On 22/10/11 11:52, c...@pampru.org wrote:
Hi Tim,

I have been specifying and running around one hundred APC 3000 UPS units spread over about fifteen or more years and installed them in different countries and running from one PC + monitor upwards with no significant operational problems. I also specified and used many of their 4KVA units without any operational problems. APC make very good UPS units for USA and European markets.

APC's support department is quite another matter. I have had battles with them over plainly incorrect specifications on their website, and on technical matters such as not isolating Neutrals when tripped out or when the APC is switched off (as I don't control wiring in the locations I was installing, I was concerned that circuits could still be at mains potential if Neutral/Live became reversed). There have been deep conflicts within APC on the issues that I have tried to resolve.

However, APC UPS 3000 units are very good in normal use and I still specified them as well as AEG.

What is the specific problem you have encountered? (i.e., not the problem APC say you have).

Charles


Quoting Peter Washington <pugwash1...@gmail.com>:

Hi Tim,

On 21 October 2011 16:47, Tim <xendis...@gmx.com> wrote:


I have and APC 3000 UPS <http://www.apc.com/resource/**
include/techspec_index.cfm?**base_sku=sua3000rmi2u<http://www.apc.com/resource/include/techspec_index.cfm?base_sku=sua3000rmi2u>>(see link below) at work and it is causing a few problem. APC tech support want me to run the UPS on battery on at least 30% load (but not using the current server that are connected as the load for obvious reason). Now as this is a 3000va UPS how many basic PC will I need to plug into the UPS to attain a
30% load (I am assuming most PC have a 300w PSU?)

http://www.apc.com/resource/**include/techspec_index.cfm?**
base_sku=sua3000rmi2u<http://www.apc.com/resource/include/techspec_index.cfm?base_sku=sua3000rmi2u>

Any help would be appreciated

Tim


The simple answer of 30 % of 3000 is 900 VA so 3 PC's is definitely wrong. This is because PC's nowadays generally have PSU's of anything from 250 W to 1000 W, AND because the load they draw from the mains is dependent on what
they are doing.

I suggest that a 1 KW electric fire would give a constant load of
approximately the right size, and if the APC tech wants a more precise load
then you need to look at other comparable electrically powered items.

If APC want a REALLY precise load, then you also need to take into account Power Factor, which is a subject that needs considerably more space than a simple email, so I'd suggest 15 x 60 Watt incandescent light bulbs, or, (if you can find them), 9 x 100 W. You certainly can't use Compact Fluorescent
bulbs though, it's that Power Factor thing.

I hope this helps.

--

Cheers Peter
--

I fitted a new battery (front panel led indicated battery failure) and network management card (previous card was serial), now when I check the status of the UPS via the web interface it tells me that if I loose power the UPS will switch off as there is no charge in the battery. If I check the status of the UPS, it shows that I have a 37% load and a 100% battery charge, the load part is bourne out by the led on the front panel while the battery charge lights are all lit and flashing.

Tim

--