On 13 April 2011 01:20, Dave <[email protected]> wrote:

> What is the L term?

Sorry, I didn't explain. L was so obviously "The value of the combined
PI limit" in my head that I forgot to explain it.

> Many or most of the PID loops that I work with  (usually for process
> control systems) have anti reset windup implemented such that once the
> PID output hits it's limit in a positive or negative direction,
> the I term is not allowed to integrate any further.
>
> Does the scheme you describe work differently?

Yes, though not necessarily better.
In this scheme, if the P output alone is enough to hit the maximum
limit, then I is clamped to zero. I only starts to increase once the
Pgain alone is no longer enough to hit the output limit.

I might mess about with spreadsheets this lunchtime to see how the
differing approaches work in practice. My feeling is that the fact
that I can start to increase before the setpoint will tend to speed up
the final approach to the setpoint, possibly at the expense of some
overshoot.

-- 
atp
"Torque wrenches are for the obedience of fools and the guidance of wise men"

------------------------------------------------------------------------------