The safety agencies will primarily look to see if the inrush will cause
nuisance tripping of any overcurrent protection devices, including the
branch circuit protection, and sometimes effects on additional earth
leakage current.  For your application, the North American agencies will
assume branch circuit protector is rated 15A (assuming your using an
ANSI/NEMA 5-15P attachment plug).  Inrush current is typically
monitored, but isn't generally a show-stopper without some secondary
effect.

Regards,

Peter L. Tarver
Nortel
ptar...@nt.com

>----------
>From:  Paul Herrick[SMTP:0007515...@mcimail.com]
>Sent:  Tuesday, April 22, 1997 7:09 PM
>
>Does anyone know of any regulatory reason to control the startup surge
>current
>to ITE units?  We have measured this startup current to be up to 90A for the
>first half cycle of applied voltage.  The unit is cord set connected and uses
>four switching power supplies and has a rating of 100-120/220-240V   7/3.5A.
>
>Do safety agencies (UL/CSA/TUV) ever measure this start up current as part of
>a
>certification investigation?
>++
>Thanks,
>Paul Herrick
>7515...@mcimail.com
>