takraj opened a new issue, #1100:
URL: https://github.com/apache/plc4x/issues/1100

   ### What happened?
   
   OPC-UA connections get dead after session timeout, which is hard-coded to 2 
minutes in the driver. After this timeout, any request made with this 
connection object fails with `INTERNAL_ERROR`. In case of subscriptions, an 
even worse `ClassCastException` gets thrown internally, complaining about being 
unable to cast a `ServiceFault` to a response object, and because of this, the 
future object earlier returned by `request.execute()` never get completed.
   
   This is especially a problem when using `plc4j-connection-pool`, which keeps 
a set of connection objects open, and thus users of the pool might get these 
dead connections.
   
   The session timeout value is hard-coded in 
[SecureChannel.java:400](https://github.com/apache/plc4x/blob/cac8254518540d6353546fcf7619203e2f64e721/plc4j/drivers/opcua/src/main/java/org/apache/plc4x/java/opcua/context/SecureChannel.java#L400)
   
   Simplest code to reproduce the issue:
   ```
   PlcDriverManager driverManager = new PlcDriverManager();
   try (PlcConnection opcuaConnection = 
driverManager.getConnection("opcua:tcp://opcuaserver.com:48010")) {
       PlcReadRequest request = opcuaConnection.readRequestBuilder()
               .addItem(
                       "Demo",
                       "ns=2;s=Demo.Static.Scalar.String"
               )
               .build();
   
       PlcReadResponse response1 = request.execute().get();
       System.out.println("RESPONSE 1: " + response1.getObject("Demo"));
   
       Thread.sleep(3 * 60 * 1000); // 3 minutes
   
       PlcReadResponse response2 = request.execute().get();
       System.out.println("RESPONSE 2: " + response2.getObject("Demo"));
   }
   ```
   
   Expected behavior would be to transparently recover from the error, and to 
create a new session internally.
   
   ### Version
   
   v0.10.0
   
   ### Programming Languages
   
   - [X] plc4j
   - [ ] plc4go
   - [ ] plc4c
   - [ ] plc4net
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] CANopen
   - [ ] DeltaV
   - [ ] DF1
   - [ ] EtherNet/IP
   - [ ] Firmata
   - [ ] KNXnet/IP
   - [ ] Modbus
   - [X] OPC-UA
   - [ ] S7


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: dev-unsubscr...@plc4x.apache.org.apache.org

For queries about this service, please contact Infrastructure at:
us...@infra.apache.org

Reply via email to