--- On Mon, 22 Jun 1998 00:44:00 -0700  "Liew, Shih Perng" 
<shih.perng.l...@intel.com> wrote:
>      Hi All,
>      
>      I have some different machines in one production line sharing a same 
>      power source, namely IX testers, ovens etc. I encountered a problem 
>      where some of the ovens tripped-off intermittently. The earth-leakage 
>      current was found to be excessive and causes the earth-leakage circuit 
>      breaker to trip. To find a short-term solution, the affected ovens 
>      were rewired from a new power source and the metal structures were 
>      insulated. The problem seems to be solved...however, I am not so 
>      convinced.
      
>      rgds,
>      sp

Shih:

Be careful! The ovens which caused the leakage path to exist have now "been 
connected to a different power source" which I assume does not have ground 
fault current sensing? And you have "insulated the metal structures"?

Seems like this creates a hazard, since the new arrangement will allow a 
dangerous voltage potential to exist between the newly insulated metal 
structures and earth ground.

Better find out where that fault path is in the ovens, and get the structure 
grounded again. Look at the heater elements, look for corrosion and 
contamination on the insulator supports. Check for corroded sensing and control 
elements, and look at the fan motors for insulation degradation.