> -----Original Message-----
> From: Chuck Mello [SMTP:chuck_me...@electro-test.com]
> Sent: Wednesday, September 01, 1999 7:41 AM
> To:   s...@world.std.com; 'emc-p...@majordomo.ieee.org'; 'n...@nfpa.org'
> Subject:      Re: NFPA and overcurrent protection requirements. 
> 
> Lauren
> The NEC and NFPA 79 are pretty much in alignment with each other for
> overcurrent protection of conductors.  The basic rule as you properly
> stated is that overcurrent protection is to be provided at the source or
> the start of the conductors being protected.  For the situation posed by
> the exceptions to paragraph 8.4 and also by NEC Section 240-21 for  tapped
> conductors, you have to consider the elements of overcurrent protection
> separately to understand the application.  
> 
> Overcurrent protection includes short circuit, ground fault and overload
> as
> the three elements.  What the exceptions and the NEC tap rules do is allow
> you to have only the short circuit and ground fault protection ahead of
> the
> conductors as provided by the main or feeder device.  That is where the
> requirements of the tap conductor having an ampacity of not less than 10
> times the feeder conductor for the 10 foot rule or the tap has to be at
> least 1/3 the ampacity of the main conductors in the 25 foot limitations. 
> The overload protection is then provided by a limited load and within the
> enclosure (10 foot rule) or a device (circuit breaker or single set of
> fuses) at the load end of the conductors (10 and 25 foot rules).  The
> position of the overload device in the circuit is not as critical in that
> it provides protection ahead of and below the device for the conductors. 
> Another example of this that is similar is motor protection where the
> short
> circuit device is at the source of the circuit, and the controller with
> the
> overload device is possibly at some distance away toward the motor.  All
> the branch circuit conductors from the short circuit device to the motor
> are protected by the overload device no matter where it is located in the
> circuit.
> 
> Joe Sheehan at NFPA is the staff liaison for NFPA 79 and is an excellent
> practical resource.  NFPA policy is that staff can provide an opinion but
> formal interpretations have to go through the technical committees which
> can take some time.  
> 
> ----------
> > From: Crane, Lauren <lcr...@bev.etn.com>
> > To: 's...@world.std.com'; 'emc-p...@majordomo.ieee.org'; 'n...@nfpa.org'
> > Subject: NFPA and overcurrent protection requirements. 
> > Date: Monday, August 30, 1999 9:19 AM
> > 
> > Dear Colleagues,
> > 
> > NFPA 79 (1997) provides the following requirement regarding overcurrent
> > protective devices...
> > 
> > "8.4 Overcurrent protective devices shall be located at the point where
> the
> > conductor to be protected receives its supply."
> > 
> > Then two exceptions are provided. However, it is not explicit if the
> > exception is regarding the placement of the protective device at the
> supply
> > point to the conductor, or is the exception regarding the provision of
> the
> > protective device. In other words, does the exception allow the
> protective
> > device to be absent under the given conditions?
> > 
> > A similar section in EN 60204 (1997) is 7.2.8
> > 
> > "An overcurrent protective device shall be located at the point where
> the
> > conductor to be protected is connected to its supply. Where that is not
> > possible, no overcurrent protection is required for those conductors
> with
> > current-carrying capacity less than that of the supply conductors,
> provided
> > that the possibility of a short circuit is reduced by all of the  
> following
> > measures:..."
> > 
> > This section clearly states that the exception allows not having any
> > protection at all. 
> > 
> > It seems reasonable that the intent of NFPA 79 is the same as EN 60204
> ..
> > but I want to be a bit more certain.
> > 
> > So...the basic question....IF all the conditions are met for either the
> > first or second exception of section 8.4 in NFPA 79, may an overcurrent
> > protective device be left out?
> > 
> > And two follow-ups
> > 
> > ...with regard to exception 1, the last condition "the conductor
> terminates
> > in a single circuit breaker or set of fuses" means, for example, a 16
> awg
> > wire may get its supply from a terminal block fed by a 2 awg wire, but
> it
> > must terminate at the other end in a circuit breaker or fuse sized
> correctly
> > for the 16 awg wire. Is this correct?
> > 
> > ...with regard to exception 2, the last condition "the conductor
> terminates
> > in a splitter block, circuit breaker or set of fuses." This means that
> the
> > 16 awg wire of the above example may also terminate to another terminal
> > block. Is this correct?    (i.e. splitter block = terminal block).
> > 
> > Thanks in advance for any comments. 
> > 
> > P.S. does anyone know how to get interpretations out of NFPA? I have a
> > question queued up at n...@nfpa.org that has been answered after a couple
> > weeks of waiting.  

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

Reply via email to