Hi Vlad,

just a last advise, I have tried once to open more than one connection
to a Siemens 1200 PLC with a multithread application and I got a problem
of disconnection similat to your.
In my code the disconnection was systematic when the second thread try
to enstablish a connection.

My suggestion is to ensure that your code use just a single connection
to the PLC, in this way you should reach a more stable solution.

Regards,
S.
 

On 17/09/2020 13:01, Vladyslav Milutin wrote:
> Hi Christofer,
>
> I can't access this machine where I got this exception, that's the problem,
> I just got logs from the machine.
>
> Kind regards,
> Vlad
>
> чт, 17 сент. 2020 г. в 13:38, Christofer Dutz <[email protected]>:
>
>> Hi Vlad,
>>
>> Your code says TCP ... so it should work, if you use WireShark on the
>> machine that is
>> trying to connect to the remote you won't even need the promiscuous mode.
>>
>>
>> Chris
>>
>>
>> Am 17.09.20, 12:26 schrieb "Vladyslav Milutin" <[email protected]>:
>>
>>     Hi Christofer,
>>
>>     Thanks for your advice, I'm not sure that I can use wireshark in my
>> case :(
>>     Thanks for your answers, I'll try to create a watchdog for it and look
>> for
>>     the connection statuses.
>>
>>     Kind regards,
>>     Vlad
>>
>>     чт, 17 сент. 2020 г. в 13:02, Christofer Dutz <
>> [email protected]>:
>>
>>     > Hi Vlad,
>>     >
>>     > I didn't miss the email, but for me it's almost impossible to give
>> you an
>>     > advice to what might be going wrong.
>>     > The error you are getting I usually got in the past as soon as I
>> send out
>>     > something the PLC doesn't like.
>>     > Just recently when we didn't reset the message-id counters and they
>>     > overflowed, some PLCs just hung up.
>>     >
>>     > So what I would do, would be to use WireShark to check what's
>> actually
>>     > going over the wire and to check if this is ok.
>>     > If it's not, well you know what to fix.
>>     >
>>     > Chris
>>     >
>>     >
>>     > Am 17.09.20, 11:56 schrieb "Vladyslav Milutin" <[email protected]>:
>>     >
>>     >     Hi guys,
>>     >
>>     >     I just will resend this message in case you missed it.
>>     >
>>     >     Hi guys,
>>     >
>>     >     I can send you this code, which doesn't have much business
>> logic, and
>>     > all
>>     >     params are renamed.
>>     >
>>     >     public abstract class LalelDriver<T extends Message> extends
>>     >     GeneratedDriverBase<T> {
>>     >
>>     >         private final ChannelHandler handler;
>>     >
>>     >         @Override
>>     >         public String getProtocolName() {
>>     >             return "Lalel";
>>     >         }
>>     >
>>     >         @Override
>>     >         protected Class<? extends Configuration>
>> getConfigurationType() {
>>     >             return LalelConfiguration.class;
>>     >         }
>>     >
>>     >         @Override
>>     >         protected String getDefaultTransport() {
>>     >             return "tcp";
>>     >         }
>>     >
>>     >         @Override
>>     >         protected boolean canSubscribe() {
>>     >             return true;
>>     >         }
>>     >
>>     >         @Override
>>     >         protected LalelFieldHandler getFieldHandler() {
>>     >             return new LalelFieldHandler();
>>     >         }
>>     >
>>     >         @Override
>>     >         protected void initializePipeline(ChannelFactory
>> channelFactory) {
>>     >             try {
>>     >                 final Channel channel =
>>     >     channelFactory.createChannel(this.handler);
>>     >
>>  channelFactory.initializePipeline(channel.pipeline());
>>     >
>>     >             } catch (PlcConnectionException e) {
>>     >                 log.error("Failed to create channel");
>>     >             }
>>     >         }
>>     >     }
>>     >
>>     >     public classLalelDriverTcp extends LalelDriver<EthernetMessage> {
>>     >
>>     >         public LalelDriverTcp(final ChannelHandler handler){
>>     >             super(handler);
>>     >         }
>>     >
>>     >         @Override
>>     >         public String getProtocolCode() {
>>     >             return "lalel-tcp";
>>     >         }
>>     >
>>     >         @Override
>>     >         protected ProtocolStackConfigurer<EthernetMessage>
>>     > getStackConfigurer()
>>     >     {
>>     >             return DriverUtils.buildStackConfigurer(
>>     >                     EthernetMessage.class, EthernetMessageIO.class,
>>     >                     LalelProtocolLogicTcp.class,
>> ByteLengthEstimator.class
>>     >             );
>>     >         }
>>     >
>>     >         /**
>>     >          * Estimate the Length of a Packet
>>     >          */
>>     >         public static class ByteLengthEstimator implements
>>     >     ToIntFunction<ByteBuf> {
>>     >             @Override
>>     >             public int applyAsInt(ByteBuf byteBuf) {
>>     >                 if (byteBuf.readableBytes() >= 2) {
>>     >                     return
>>     > byteBuf.getUnsignedShortLE(byteBuf.readerIndex());
>>     >                 }
>>     >                 return -1;
>>     >             }
>>     >         }
>>     >
>>     >     }
>>     >
>>     >     And connection code:
>>     >
>>     >             this.connection = driver.getConnection(connectionString);
>>     >
>>     >             this.connection.connect();
>>     >
>>     >
>>     >     Kind regards,
>>     >     Vlad
>>     >
>>     >
>>     >     Kind regards,
>>     >     Vlad
>>     >
>>     >     чт, 17 сент. 2020 г. в 12:09, Christofer Dutz <
>>     > [email protected]>:
>>     >
>>     >     > Hi Vlad,
>>     >     >
>>     >     > 0.8.0-SNAPSHOT is the current development version ...
>>     >     > we'll be releasing that as soon as we tied up some things we're
>>     > currently
>>     >     > working on.
>>     >     >
>>     >     > Chris
>>     >     >
>>     >     >
>>     >     >
>>     >     > Am 17.09.20, 11:02 schrieb "Vladyslav Milutin" <
>> [email protected]>:
>>     >     >
>>     >     >     Hi Stefano,
>>     >     >
>>     >     >     I'm curious about the 0.8.0 version, where I can find it?
>> Since
>>     > maven
>>     >     > repo
>>     >     >     contains the latest version 0.7.0.
>>     >     >
>>     >     >     Kind regards,
>>     >     >     Vlad
>>     >     >
>>     >     >     ср, 16 сент. 2020 г. в 17:30, Stefano Bossi <
>>     > [email protected]>:
>>     >     >
>>     >     >     > Hi Vlad,
>>     >     >     >
>>     >     >     > this seems similar to a bug fixed some time ago, I am not
>>     > really
>>     >     > sure but
>>     >     >     > it worth to try to use the 0.8.0 version where this fix
>> is
>>     > present.
>>     >     >     >
>>     >     >     > You should try to build the version and here you could
>> fine
>>     > some
>>     >     > help:
>>     >     >     > https://plc4x.apache.org/developers/index.html
>>     >     >     >
>>     >     >     > Regards,
>>     >     >     > Stefano
>>     >     >     >
>>     >     >     > On 16/09/2020 14:32, Vladyslav Milutin wrote:
>>     >     >     >
>>     >     >     > Hello guys,
>>     >     >     >
>>     >     >     > I'm writing to you with a hope that you can help me with
>>     > exception
>>     >     >     > handling.
>>     >     >     > Currently after a long time connection can be reset by
>> peer.
>>     > See
>>     >     > stacktrace
>>     >     >     > below.
>>     >     >     >
>>     >     >     > I've tried to add a custom ChannelHandler which Overrides
>>     >     > exceptionCaught()
>>     >     >     > and add it in Driver#initializePipeline() see code
>> below. Also
>>     > has
>>     >     > tried to
>>     >     >     > add a channel that can be obtained from
>>     > DefaultNettyPlcConnection.
>>     >     > And none
>>     >     >     > of them actualy was added to the pipeline where this
>> exception
>>     > was
>>     >     > thrown.
>>     >     >     >
>>     >     >     > plc4x version: 0.7.0
>>     >     >     >
>>     >     >     > StatckTrace:
>>     >     >     > 2020-09-16 13:50:03.340 WARN  [nioEventLoopGroup-58-1]
>>     >     >     > [io.netty.channel.DefaultChannelPipeline]
>>     >     > onUnhandledInboundException - An
>>     >     >     > exceptionCaught() event was fired, and it reached at the
>> tail
>>     > of the
>>     >     >     > pipeline. It usually means the last handler in the
>> pipeline
>>     > did not
>>     >     > handle
>>     >     >     > the exception.
>>     >     >     > java.io.IOException: Connection reset by peer
>>     >     >     >   at java.base/sun.nio.ch
>> .FileDispatcherImpl.read0(Native
>>     > Method)
>>     >     >     >   at java.base/sun.nio.ch
>>     >     > .SocketDispatcher.read(SocketDispatcher.java:39)
>>     >     >     >   at
>>     >     >
>> java.base/sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:276)
>>     >     >     >   at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:233)
>>     >     >     >   at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:223)
>>     >     >     >   at java.base/sun.nio.ch
>>     >     > .SocketChannelImpl.read(SocketChannelImpl.java:358)
>>     >     >     >   at
>>     > io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:253)
>>     >     >     >   at
>>     >     >
>> io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1133)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:350)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:714)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:650)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:576)
>>     >     >     >   at
>>     > io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:493)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:989)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
>>     >     >     >   at
>>     >     >     >
>>     >     >
>>     >
>> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>>     >     >     >   at java.base/java.lang.Thread.run(Thread.java:834)
>>     >     >     >
>>     >     >     > Driver#initializePipeline:
>>     >     >     >         try {
>>     >     >     >             final Channel channel =
>>     >     >     > channelFactory.createChannel(this.handler);
>>     >     >     >
>>     >  channelFactory.initializePipeline(channel.pipeline());
>>     >     >     >
>>     >     >     >         } catch (PlcConnectionException e) {
>>     >     >     >             log.error("Failed to create channel");
>>     >     >     >         }
>>     >     >     >
>>     >     >     > ChannelHandler:
>>     >     >     >     @Override
>>     >     >     >     public void exceptionCaught(ChannelHandlerContext
>> ctx,
>>     > Throwable
>>     >     > cause)
>>     >     >     > {
>>     >     >     >         log.warn("ExceptionCaught in worker: ctx = [{}],
>> cause
>>     > =
>>     >     > [{}, {}],
>>     >     >     > workerName = [{}]",
>>     >     >     >                 ctx, cause.getClass(),
>> cause.getMessage(),
>>     >     > workerName);
>>     >     >     >         if (cause instanceof ConnectTimeoutException) {
>>     >     >     >             log.warn("ConnectionTimeout caught:
>> workerName =
>>     > [{}]",
>>     >     >     > workerName);
>>     >     >     >         }
>>     >     >     >         if ((cause instanceof IOException) &&
>>     >     >     > cause.getMessage().contains("Connection reset by peer"))
>> {
>>     >     >     >             log.warn("Connection reset by peer caught:
>>     > workerName =
>>     >     > [{}]",
>>     >     >     > workerName);
>>     >     >     >         } else {
>>     >     >     >             log.info("Unexpected exception caught:
>> workerName
>>     > =
>>     >     > [{}]",
>>     >     >     > workerName);
>>     >     >     >         }
>>     >     >     >
>>     >     >     >         this.callback.accept(cause);
>>     >     >     >     }
>>     >     >     >
>>     >     >     > DefaultNettyPlcConnection#channel:log.info("Trying to
>> get
>>     >     > connection channel: worker name = [{}]",
>>     >     >     > this.workerName);
>>     >     >     >         final Channel channel =
>> ((DefaultNettyPlcConnection)
>>     >     >     > this.connection).getChannel();
>>     >     >     >         log.info("Channel obtained successfully. Adding
>> custom
>>     >     >     > channelHandler to it: channel = [{}], workerName = [{}]",
>>     > channel,
>>     >     >     > this.workerName);
>>     >     >     >         channel.pipeline().addLast(this.channelHandler);
>>     >     >     >         log.info("ChannelHandler added: channel = [{}],
>>     >     > channelHandler =
>>     >     >     > [{}], workerName = [{}]", channel, this.channelHandler,
>>     >     > this.workerName);
>>     >     >     >
>>     >     >     > Kind regards,
>>     >     >     > Vlad
>>     >     >     >
>>     >     >     >
>>     >     >     >
>>     >     >     >
>>     >     >
>>     >     >
>>     >
>>     >
>>
>>