As Doug said, the APC UPSes handle a very wide range of input voltage
with no trouble. I used to be on a campus with 208V power everywhere,
but now I'm off-campus where 120V and 240V are the norm.

My office is in a commercial leased space in a residential area, so we
use a SmartUPS 3000 with the 240V input to power our rack, which expects
208V power. The rack PDUs handle the 120V side for the servers. I had a
nice chat with APC tech support about the input and outputs before we
bought it, and the UPS is quite capable of handling the various voltages.

NOTE: Also, you may need to set the input sensors not to call 240V a
spike and alarm or switch to battery. I think our unit came with the
widest sensitivity, but I've had units from the factory with the
narrowest sensitivity set.

Enjoy the new toy!
Allan

On 7/13/12 12:51 AM, Doug Hughes wrote:
> 
> I just checked the specs for that unit online. It's a wide sensing
> input, as most single phase devices are:
> http://excessups.com/smartups-3000-rackmount-dla3000rmt2u-sua3000rmt2u-208v-p-74.html
> 
> Input voltage range for main operations: 141 - 255V 
> 
> You can plug it into 240V no problem, as long as you have the right
> receptacle.
> 
> 
> On 7/13/2012 12:14 AM, Nick Whalen wrote:
>> I appear to have become the victim of my own hastiness.  I picked up
>> an APC 3000VA 208V UPS (DLA3000RMT2U) with the corresponding
>> 208v->120v transformer (SURT005)  for $200 from a guy on Craigslist. 
>> Being in a hurry to get home, I missed the fact that these are _208v_
>> when I looked up the units on APC's website.  If my electrical
>> knowledge serves me right this is two legs off commercial 3-phase
>> service voltage.
>>
>> Obviously I do not have three phase in my home, where these were going
>> to be used, so my question is this... have any of you had experience
>> running 208v equipment on 240v single-phase mains (most likely using a
>> buck autotransformer)?  If so, do you have suggestions on where to get
>> an appropriate autotransformer?
>>
>> My other option is to just turn around and re-sell these things to
>> someone who could use them on 208v; or swap with someone for a 120 or
>> 240V unit of a similar capacity (moving your server room to commercial
>> power?).  I'm in the Seattle area of Washington state, in the unlikely
>> chance someone wanted units like these.
>>
>> Nick