George -

The answer to your question is: yes.  However, in the US, this is type
of system is used to deliver power to homes and there are either no or
very few homes supplied with three-phase power.  Such a system would be
abhorrent to any user of all three phases, who would prefer the
corner-grounding method.

Perhaps this thread has become a bit muddled in that I was responding to
a question Doug McKean posed about grounding of delta secondaries.
There are two basic methods, as I described.  I was not trying to
address the GFCI question or otherwise say that the
center-grounded-delta configuration was suitable for other than power
delivery to homes, receiving 120V line-to-neutral and 240V line-to-line.
 My apologies for the confusion.

Regards,

Peter L. Tarver
Nortel
ptar...@nt.com

>----------
>From:  Georg M. Dancau[SMTP:dan...@compuserve.com]
>Sent:  Thursday, February 26, 1998 3:47 AM
>
> Peter Tarver wrote:
>
>  Delta-delta transformers are popular with the utilities for economy's
>  sake (they are less expensive than WYE transformers)  For similar
>  reasons, some industrial applications distribute and use power within
>  their plants on delta feeds.
>
>  In office environments, however, it's typical to use a WYE connected
>  secondary, i.e., 120Y/208V, for general appliance use and other WYE
>  connected configurations for lighting and other power.
>
>  When a delta transformer is grounded, it typically occurs at either a
>  "corner", where two secondaries are electrically connected, or
>  "center-grounded" at the center of one of the secondaries.  It is my
>  understanding that the latter case is typical for power provided to
>  homes in the US and is also referred to as "split-phase."
>
>  Regards,
>
>  Peter L. Tarver
>  Nortel
>  ptar...@nt.com
>
>
>Hi Pete
>
>I want to address the issue of or <"center-grounded" at the center of
>one of the secondaries>.
>
>Do you mean like this ?
>
>  [Image]
>
>I never encountered this yet. In this case, the voltages of the three
>active conductors with respect to earth would be:
>
>V(L1)=480V*sqrt(3)/2=415V
>V(L2)=480V/2=240V
>V(L3)=480V/2=240V
>
>The voltage of the imaginary center point would be about 208V. You would
>have enormous leakage
>currents through the Y capacitors in the power line filters.
>
>On the other hand, as far as I remember, the IEC 38 states, that for a
>TN network, one active
>conductor is earthed (not stating which one). In this case I do not see
>any conformance with the IEC38.
>
>I'll be glad for any comment from the pstc community on this issue.
>
>Best regards
>
>
>George
>
>--
>**************************************************************
>* Dr. Georg M. Dancau             *  HAUNI MASCHINENBAU AG   *
>* g.m.dan...@ieee.org             *  Manager EMC Lab         *
>* TEL: +49 40 7250 2102           *  Kampchaussee 8..32      *
>* FAX: +49 40 7250 3801           *  21027 Hamburg, Germany  *
>**************************************************************