Rich,

this is a very interesting discussion. I agree with most you are saying. 
I like to add that there is some pressure from ACOS (IEC Advisory 
Committee on Safety) to bring together IEC 65 and IEC 950 into one set 
of requirements. The problem arises in residential areas where you have 
cable-TV, your PC hooked to a telecommunication network, and other 
applications, e.g. you control your entrance with a TV camera, or you 
monitor your windows/doors in the home for burgler-protection. Assuming 
you have tied all together into one system,

>>>>what is the correct standard to be applied?<<<<

With your following statement 
"Standards should not limit the acceptable constructions, but
should specify ALL the alternative constructions that provide
equivalent protection" 
I do not agree to 100 percent. It is not the correct approach to specify 
ALL possible alternative constructions. This may be required in some 
exceptional situations where you are not in the position to clearly 
specify the goal which hazard you need protection from. The discussions 
and interpretation problems with testhouses arise if you choose an 
alternative construction which was not described before in the standard, 
but which provides at least the same level of safety as the specified 
ones (see IEC 950, 1.3.1).
The normal case in a standard should be to specify exactly what shall be 
or what shall not be.

(BTW: I consider IEC 950 to be of the form "If .... , then .... .", 
again see 1.3.1 and also 1.4.1.)
-- 
Kind regards/mit freundlichen Gruessen,