We are designing transformers for use in products that will require the CE 
Mark, and we need to use triple insulated wire such as the Furukawa TEX-E 
wire to get the internal creepage and clearance required in 950.  At 
present, the transformers run hot enough that a class 130C system is 
required.

I have recently discovered that both the Rubadue and Furukawa wires do not 
have a Class 130C temperature rating, which is what our insulation systems 
to date have all been.  Both wires have UL and CSA listings only for Class 
105C.

Does anyone have any experience (ie success) in getting UL to accept these 
wires in Class B systems or at Class B temperatures?  I have a copy of one 
RIS listing that includes the Furukawa wire, so I know the wire is good 
enough and it is possible to get the listing.  However the number of 
materials in that listing was very low, so I didn't see any of our specific 
materials there (such as 3M#56, phenolic bobbins, etc.).  While the listing 
proves it is possible to get a less-than-130C material into an 130C system, 
it doesn't do us much practical good.

What I am looking for is the easiest way to prove that the temperatures we 
are getting are acceptable.  I am not sure what the approach is for CE 
self-declaration:  must the system be evaluated by some agency, looking for 
detrimental interactions under long-term or accelerated aging conditions? 
 Suppose all our materials were rated at least 130C - can we just take a 
"the system is as good as the weakest link in the chain" approach?  Now 
given that we are using a material rated less than 130C, what are our 
options?  I know what the answers are for CSA and UL approvals, but for 
self-declaration for the CE Mark I'm not so sure.

The safety engineer in me says I should submit our system to UL for the RIS 
process.  Does anyone else have any easier ideas?  Does anyone know what the 
time and cost involved are?

Your help would be greatly appreciated,

Yours truly,


Jim Eichner
Statpower Technologies Corporation
[email protected]