLC4X?

Hi there,

I’m working on using the PLC4X framework within my research projects involving 
datalogging from Beckhoff PLC via ADS protocol.

I was able to connect with the PLC using the following code, but it fails on 
the line where the read request is executed:

PlcConnection plcConnection = null;
String connectionStr = " 
ads:tcp://127.0.0.1:48898/5.23.164.94.1.1:851/129.254.235.187.1.1:32835”;
try {
                        plcConnection = new 
PlcDriverManager().getConnection(connectionStr);
                        if (this.plcConnection.isConnected()){
                                    if (!this.isAdsReadable() || 
!this.isAdsWritable() || !this.isAdsSubscribable()) {
                                               return false;
                                   }
                                   this.logger.log("Connected successfully with 
" + connectionStr);
                                   return true;
                        } else {
                                   this.logger.log(Level.ERROR, "Could not 
connect with " + connectionStr);
                                   return false;
                        }
            } catch (PlcConnectionException e) {
                        // TODO Auto-generated catch block
                        this.logger.log(e);
                        return false;
            }
            PlcReadRequest.Builder builder =plcConnection.readRequestBuilder();
            builder.addItem(“BOOL1”, "BOOL1:BOOL");                      // 
Boolean variable in GVL (global) list of SPS Project
            PlcReadRequest readRequest = builder.build();
            PlcReadResponse response = null;
            try {
                        response = readRequest.execute().get();                 
// CODE FAILS HERE
            } catch (InterruptedException e) {
                        // TODO Auto-generated catch block
                        this.logger.log(e);
            } catch (ExecutionException e) {
                        // TODO Auto-generated catch block
                        this.logger.log(e);
            }

Console Output:
        Connected successfully with 
ads:tcp://127.0.0.1:48898/5.23.164.94.1.1:851/129.254.235.187.1.1:32835

Exception in thread "main" 
org.apache.plc4x.java.api.exceptions.PlcRuntimeException: Non error code 
received Result{AdsReturnCode{hex=0x0710, dec=1808, description='symbol not 
found', possibleCauses='', solution=''}}
        at 
org.apache.plc4x.java.ads.connection.AdsAbstractPlcConnection.lambda$mapFields$3(AdsAbstractPlcConnection.java:184)
        at 
java.base/java.util.concurrent.ConcurrentHashMap.computeIfAbsent(ConcurrentHashMap.java:1708)
        at 
org.apache.plc4x.java.ads.connection.AdsAbstractPlcConnection.mapFields(AdsAbstractPlcConnection.java:163)
        at 
java.base/java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:183)
        at 
java.base/java.util.stream.ReferencePipeline$3$1.accept(ReferencePipeline.java:195)
        at 
java.base/java.util.stream.ReferencePipeline$2$1.accept(ReferencePipeline.java:177)
        at 
java.base/java.util.LinkedList$LLSpliterator.forEachRemaining(LinkedList.java:1242)
        at 
java.base/java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:484)
        at 
java.base/java.util.stream.ForEachOps$ForEachTask.compute(ForEachOps.java:290)
        at 
java.base/java.util.concurrent.CountedCompleter.exec(CountedCompleter.java:746)
        at 
java.base/java.util.concurrent.ForkJoinTask.doExec(ForkJoinTask.java:290)
        at 
java.base/java.util.concurrent.ForkJoinTask.doInvoke(ForkJoinTask.java:408)
        at 
java.base/java.util.concurrent.ForkJoinTask.invoke(ForkJoinTask.java:736)
        at 
java.base/java.util.stream.ForEachOps$ForEachOp.evaluateParallel(ForEachOps.java:159)
        at 
java.base/java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateParallel(ForEachOps.java:173)
        at 
java.base/java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:233)
        at 
java.base/java.util.stream.ReferencePipeline.forEach(ReferencePipeline.java:497)
        at 
org.apache.plc4x.java.ads.connection.AdsAbstractPlcConnection.mapFields(AdsAbstractPlcConnection.java:157)
        at 
org.apache.plc4x.java.ads.connection.AdsAbstractPlcConnection.read(AdsAbstractPlcConnection.java:103)
        at 
org.apache.plc4x.java.base.messages.DefaultPlcReadRequest.execute(DefaultPlcReadRequest.java:44)
        at 
net.sytes.botg.ads.MyADSClient.executeReadRequest(MyADSClient.java:108)
        at 
net.sytes.botg.ads.UnitTest_MyADSClient.test2(UnitTest_MyADSClient.java:60)
        at 
net.sytes.botg.ads.UnitTest_MyADSClient.main(UnitTest_MyADSClient.java:44)

Could anybody offer some help? Am I constructing the item for the read request 
correctly, what if I’m trying to read variables in a subroutine let’s say in 
the Project “1Achser” my PLC Project name is “SPSObject” and I have a PRG block 
named “MainGUI”, in there I have the variable “CurPos [LREAL]”, how would I 
conceive the addItem Method?  --> builder.addItem(“CurPos”, 
"1Achser.SPSObject.MainGUI.CurPos:LReal")?

Anyhelp would be appreciated.

And by the way, I like the idea of PLC4X very much and love to contribute, 
given that I can make it work for my setup :D

Best Regards
Jonas

Reply via email to