>What voltages can I expect on the Neutral (referenced to ground) line in
various countries
>and connection systems? Is there a limit on how high the voltage may be, both
in normal and
>fault conditions?

Moshe,
THE's booklet, "World Electricity Supplies", lists the supply voltage,
frequency, and power distribution systems used in over 200 countries.  You can
order it through Technical Standards Services, Ltd. webpage at
http://www.techstandards.co.uk/thsguide.html

"TN" and "TT" power systems (IEC 950  1.2.12.1 and 1.2.12.2) are the ones
usually encountered.  Neutral-to-ground voltages should be less than a few (5 or
so) volts even under a line-to-ground fault.  Hospitals and other
high-reliability installations sometimes use "IT" power systems (IEC 950
1.2.12.3) permitting continued operation even if a line-to-ground fault occurs--
at the cost of:
*  Neutral-to-ground voltage approaching the single-phase line voltage.
*  In a three-phase system, the other phase-to-ground voltages approaching
sqrt(3) times the single-phase line voltage.

This can double the required creepage and clearance distances for (to us) a tiny
additional market.  So we specify that our products are not to be installed on
IT power systems, but may be powered by an isolation transformer that gets its
power from an IT power system  to create a local TN-S power system.
                                                        John Barnes   Advisory
Engineer
                                                        Lexmark International



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

Reply via email to