Hi all,

Myhongk just brought up an issue in the Modbus driver, which I think could 
probably also come up in other protocols.

When reading a BOOL or BOOL[] the driver generally reads chunks of 16 bits 
(words). Now we need to define how we count the bits.

Currently when reading a simple BOOL we do this (0 = skipped, 1 = read):

00000000 00000001

So, the least significant bit is the value and the ones before are skipped.

When reading an array, we currently start at the end. So reading BOOL[6] would 
be this:

11111100 00000000

In this case we start at the most significant bits.

Both variants have its logic and it's downsides.

Downside by starting at the least significant bits is as soon as we read more 
than 16 bits.
So, if we read BOOL[19] we'd probably have this

XXXXXXXX XXXXXXXX 00000000 00000XXX

Where the indexes in the array would probably be:

15 14 13 12 11 10 9     8 7 6 5 4 3 2 1 0   X X X X X X X X    X X X X X 18 17 
16

Or would it be different?

Another option would be to start at the end of the last word read and to count 
"from right to left"


If we start at the most significant bits, it would make things easier for 
multiple elements, as we'd have this for BOOL[19]:

0 1 2 3 4 5 6 7 8     9 10 11 12 13 14 15     16 17 18 X X X X X     X X X X X 
X X X

But we would have only read the register value: 32768 or 0x8000 as "True".


Would be cool to know what's the default industry way to do thins (I'm sort of 
expecting an "it depends").
Possibly we could make it configurable (Which would complicate things a bit).

Another thing is ... in S7 we can address parts of a byte as BOOL by using a 
Bit address ... would it be cool to extend the Modbus to allow this too?

So something like this would work:

500001.4:BOOL[3]

Which would return (assuming we start counting at the most significant bit):

X X X X X 1 2 3    X X X X X X X X


Feedback highly appreciated :-)

Chris