Hi Luiz,

The mod should already be available in the development branch.

I Performed tests using Odot equipment against the S7-300 and S7-400.

I still have things to do regarding event management, diagnostics and other
functionalities, but it will be the weekend.

Waiting for your comments,

Kind regards,

El mar, 16 jul 2024 a las 20:33, Luiz doleron (<[email protected]>)
escribió:

> Hi Cesar,
>
> I'm glad to hear that!
>
> I am looking forward to testing it myself.
>
> Atenciosamente,
> Luiz
>
> Em ter., 16 de jul. de 2024 às 09:17, Cesar Garcia <
> [email protected]>
> escreveu:
>
> > Hello Luiz,
> >
> > I already have the Odot gateway working with the Plc4x-S7 driver.
> >
> > I will be running tests throughout the day to verify that the small
> change
> > needed does not affect anything else. Basically it is a number.
> >
> > Kind regards,
> >
> > El lun, 15 jul 2024 a las 8:53, Luiz doleron (<[email protected]>)
> > escribió:
> >
> > > Hi Cesar,
> > >
> > > thank you for the follow-up & confirmation.
> > >
> > > Let me know if there is something I can help with.
> > >
> > > Best regards,
> > > Luiz
> > >
> > >
> > >
> > > Em seg., 15 de jul. de 2024 às 01:36, Cesar Garcia <
> > > [email protected]>
> > > escreveu:
> > >
> > > > Hi Luiz,
> > > >
> > > > I tested the Odot modules and indeed with our version of the Plc4x-S7
> > > > driver it fails.
> > > >
> > > > I performed the tests with S7-300 and S7-400 and on both  behave the
> > same
> > > > way.
> > > >
> > > > The Odot equipment does not respond to the first "Setup
> communication"
> > > > message; comparing the frames you can see the difference with respect
> > to
> > > > the use of an HMI or the KepWare driver. I modify the parameters via
> > URL
> > > > but it still does not respond.
> > > >
> > > > It's time to investigate,
> > > >
> > > > El sáb, 13 jul 2024 a las 14:29, Luiz doleron (<[email protected]>)
> > > > escribió:
> > > >
> > > > > Hey Cesar,
> > > > >
> > > > > I modified my code to use CachedPlcConnectionManager but the
> problem
> > > > > persists: the program gets stuck on the getConnection call.
> > > > >
> > > > > This is my code now:
> > > > >
> > > > > public static void main(String[] args) {
> > > > >
> > > > > // System.setProperty(SimpleLogger.DEFAULT_LOG_LEVEL_KEY, "Error");
> > > > >
> > > > > Logger logger = LoggerFactory.getLogger(TestConnection.class);
> > > > >
> > > > > String connectionString = "s7://10.10.26.88?controller-type:S7_300
> ";
> > > > >
> > > > > PlcConnection plcConnection = null;
> > > > >
> > > > > try {
> > > > >
> > > > > CachedPlcConnectionManager connectionManager =
> > > > CachedPlcConnectionManager.
> > > > > getBuilder(new DefaultPlcDriverManager()).build();
> > > > >
> > > > > plcConnection = connectionManager.getConnection(connectionString);
> > > > >
> > > > > if (!plcConnection.getMetadata().isReadSupported()) {
> > > > >
> > > > > logger.error("This connection doesn't support reading.");
> > > > >
> > > > > return;
> > > > >
> > > > > }
> > > > >
> > > > > System.out.println("Success");
> > > > >
> > > > > } catch (Exception e) {
> > > > >
> > > > > e.printStackTrace();
> > > > >
> > > > > } finally {
> > > > >
> > > > > if (plcConnection != null) {
> > > > >
> > > > > try {
> > > > >
> > > > > plcConnection.close();
> > > > >
> > > > > } catch (Exception e) {
> > > > >
> > > > > e.printStackTrace();
> > > > >
> > > > > }
> > > > >
> > > > > }
> > > > >
> > > > > }
> > > > >
> > > > >
> > > > > }
> > > > >
> > > > >
> > > > > The exception trace is:
> > > > >
> > > > > [main] INFO org.apache.plc4x.java.DefaultPlcDriverManager -
> > > Instantiating
> > > > > new PLC Driver Manager with class loader
> > > > > jdk.internal.loader.ClassLoaders$AppClassLoader@2cdf8d8a
> > > > >
> > > > > [main] INFO org.apache.plc4x.java.DefaultPlcDriverManager -
> > Registering
> > > > > available drivers...
> > > > >
> > > > > [main] INFO org.apache.plc4x.java.DefaultPlcDriverManager -
> > Registering
> > > > > driver for Protocol s7 (Siemens S7 (Basic))
> > > > >
> > > > > [main] INFO org.apache.plc4x.java.transport.tcp.TcpChannelFactory -
> > > > > Configuring Bootstrap with
> > > > >
> > > > >
> > > >
> > >
> >
> org.apache.plc4x.java.s7.readwrite.configuration.S7TcpTransportConfiguration@345965f2
> > > > >
> > > > > [main] INFO
> > > org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic -
> > > > > S7 Driver running in ACTIVE mode.
> > > > >
> > > > > [main] INFO org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl
> -
> > > > > 15:11:46.130938260 userEventTriggered: Multiplexor Event:
> > > > > org.apache.plc4x.java.spi.events.ConnectEvent@139982de
> > > > >
> > > > > [nioEventLoopGroup-2-1] WARN
> > io.netty.channel.embedded.EmbeddedChannel
> > > -
> > > > > More than one exception was raised. Will report only the first one
> > and
> > > > log
> > > > > others.
> > > > >
> > > > > io.netty.handler.codec.DecoderException:
> > > > > io.netty.handler.codec.EncoderException: MessageToMessageCodec$1
> must
> > > > > produce at least one message.
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageDecoder.channelRead(
> > > > > MessageToMessageDecoder.java:98)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.channelRead(
> > > > > MessageToMessageCodec.java:111)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:442)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(
> > > > > AbstractChannelHandlerContext.java:412)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageDecoder.channelRead(
> > > > > MessageToMessageDecoder.java:103)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.channelRead(
> > > > > MessageToMessageCodec.java:111)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:442)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(
> > > > > AbstractChannelHandlerContext.java:412)
> > > > >
> > > > > at io.netty.handler.codec.ByteToMessageDecoder.fireChannelRead(
> > > > > ByteToMessageDecoder.java:346)
> > > > >
> > > > > at io.netty.handler.codec.ByteToMessageDecoder.channelRead(
> > > > > ByteToMessageDecoder.java:318)
> > > > >
> > > > > at io.netty.handler.codec.ByteToMessageCodec.channelRead(
> > > > > ByteToMessageCodec.java:103)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:442)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(
> > > > > AbstractChannelHandlerContext.java:412)
> > > > >
> > > > > at io.netty.handler.logging.LoggingHandler.channelRead(
> > > > > LoggingHandler.java:280)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:442)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(
> > > > > AbstractChannelHandlerContext.java:412)
> > > > >
> > > > > at org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl.decode(
> > > > > S7HMuxImpl.java:145)
> > > > >
> > > > > at org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl.decode(
> > > > > S7HMuxImpl.java:1)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec$2.decode(
> > > > > MessageToMessageCodec.java:81)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageDecoder.channelRead(
> > > > > MessageToMessageDecoder.java:88)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.channelRead(
> > > > > MessageToMessageCodec.java:111)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:442)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(
> > > > > AbstractChannelHandlerContext.java:412)
> > > > >
> > > > > at io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(
> > > > > DefaultChannelPipeline.java:1410)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:440)
> > > > >
> > > > > at
> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(
> > > > > AbstractChannelHandlerContext.java:420)
> > > > >
> > > > > at io.netty.channel.DefaultChannelPipeline.fireChannelRead(
> > > > > DefaultChannelPipeline.java:919)
> > > > >
> > > > > at io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(
> > > > > AbstractNioByteChannel.java:166)
> > > > >
> > > > > at io.netty.channel.nio.NioEventLoop.processSelectedKey(
> > > > > NioEventLoop.java:788)
> > > > >
> > > > > at io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(
> > > > > NioEventLoop.java:724)
> > > > >
> > > > > at io.netty.channel.nio.NioEventLoop.processSelectedKeys(
> > > > > NioEventLoop.java:650)
> > > > >
> > > > > at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562)
> > > > >
> > > > > at io.netty.util.concurrent.SingleThreadEventExecutor$4.run(
> > > > > SingleThreadEventExecutor.java:997)
> > > > >
> > > > > at
> > > > >
> > >
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
> > > > >
> > > > > at io.netty.util.concurrent.FastThreadLocalRunnable.run(
> > > > > FastThreadLocalRunnable.java:30)
> > > > >
> > > > > at java.base/java.lang.Thread.run(Thread.java:840)
> > > > >
> > > > > Caused by: io.netty.handler.codec.EncoderException:
> > > > MessageToMessageCodec$1
> > > > > must produce at least one message.
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageEncoder.write(
> > > > > MessageToMessageEncoder.java:99)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.write(
> > > > > MessageToMessageCodec.java:116)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(
> > > > > AbstractChannelHandlerContext.java:891)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite(
> > > > > AbstractChannelHandlerContext.java:875)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:984)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:868)
> > > > >
> > > > > at
> > > io.netty.handler.logging.LoggingHandler.write(LoggingHandler.java:288)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(
> > > > > AbstractChannelHandlerContext.java:891)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite(
> > > > > AbstractChannelHandlerContext.java:875)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:984)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:868)
> > > > >
> > > > > at io.netty.handler.codec.MessageToByteEncoder.write(
> > > > > MessageToByteEncoder.java:113)
> > > > >
> > > > > at io.netty.handler.codec.ByteToMessageCodec.write(
> > > > > ByteToMessageCodec.java:108)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(
> > > > > AbstractChannelHandlerContext.java:891)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite(
> > > > > AbstractChannelHandlerContext.java:875)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:984)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:868)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageEncoder.write(
> > > > > MessageToMessageEncoder.java:113)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.write(
> > > > > MessageToMessageCodec.java:116)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(
> > > > > AbstractChannelHandlerContext.java:891)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite(
> > > > > AbstractChannelHandlerContext.java:875)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:984)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:868)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageEncoder.write(
> > > > > MessageToMessageEncoder.java:113)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec.write(
> > > > > MessageToMessageCodec.java:116)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(
> > > > > AbstractChannelHandlerContext.java:891)
> > > > >
> > > > > at
> > io.netty.channel.AbstractChannelHandlerContext.invokeWriteAndFlush(
> > > > > AbstractChannelHandlerContext.java:956)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.write(
> > > > > AbstractChannelHandlerContext.java:982)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.writeAndFlush(
> > > > > AbstractChannelHandlerContext.java:950)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.writeAndFlush(
> > > > > AbstractChannelHandlerContext.java:1000)
> > > > >
> > > > > at io.netty.channel.DefaultChannelPipeline.writeAndFlush(
> > > > > DefaultChannelPipeline.java:1025)
> > > > >
> > > > > at
> > > >
> > io.netty.channel.AbstractChannel.writeAndFlush(AbstractChannel.java:306)
> > > > >
> > > > > at
> > > > >
> > >
> org.apache.plc4x.java.spi.internal.DefaultConversationContext.sendToWire(
> > > > > DefaultConversationContext.java:70)
> > > > >
> > > > > at
> > org.apache.plc4x.java.spi.internal.DefaultSendRequestContext.handle(
> > > > > DefaultSendRequestContext.java:107)
> > > > >
> > > > > at
> > org.apache.plc4x.java.spi.internal.DefaultSendRequestContext.handle(
> > > > > DefaultSendRequestContext.java:1)
> > > > >
> > > > > at
> > > org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.lambda$3(
> > > > > S7ProtocolLogic.java:194)
> > > > >
> > > > > at
> > > >
> > java.base/java.util.function.Consumer.lambda$andThen$0(Consumer.java:65)
> > > > >
> > > > > at org.apache.plc4x.java.spi.Plc4xNettyWrapper.decode(
> > > > > Plc4xNettyWrapper.java:183)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageCodec$2.decode(
> > > > > MessageToMessageCodec.java:81)
> > > > >
> > > > > at io.netty.handler.codec.MessageToMessageDecoder.channelRead(
> > > > > MessageToMessageDecoder.java:88)
> > > > >
> > > > > ... 40 more
> > > > >
> > > > > [pool-6-thread-1] WARN
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic -
> Timeout
> > > > > during Connection establishing, closing channel...
> > > > >
> > > > > [pool-6-thread-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> Unregistered
> > > of
> > > > > channel: PRIMARY
> > > > >
> > > > > [pool-6-thread-1] WARN
> > io.netty.channel.AbstractChannelHandlerContext -
> > > > > Failed to mark a promise as failure because it has succeeded
> already:
> > > > > DefaultChannelPromise@53d1d4d1(success)
> > > > >
> > > > > java.lang.IllegalStateException: HashedWheelTimer.stop() cannot be
> > > called
> > > > > from TimerTask
> > > > >
> > > > > at io.netty.util.HashedWheelTimer.stop(HashedWheelTimer.java:393)
> > > > >
> > > > > at
> org.apache.plc4x.java.spi.netty.NettyHashTimerTimeoutManager.stop(
> > > > > NettyHashTimerTimeoutManager.java:63)
> > > > >
> > > > > at org.apache.plc4x.java.spi.Plc4xNettyWrapper.close(
> > > > > Plc4xNettyWrapper.java:130)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.invokeClose(
> > > > > AbstractChannelHandlerContext.java:757)
> > > > >
> > > > > at io.netty.channel.AbstractChannelHandlerContext.close(
> > > > > AbstractChannelHandlerContext.java:733)
> > > > >
> > > > > at io.netty.channel.DefaultChannelPipeline.close(
> > > > > DefaultChannelPipeline.java:994)
> > > > >
> > > > > at io.netty.channel.AbstractChannel.close(AbstractChannel.java:280)
> > > > >
> > > > > at
> > > > >
> > >
> io.netty.channel.embedded.EmbeddedChannel.close(EmbeddedChannel.java:569)
> > > > >
> > > > > at
> > > > >
> > >
> io.netty.channel.embedded.EmbeddedChannel.close(EmbeddedChannel.java:556)
> > > > >
> > > > > at
> > > org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.lambda$4(
> > > > > S7ProtocolLogic.java:185)
> > > > >
> > > > > at org.apache.plc4x.java.spi.Plc4xNettyWrapper.lambda$8(
> > > > > Plc4xNettyWrapper.java:253)
> > > > >
> > > > > at
> > > org.apache.plc4x.java.spi.netty.NettyHashTimerTimeoutManager.lambda$0(
> > > > > NettyHashTimerTimeoutManager.java:55)
> > > > >
> > > > > at io.netty.util.HashedWheelTimer$HashedWheelTimeout.run(
> > > > > HashedWheelTimer.java:715)
> > > > >
> > > > > at io.netty.util.concurrent.ImmediateExecutor.execute(
> > > > > ImmediateExecutor.java:34)
> > > > >
> > > > > at io.netty.util.HashedWheelTimer$HashedWheelTimeout.expire(
> > > > > HashedWheelTimer.java:703)
> > > > >
> > > > > at io.netty.util.HashedWheelTimer$HashedWheelBucket.expireTimeouts(
> > > > > HashedWheelTimer.java:790)
> > > > >
> > > > > at
> > io.netty.util.HashedWheelTimer$Worker.run(HashedWheelTimer.java:503)
> > > > >
> > > > > at java.base/java.lang.Thread.run(Thread.java:840)
> > > > >
> > > > > [nioEventLoopGroup-2-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> Unregistered
> > > of
> > > > > channel: PRIMARY
> > > > >
> > > > > [nioEventLoopGroup-2-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> > > > > io.netty.channel.embedded.EmbeddedEventLoop@476a35e8
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HPlcConnection -
> > Creating
> > > > > prymary connection.
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.transport.tcp.TcpChannelFactory - Configuring
> > > > > Bootstrap with
> > > > >
> > > > >
> > > >
> > >
> >
> org.apache.plc4x.java.s7.readwrite.configuration.S7TcpTransportConfiguration@345965f2
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HPlcConnection -
> > > > Reconnecting
> > > > > primary channel.
> > > > >
> > > > > [nioEventLoopGroup-3-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> Unregistered
> > > of
> > > > > channel: PRIMARY
> > > > >
> > > > > [nioEventLoopGroup-3-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> > > > > io.netty.channel.embedded.EmbeddedEventLoop@476a35e8
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HPlcConnection -
> > Creating
> > > > > prymary connection.
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.transport.tcp.TcpChannelFactory - Configuring
> > > > > Bootstrap with
> > > > >
> > > > >
> > > >
> > >
> >
> org.apache.plc4x.java.s7.readwrite.configuration.S7TcpTransportConfiguration@345965f2
> > > > >
> > > > > [plc4x-s7ha-thread-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HPlcConnection -
> > > > Reconnecting
> > > > > primary channel.
> > > > >
> > > > > [nioEventLoopGroup-4-1] INFO
> > > > > org.apache.plc4x.java.s7.readwrite.protocol.S7HMuxImpl -
> Unregistered
> > > of
> > > > > channel: PRIMARY
> > > > >
> > > > > ...
> > > > >
> > > >
> > > >
> > > > --
> > > > *CEOS Automatización, C.A.*
> > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
> > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
> > > >
> > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
> > > > *Ing. César García*
> > > >
> > > > *Cel: +58 414-760.98.95*
> > > >
> > > > *Hotline Técnica SIEMENS: 0800 1005080*
> > > >
> > > > *Email: [email protected]
> > > > <[email protected]>*
> > > >
> > >
> > >
> > > --
> > > Luiz Carlos d´Oleron
> > >
> >
> >
> > --
> > *CEOS Automatización, C.A.*
> > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
> > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
> >
> > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
> > *Ing. César García*
> >
> > *Cel: +58 414-760.98.95*
> >
> > *Hotline Técnica SIEMENS: 0800 1005080*
> >
> > *Email: [email protected]
> > <[email protected]>*
> >
>
>
> --
> Luiz Carlos d´Oleron
>


-- 
*CEOS Automatización, C.A.*
*GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
*PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*

*FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
*Ing. César García*

*Cel: +58 414-760.98.95*

*Hotline Técnica SIEMENS: 0800 1005080*

*Email: [email protected]
<[email protected]>*

Reply via email to