Georg, My representative from LGA America did a little research for me some time ago about leakage current as associated with prEN50178. The research was on the 1994 issue of the standard but it still applies in the 1995 issue.
The results are based on section 5.2.11.1 of the standard: 1) For pluggable (removable or modular line cord) equipment the limit is 3.5mA AC / 10 mA DC. 2) If the leakage current exceeds this level then there are three possible ways of dealing with the problem. a) a duplicate PE conductor or an automatic disconnect which monitors the continuity of the PE conductor or a double-wound transformer. I believe the "double-wound transformer" is referring to an isolation transformer in the primary circuit which actually reduces leakage current. We have always used an auxiliary PE conductor which is bonded to the rear of the chassis and the PE symbol is located at both the conductors bonding points. When the second PE conductor is used a note is required in the operating documents which requires the connection of this conductor for proper installation (section 7.2.3.2). 3) For fixed installations there is effectively no limit to the amount of leakage current allowed. See section 5.2.11.1 paragraph 4, "Measurement of leakage current is required on EE which is not intended for permanent connection". Conversely, for EE that is intended for permanent connection (fixed wiring), the measurement is not required. There was a letter written by LGA Nrnberg with instructions to this effect. I do not readily have my copy but if you contact LGA in Nurnberg and reference a letter written to Mr. Werner Pster of LGA America / EuroConsult, Inc. They should be able to copy you with the information. Also the letter was originated in German, if you want an English version I believe Mr. Pster still has a translated copy. You reference myself and reach him at: Mr. Werner Pster / EuroConsult, Inc. euroc...@shore.net However he is a consultant and he may charge for his time. As far as the status of the standard is concerned, I was told that even though it is still in preliminary status, the standard has been released for type testing. Once again you may validate this with LGA Nrnberg. Hope this helps you. Doug Powell Advanced Energy Industries, Inc. Ft. Collins, Colorado USA do...@ftc2.aei.com ---------- From: Georg M. Dancau To: emc-pstc discussion group Subject: Status of prEN50178 List-Post: emc-pstc@listserv.ieee.org Date: Tuesday, August 12, 1997 6:28AM Hi compliance folks Does anybody have information about the status of prEN50178. This standard specifies some measures which must be taken if the leakage greater than 3.5 mA (clause 5.2.11). Best regards George -- ************************************************************** * Dr. Georg M. Dancau * HAUNI MASCHINENBAU AG * * g.m.dan...@ieee.org * EMC Lab * * TEL: +49 40 7250 2102 * Kampchaussee 8..32 * * FAX: +49 40 7250 3801 * 21027 Hamburg, Germany * ************************************************************** * home: Tel: +49 4122 99451 * Hauptstr. 60a * * Fax: +49 4122 99454 * 25492 Heist, Germany * **************************************************************