Thanks for the thoughts.

Would you recommend any one of the "soft PLC" projects that I should look at 
further.
Certainly I think the idea of a PLC emulator is too ambitious.
I think the minimum effort approach, though still lots of effort, is too run 
the PLC code using the standard propriety tools in a VM and the to drive the 
input output of this VM with software to simulate the connection to hardware.

On Wed, May 4, 2022, at 11:18 AM, Łukasz Dywicki wrote:
> Hey Chris,
> Sorry for mixing authorship. I didn't check simulator since a while, 
> hence was not certain if its up to date.
>
> My point is about reusing network layer which PLC4X provides in order to 
> simulate a device. This is how you normally interact with PLC so it is a 
> natural way to make an "integration test" at this level. It is not 
> beyond typical BDD which is more about defining scenarios. How they are 
> actually executed depend on a BDD toolkits and how they integrate with 
> test or build environment.
> I get that scope of Peter work is to emulate a PLC runtime, that's why I 
> mentioned IEC grammars (so he can somehow parse or compile entire 
> program), which is the hardest part.
> Once program can be interpreted and executed (ie. by turning ST into 
> LLVM and firing graalvm or c runtime or simply running it with one of 
> existing tools such as openplc), the remaining part will be possible 
> after proper adoption of code generated from MSpec.
> Looking at amount of "soft plc" projects I have no doubts that its 
> possible. Its just matter of how much time and simplifications we can 
> accept.
> I agree that we don't have a capacity nor will to dive into even more 
> specific parts of how PLCs work. If somebody else has such interest I 
> will definitely look for results and see if we could improve our part 
> afterwards.
>
> Best,
> Łukasz
>
> On 4.05.2022 09:09, Christofer Dutz wrote:
>> Hi Lukasz,
>> 
>> I intentionally didn't mention the simulator, as I understood Peter, that 
>> he's looking for something to run his PLC programs on for testing. Yes, the 
>> simulator we have could be used to simulate being a PLC, but it can't 
>> actually simulate the PLC itself. That's not the scope of that thing. I 
>> think implementing the internal stuff needed to create a simulator where you 
>> can deploy a program from TIA Portal is totally unthinkable, considering how 
>> many different PLCs are out there.
>> 
>> Perhaps we should name it differently in order to manage expectations. 
>> "plc-mock"?
>> 
>> And our simulator was actually created by me and it's up-to-date and we just 
>> recently checked that it still works with the StreamPipes folks, as they 
>> were looking for something to use in their StreamPipes integration-tests.
>> 
>> Chris
>> 
>> -----Original Message-----
>> From: Łukasz Dywicki <[email protected]>
>> Sent: Dienstag, 3. Mai 2022 22:47
>> To: [email protected]
>> Cc: [email protected]
>> Subject: Re: Scope of using PLC4x as simulated driver for PLC projects
>> 
>> Hey Peter, welcome on mailing lists. First of all thank you for showing a 
>> interest in a project and bringing interesting topic!
>> 
>> Just to oppose a little bit what Chris says, I would say there is no real 
>> blocker for trying to do a PLC simulator within PLC4X. We do (or
>> did) have a S7 simulator in sandbox already. It was built a while ago by 
>> Julian based on netty tcp server and I think 0.6 structures, so it might be 
>> a little bit behind of what we currently have in a develop branch.
>> 
>> Technically speaking what you need in most of the cases is launching a TCP 
>> server (in case of ADS/Modbus/S7) or a serial receiver (Modbus RTU/till some 
>> degree CANopen) and answering requests which come over such communication 
>> channel. If you get closer to basic fieldbus like a Modbus RTU or CANopen 
>> difference between sending a request and answering it is not that large.
>> Few remarks - we currently do not have any support beside mentioned sandbox 
>> project. If you decide to do such thing, it will be a far away from a 
>> realtime, yet TCP/UDP stuff involving IP routing by definition is not! You 
>> will still have to invest a ton of time in order to mimic a complete PLC 
>> behavior. I suppose it might be problematic to keep it up with manufacturer 
>> tooling, simply cause they can share some libraries or specifications unseen 
>> by any of us. Also a device behavior can change with firmware upgrade, so 
>> you have to keep a close look on that.
>> If you can sacrifice realtime requirement which is often crucial to 
>> certification, live with above simplifications and caveats, then 
>> infrastructure available in PLC4X will serve you better than any other open 
>> source components available out there.
>> 
>> Before we go too optimistic, a fairly common problems is how devices react 
>> on read/write operations. Each brand does it in an unique way, some models 
>> have extended functionality, plus each device report errors differently. 
>> There is also handling of parallel/overlapping requests which we handle 
>> partially even in client side.
>> ADS for example has an internal notion of an routing table which is somehow 
>> associated with communication peer, it has support for read single and read 
>> multiple addresses, it has also support for subscriptions which you have to 
>> coordinate. If you are not afraid of it, the communication structures will 
>> be provided by MSpec. :)
>> 
>> I think that this is still a major advantage of MSpec approach and code 
>> generation framework provided by PLC4X which awaits more use cases.
>> MSpec gives us a symmetric read/write operations which we prove through 
>> serialization unit tests. This is unseen in most of libraries as they 
>> usually focus on one of the sides - either a client/master or server/slave 
>> structures and handle only half which is needed by them. A prime example 
>> could be a S7 client which does a request serialization and reply 
>> deserialization or S7 server which does request serialization and response 
>> serialization. Code generated by PLC4X handles both ways.
>> Even if we miss a support for making server side framework, its something 
>> you can definitely do on top of what PLC4X provide.
>> An interesting benefit you could get from relying on PLC4X is possibility to 
>> make a test of different communications for assumed simulation logic. If you 
>> find a way for example to write a PLC program in some portable way, then by 
>> mapping such program inputs and outputs to PLC specific communication 
>> semantics you get a very nice training suite.
>> If you search for ie. ANTRL IEC 61131-3 you will find a bunch of grammar 
>> files allowing to parse structured text programs. From there you "just"
>> need to make interpreter working with one of languages supported by PLC4X 
>> code generators.
>> Making a partial toolkit, even for a single brand/product line, is a lot of 
>> work and code to be made. This code is potentially hard to maintain due to 
>> various firmware versions, yet nothing really blocks you from trying. Do 
>> your thing and report your findings if you wish. I am eager to hear your 
>> feedback. I believe with your work we could improve our client side 
>> implementations too!
>> 
>> Cheers,
>> Łukasz
>> 
>> On 3.05.2022 13:55, Christofer Dutz wrote:
>>> Hi Peter,
>>>
>>> well simulating a real PLC generally would totally be out of scope of 
>>> PLC4X. I was more referring to the code to extract the program from a PLC 
>>> and to deploy it somewhere (like in a simulator or in case of Codesys you 
>>> could run the runtime on a test-server). But there are simulators out 
>>> there. Usually, the PLC vendors have them. Unfortunately, they usually are 
>>> not for free. But I know Siemens has various simulators to which you could 
>>> deploy your program and then interact with PLC4X.
>>>
>>> Well, I guess you would need to find out how to make a software like TIA 
>>> portal believe your application is a S7 PLC and then need to implement the 
>>> parts of the protocol, that we haven't implemented yet. As S7 doesn't have 
>>> a public spec, you'll have to reverse engineer most of it. And another 
>>> problem will be that newer S7 devices use S7comm ... to convince TIA that 
>>> you're a real device, you would probably need to implement the S7comm 
>>> protocol, which opens a whole new box of worms.
>>>
>>> All in all, I think the industry would need such a solution, but I also 
>>> think they haven't realized it yet and therefore are not willing to pay the 
>>> money for it.
>>>
>>> Perhaps I'll try this concept out as part of my job, but that will probably 
>>> only have an effect on the types of PLCs that we use, and I have no idea, 
>>> if I'll get the time needed to do it.
>>>
>>> Chris
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: Peter Saxton <[email protected]>
>>> Sent: Dienstag, 3. Mai 2022 13:30
>>> To: [email protected]
>>> Subject: RE: RE: Scope of using PLC4x as simulated driver for PLC
>>> projects
>>>
>>> Hi Chris,
>>>
>>> Thanks for the clarification. So potentially PLC4X could drive the tests 
>>> but would leave the problem of simulating a PLC as outstanding.
>>> One other approach I have head about is putting the PLC in a
>>> completely virtual environment and then manipulating it by setting
>>> values on the Virtual Machine. I don't have much information on this
>>> approach just this blog post
>>> https://www.plcnext-community.net/makersblog/painful-memories-of-plc-s
>>> imulations/
>>>
>>> You mentioned that you had though about working on something like this. 
>>> What would be the rough shape of your solution? Apart from industry 
>>> resistance what would be the hardest thing to get through in this project.
>>> In my area there is a desire to embrace testing and CI probably not CD that 
>>> seems bold. At least the right noises are being made. We can see how it 
>>> plays out.
>>>
>>> Peter
>>>
>>>
>>> On 2022/05/03 08:17:49 Christofer Dutz wrote:
>>>> Hi Peter,
>>>>
>>>> Well, if you want to use PLC4X to communicate with the real or the 
>>>> simulated PLC in order to execute various test-scenarios: then probably 
>>>> PLC4X is what you're looking for.
>>>>
>>>> If you want to extract the PLC program from one PLC and write that to a 
>>>> simulator, then unfortunately PLC4X doesn't have that focus and therefore 
>>>> doesn't support this.
>>>>
>>>> The programming part of automation engineering is what every PLC vendor 
>>>> implements separately. Sometimes even one vendor has multiple ways of 
>>>> doing that for their different products.
>>>>
>>>> However, PLC4X does have the parts that you probably need to implement 
>>>> such a feature, however it will certainly require reverse engineering for 
>>>> almost every type of PLC.
>>>>
>>>> I had been thinking about starting to work on something like what you 
>>>> describe. However, my idea would have been to simulate just enough of a 
>>>> PLC for the engineering tool to accept it and to have the Engineering tool 
>>>> deploy the new program to that instead of a real PLC. This component would 
>>>> then pass the program to a CI/CD pipeline, just as you describe it. 
>>>> However, I knew this would be a lot of work and considering how well the 
>>>> industry accepted my offers in the past, I decided that I won't do this, 
>>>> as it's not worth it. They haven't even started thinking of concepts like 
>>>> continuous-integration or continuous-delivery or even testing.
>>>>
>>>> Chris
>>>>
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: Peter Saxton <[email protected]>
>>>> Sent: Dienstag, 3. Mai 2022 09:35
>>>> To: [email protected]
>>>> Subject: Scope of using PLC4x as simulated driver for PLC projects
>>>>
>>>> Hi everyone.
>>>>
>>>> First post here so apologies if my terminology is a bit off, I'm from a 
>>>> web software background.
>>>>
>>>> If I want to write behavior tests for a PLC project that already exists, 
>>>> is PLC4x the right tool for that job or would there be something better?
>>>>
>>>> Ideally I would be able to export a whole PLC project from a machine. 
>>>> Start that exported project in a soft/simulated PLC environment and run a 
>>>> suite of tests against the PLC logic. Ideally at no point would I be 
>>>> reliant on having the correct hardware.
>>>>
>>>> Reading through the PLC4x pages I found the section on "Testing (or using 
>>>> PLC4X without a PLC)". As I understand this this is for testing software 
>>>> outside the PLC but simulating a PLC. I would like to go the other way 
>>>> round and test a PLC project by simulating the outside world. I also 
>>>> looked at the section on the simulated protocol, but again I think this is 
>>>> for simulating values for a plc4x client.
>>>>
>>>> Essentially we'd like to write a test saying "when input 1 & 2 are on the 
>>>> output A is live", and check that the PLC code was going to do this.
>>>>
>>>> I'm interested in testing against Siemens PLC projects, however for 
>>>> getting started I would happily run a proof of concept on something like 
>>>> OpenPLC if that was easier without hardware.
>>>>
>>>> Cheers, Peter
>>>>

Reply via email to