Nick As Doug said, the APC UPSes handle a very wide range of input voltage with no trouble. I used to be on a campus with 208V power everywhere, but now I'm off-campus where 120V and 240V are the norm.
My office is in a commercial leased space in a residential area, so we use a SmartUPS 3000 with the 240V input to power our rack, which expects 208V power. The rack PDUs handle the 120V side for the servers. I had a nice chat with APC tech support about the input and outputs before we bought it, and the UPS is quite capable of handling the various voltages. NOTE: Also, you may need to set the input sensors not to call 240V a spike and alarm or switch to battery. I think our unit came with the widest sensitivity, but I've had units from the factory with the narrowest sensitivity set. Enjoy the new toy! Allan On 7/13/12 12:51 AM, Doug Hughes wrote: > > I just checked the specs for that unit online. It's a wide sensing > input, as most single phase devices are: > http://excessups.com/smartups-3000-rackmount-dla3000rmt2u-sua3000rmt2u-208v-p-74.html > > Input voltage range for main operations: 141 - 255V > > You can plug it into 240V no problem, as long as you have the right > receptacle. > > > On 7/13/2012 12:14 AM, Nick Whalen wrote: >> I appear to have become the victim of my own hastiness. I picked up >> an APC 3000VA 208V UPS (DLA3000RMT2U) with the corresponding >> 208v->120v transformer (SURT005) for $200 from a guy on Craigslist. >> Being in a hurry to get home, I missed the fact that these are _208v_ >> when I looked up the units on APC's website. If my electrical >> knowledge serves me right this is two legs off commercial 3-phase >> service voltage. >> >> Obviously I do not have three phase in my home, where these were going >> to be used, so my question is this... have any of you had experience >> running 208v equipment on 240v single-phase mains (most likely using a >> buck autotransformer)? If so, do you have suggestions on where to get >> an appropriate autotransformer? >> >> My other option is to just turn around and re-sell these things to >> someone who could use them on 208v; or swap with someone for a 120 or >> 240V unit of a similar capacity (moving your server room to commercial >> power?). I'm in the Seattle area of Washington state, in the unlikely >> chance someone wanted units like these. >> >> Nick _______________________________________________ Discuss mailing list Discuss@lists.lopsa.org https://lists.lopsa.org/cgi-bin/mailman/listinfo/discuss This list provided by the League of Professional System Administrators http://lopsa.org/